    The Evaporating Temp Of R407c



    Hello

    Dear Colleagues

    I need to know the evaporating temperature used in heat pump split system air conditioner (9000 btu 18000btu) using R407C.

    Also I need to know if there is a special way to fill the unit by R407C.

    Thanks.
    Last edited by Brian_UK; 06-10-2006 at 06:44 PM. Reason: Changed capitals to lower case, no need to shout!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: The Evaporating Temp Of R407c

    To fill system with R407C you must charge it in the liquid state.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: The Evaporating Temp Of R407c

    There is no unique "evaporating temperature" because R407c is zeotropic, and it shows a glide between dew point and bubble point.
    As a rule of thumb, mid point evap temp is usually 10 to 12°K below ambient temperature in heat pump mode.

  4. #4
    acfrigoman's Avatar
    acfrigoman Guest

    Re: The Evaporating Temp Of R407c

    Thanks Brian And Nonickname For Your Help.

    Regards

  5. #5
    Join Date
    Aug 2006
    Location
    Sri Lanka
    Posts
    34
    Rep Power
    0

    Re: The Evaporating Temp Of R407c

    R407c is a zoetropic blend of R32/R125/R134a, where the three refrigerants have non-similar boiling points. As a result, R407c gas a temperature glide of about 7 deg C at 100 kPa. Further the magnitude of temperature glide depends on the pressure as well in such a way that one gets a smaller temperature glide in the condenser than in the evaporator.

    In addition, composition shift of R407c during phase change affect the magnitude of temperature glide so that the actual magnitude of glide during running is system specific.

    lraja

  6. #6
    acfrigoman's Avatar
    acfrigoman Guest

    Re: The Evaporating Temp Of R407c

    hi Iraja

    thank u for your usuful information about composition

    of R407c and it caracteristique.
    said