    Thumbs up NH3 system for minus 40 deg c brine temperature



    Hello everybody,

    This is my first mail on such a informative web site.

    Has anybody designed ammonia system for minus 40 deg C brine temperature? Please clarify following doubts:-

    1) apart from oil seperator what are the necessary arrangements to be provided for avoiding oil entering in to the evaporator. kindly mentioned the recovery system too.

    waiting for positive reply.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: NH3 system for minus 40 deg c brine temperature

    I haven't designed such a systems but for a brine of -40°C (= -40°F) or evaporating at -46°C (-50.8°F) is a low pressure below atmospheric pressure when using NH3
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: NH3 system for minus 40 deg c brine temperature

    Hi, Meg

    Welcome to RE

    Quote Originally Posted by meg View Post
    Hello everybody,

    This is my first mail on such a informative web site.

    Has anybody designed ammonia system for minus 40 deg C brine temperature? Please clarify following doubts:-

    1) apart from oil seperator what are the necessary arrangements to be provided for avoiding oil entering in to the evaporator. kindly mentioned the recovery system too.

    waiting for positive reply.
    Tell us, please, what is your system for?

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    meg's Avatar
    meg Guest

    Re: NH3 system for minus 40 deg c brine temperature

    Dear Mr.Peter,

    Your suggestion will not solve the problem.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: NH3 system for minus 40 deg c brine temperature

    Was that a suggestion I've made?
    I haven't read you had a problem, only a doubt.

    You may install the best oil separtor, there will allways oil passing through it.
    So necessary arrangements will have to be a system removing the oil out of teh NH3/oil solution.

    You haven't even mentioned what kind and size of evaporator you will use.

    Sorry if I didn't give you the answer you expected.
    Last edited by Peter_1; 05-10-2006 at 07:30 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: NH3 system for minus 40 deg c brine temperature

    Quote Originally Posted by meg
    what are the necessary arrangements to be provided for avoiding oil entering in to the evaporator
    Absolutely none. Oil will enter the evaporator no matter what you do. The only way to prevent this is to use an dry compressor (no oil in circulation).

    The oil recovery system is a simple small vessel which allows oil to drain into it by gravity from the bottom of the chiller. They are called "oil pots".

    I'm assuming the chiller is a flooded shell & tube. You did not mention sufficient details for a lengthy answer. Sorry.

  7. #7
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: NH3 system for minus 40 deg c brine temperature

    hi

    i think the use of gammonia for this, only will give you problems, try a caskad system NH3/CO2 R717/R744 or R717/R1150 ammonia/ethylen

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: NH3 system for minus 40 deg c brine temperature

    Kasper, Meg doesn't want suggestions,
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Oct 2006
    Location
    India
    Age
    56
    Posts
    7
    Rep Power
    0

    Re: NH3 system for minus 40 deg c brine temperature

    we can use ammonia for this type of application. Of course the pressures are lower than ambient and need to provide only welded joints. The oil throw from compressor alongwith gas can be minimised with larger oil separtor/coaliscer element. Also you can provide some special automatic oil draining system to collect the oil from receiver and charge back to the compressor after heating. I hope this would help you. Any oil reached the chiller can be drained only after the siwtching off the compressor as the chiller is under negative pressure during operation.

  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: NH3 system for minus 40 deg c brine temperature

    Quote Originally Posted by refsystem View Post
    Any oil reached the chiller can be drained only after the siwtching off the compressor as the chiller is under negative pressure during operation.
    Unless you use a pump, just a suggestion.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Mar 2006
    Location
    Frederikssund
    Age
    49
    Posts
    24
    Rep Power
    0

    Re: NH3 system for minus 40 deg c brine temperature

    dear Mr Peter_1

    Sorry my fault :-)

    -------------

    For a olie return system from the evap. , i´l use enjektor or pump drum using hotgas

    what Olietype will/or are you using?

    i do not think i will want the olie form the evap returning to the compressor/s it may be damage
    ------------

    -but you still have th the problem with Air that will enter the system

  12. #12
    luzhang's Avatar
    luzhang Guest

    Re: NH3 system for minus 40 deg c brine temperature

    Good oil separator design will help reduce the oil amount enter in the evaporator.the oil recovery system is necessary.It is better to design an auto air purger to remove the non-condensing foul gas.

  13. #13
    Join Date
    Jul 2006
    Location
    New Berlin, Wisconsin, USA
    Age
    65
    Posts
    57
    Rep Power
    18

    Re: NH3 system for minus 40 deg c brine temperature

    You may want to look at using a PAO oil, it is a full synthetic which will give you around a -55 C pour point. Instead of a mineral based oil.

    This way if any oil makes it through the separator, it will still remain fluid at the temperatures you are running.

  14. #14
    tinglehand's Avatar
    tinglehand Guest

    Re: NH3 system for minus 40 deg c brine temperature

    Hello.

    I believe someone answer this question in this same thread some time ago. It is almost impossible to prevent the oil going into the evaporator. I worked some time with system at -30 and -42 deg C (screw compressors). All this will depend of your compressors and the oil separator that they have. Also how good is the oil separation after the condenser. As Iceman said use oil pots in you evaporator, maybe you will not need defrost but it will be really difficult to take the oil out of your evaporator at such temperature of the brine (hot gas could help you a lot) and of course there is the issue of the pressure.

    I will not recommend oil recovery in the evaporator or condensers due to the cost and the quality of the oil there that will depend of the discharge compressor temperature and ammonia quality (water presence).

  15. #15
    tinglehand's Avatar
    tinglehand Guest

    Re: NH3 system for minus 40 deg c brine temperature

    Good point refteach

  16. #16
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: NH3 system for minus 40 deg c brine temperature

    Quote Originally Posted by US Iceman View Post
    Absolutely none. Oil will enter the evaporator no matter what you do. The only way to prevent this is to use an dry compressor (no oil in circulation).

    The oil recovery system is a simple small vessel which allows oil to drain into it by gravity from the bottom of the chiller. They are called "oil pots".

    I'm assuming the chiller is a flooded shell & tube. You did not mention sufficient details for a lengthy answer. Sorry.

    Right on US Iceman.

    I sure hope it is flooded as DX just will not work at these levels on NH3. As for the comment made to not recover the oil in the evaporator or condenser, I do not know the reasoning behind this. We as a standard build flooded ammonia chillers to the temperature levels discussed her. They all get a settling leg on the chiller and a heated oil pot connected to the leg. Oil has a SG of 0.9 to slightylu over 1 in some cases and ammonia is closer to 0.6. Even at lower temperatures, in a still area, th eoil drops to the bottom and migrates to the oil pot. Avery few days, turn off the drain to the pot, leave the vent line open and turn on the electric heater. The ammonia boils off, the oil remains behind and is warm enough to pressurize or pump back to the compressor.

    Also, need a very tight piping systems, seal-cap valves and good purger to remove the inerts. I'd suggest the Hansen Auto Purger Plus.


    US, were you at the RETA Convention in Arlington, Texas last week?

    Ken
    Last edited by TXiceman; 10-10-2006 at 02:48 AM.

  17. #17
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: NH3 system for minus 40 deg c brine temperature

    Hi Ken,

    Quote Originally Posted by TXiceman
    US, were you at the RETA Convention in Arlington, Texas last week?
    No, I had to miss it. For the last several months I have been fighting a loosing battle with alligators in my effort to drain the swamps. (If you know what I mean )

    I really did want to go, but no such luck. I'm going to try for the IIAR convention early next year. As we get a little closer to this date we should touch base and see if we can meet up.

  18. #18
    Join Date
    Dec 2007
    Location
    Nebraska
    Age
    76
    Posts
    25
    Rep Power
    0

    Re: NH3 system for minus 40 deg c brine temperature

    If your chilling a brine I assume it is not mixed with the NH3 so your suction pressure is at least 11.7"
    the oil comes from the compressor and should be at the bottom of the intercooler and if your vessel is designed properly the oil shouldn't get to the pumps.
    Unless I am missing something you have a severe design flaw.