    Electronic expansion valve for flooded chillers



    Can we use electronic expansion valve for flooded chiller without level transmitter or level cotroller. Can we control of chiller level with super heat measurement/super heat controller?



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Electronic expansion valve for flooded chillers

    Quote Originally Posted by lowtempref View Post
    Can we use electronic expansion valve for flooded chiller without level transmitter or level cotroller. Can we control of chiller level with super heat measurement/super heat controller?
    Hi Lowtempref

    yes and no. I have one site where I used danfoss controllers, just the ordinary electronic superheat control type. WhatI do is allow the controller to control the level on superheat with a thermistor imersed in the liquid, if the thermistor circuit senses a high level I force close the electronic valve. So what happens is the chiller is normally controlled on supheat heat but if the level creeps up during low load the thermistor level control allows the chiller to pump out a little.

    Hope this helps.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    639
    Rep Power
    20

    Re: Electronic expansion valve for flooded chillers

    Sporland made a valve named a Sporlan Levelmaster. I don't know if it is still available or not.

    On a flooded evaporator, you normally run with all of the tubes submerged or wetted and a staurated suction. The only way to get superheat will be to uncover some of the tubes, which will reduce you capacity.

    It is simple enough to use a low side float control or if it is critically charged, a high side float control.

    ken

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: Electronic expansion valve for flooded chillers

    Quote Originally Posted by lowtempref View Post
    Can we use electronic expansion valve for flooded chiller without level transmitter or level cotroller. Can we control of chiller level with super heat measurement/super heat controller?

    You should be able to. The danfoss valve controls to about .2 of a deg on superheat, which means your evap is nearly flooded.

    Cheers taz.

  5. #5
    Join Date
    Mar 2006
    Location
    Greece
    Posts
    34
    Rep Power
    0

    Re: Electronic expansion valve for flooded chillers

    Hi lowtempref, I think that the best way to use an EXV on flooded type chillers is monitoring and controlling the DISCHARGE superheat with a thermistor.
    (low discharge superheat=high level refrigerant)
    Hope this helps. Dimitri

  6. #6
    Join Date
    Aug 2006
    Location
    Scotland
    Posts
    104
    Rep Power
    18

    Re: Electronic expansion valve for flooded chillers

    Quote Originally Posted by Dimitris View Post
    Hi lowtempref, I think that the best way to use an EXV on flooded type chillers is monitoring and controlling the DISCHARGE superheat with a thermistor.
    (low discharge superheat=high level refrigerant)
    Hope this helps. Dimitri
    Woah there! The only way you get low discharge superheat from a flooded evaporator is by putting liquid through your compressor - this is just what he's trying to avoid. If the compressor is a semi-hermetic you might get away with it provided the motor heat can keep the suction dry. If it is an open drive - especially an open drive recip then you are asking for trouble!

    cheers
    Andy P

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Electronic expansion valve for flooded chillers

    You can certainly monitor the discharge superheat as a means of detecting the presence of "liquid", but by no means should you be using this as a control point for a flooded chiller.