    Quality of refrigerant



    Quality of refrigerant with respect to moisture and acid content is vety detrimental for unit operation.
    I am looking for a method for determining exact moisture and acid content in ***** at site. Kindly enlighten.



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Quality of refrigerant

    .

    There are degrees of exactitude.

    Commercially produced indicators that you can use at site are unlikely to provide the accuracy to determine a precise level of contamination.

    I would venture that this can only be achieved with a laboratory test of a sample in both phases, liquid and vapour, together with an oil sample.

    Most of the major refrigerant suppliers will be able to analyse samples – though it is probably very costly – hence your question.

    .