    Frozen suction line



    Went to look at a Mitsi Elec MUZ 09 (YV Inveter) which was underperforming.
    Cool mode; no temp difference whatsoever with indoor air on on/off.
    Outside put gauges on, (410a) head pressure was 10.5bar which seemed pretty low, once comp running full speed, suction at 5-6 bar.
    Liquid line was sweating, suction line and accummulator froze over, comp. discharge pipe was not even warm.
    Clearly a problem with the charge so going to recover and weigh in correct charge but what I cant understand is if these symptoms mentioned are due to an overcharge or undercharge of refrigerant. From my experience undercharged systems seem to frost on the liquid line?
    Am I also right in saying that undercharged system will have a high comp disharge temp as it is starved of refrigerant?
    Some help much appreciated.
    Last edited by Slim R410a; 28-09-2006 at 06:44 PM.



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Frozen suction line

    [QUOTE]
    Quote Originally Posted by Slim R410a View Post
    Went to look at a Mitsi Elec MUZ 09 (YV Inveter) which was underperforming.
    Cool mode; no temp difference whatsoever with indoor air on on/off.
    Outside put gauges on, (410a) head pressure was 10.5bar which seemed pretty low, once comp running full speed, suction at 5-6 bar.
    shortage of refrigerant seems the first option to check..

    Liquid line was sweating, suction line and accummulator froze over, comp. discharge pipe was not even warm.
    Clearly a problem with the charge so going to recover and weigh in correct charge but what I cant understand is if these symptoms mentioned are due to an overcharge or undercharge of refrigerant. From my experience undercharged systems seem to frost on the liquid line?
    there is no hard and fast rule as the shortage can be from 1-100% which means various symptoms as the % changes


    Am I also right in saying that undercharged system will have a high comp disharge temp as it is starved of refrigerant?
    Some help much appreciated.
    see above. however the smaller % loss the higher the likelyhood of a H.D T occuring..

    Cheers

    Richard
    Last edited by rbartlett; 01-10-2006 at 11:41 AM.

  3. #3
    A Deeb's Avatar
    A Deeb Guest

    Re: Frozen suction line

    your unit seems to be over charge, or evaporator fan not running. mostly these to reasons makes the suction line frozen. and take a look to the return air filter. it may be too dirty need to be replaced.

  4. #4
    Join Date
    Apr 2006
    Location
    Torquay
    Age
    59
    Posts
    130
    Rep Power
    19

    Re: Frozen suction line

    Reversing valve could be stuck part way.Try measuring temp on inlet/outlets.

  5. #5
    rbartlett's Avatar
    rbartlett Guest

    Re: Frozen suction line

    Quote Originally Posted by 1torr View Post
    Reversing valve could be stuck part way.Try measuring temp on inlet/outlets.
    so how does this cause icing up..?

    cheers

    richard

  6. #6
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Frozen suction line

    Thanks for the replies.
    Filters are as new and I very doubt it is a 4-way valve problem.
    Also ran the system on heat mode along with the same split which serves another room next to it. The difference in heating performance was noticible between them, one having an air off of 45degc and the one I am working on 30degc. (22degc air on)

  7. #7
    Join Date
    Sep 2006
    Location
    italy
    Age
    53
    Posts
    93
    Rep Power
    18

    Re: Frozen suction line

    Hi mate,

    I'm new on the forum and this is my first reply.
    This behavior can be produced by a closed one circuit of your evaporator. Check if all the bending curves are wet on the left side of the evaporator.(on cooling mode).

    Also you can set it on the heating mode and if you have a closed circuit of the evaporator you will have an anormally HP(much higher than normal)

    I don,t think that is a problem with a 4-way valves because in that case you will have a HP lower than normal and a BP higher than normal.

    Best regards,

    Nicola

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Frozen suction line

    It looks like an excessive subcooling caused by too much refrigerant. Please check the liquid line temp. leaving the condenser.

  9. #9
    rbartlett's Avatar
    rbartlett Guest

    Re: Frozen suction line

    Quote Originally Posted by NoNickName View Post
    It looks like an excessive subcooling caused by too much refrigerant. Please check the liquid line temp. leaving the condenser.

    there is no liq line leaving the condenser...


    cheers

    richard

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Frozen suction line

    Quote Originally Posted by rbartlett View Post
    there is no liq line leaving the condenser...


    cheers

    richard
    No? Is it magic?

  11. #11
    rbartlett's Avatar
    rbartlett Guest

    Re: Frozen suction line

    Quote Originally Posted by NoNickName View Post
    No? Is it magic?
    the expansion device is in the condenser..

    cheers

    richard

  12. #12
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Frozen suction line

    Well, the condenser condenses and the evaporator evaporates, whatever the cycle is.

  13. #13
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Frozen suction line

    Right!

    If it is a heatpump there will be an expansionvalve situated in the outdoor unit along with a fourwayvalve.

    Most of these units will come prefilled up to 10m of single piping length. if the unit's are closer to each other the charge will be too high!

    If it's futher away, more charge will be required and if i remembered correctly the units shouldn't be futher apart than 20 m

    Give us the suction pipe temperature, suction pressure,
    liquid pressure and temperature, head temperature and if possible discharge pressure
    Last edited by Lowrider; 02-10-2006 at 09:19 PM.

  14. #14
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Frozen suction line

    Quote Originally Posted by rbartlett View Post
    the expansion device is in the condenser..
    richard
    Every condenser has a liquid outlet, what you meant I suppose was an expansion device in the outdoor unit but not in the condenser.
    And if the expansion device should be soldered direct in the last tube, event then there's a liquid line, perhaps only an inch long but there's one.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  15. #15
    Join Date
    Jul 2006
    Location
    Australia
    Age
    52
    Posts
    28
    Rep Power
    0

    Re: Frozen suction line

    hhahahha richard you right 100% gas leak!!!

  16. #16
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Frozen suction line

    Quote Originally Posted by NoNickName View Post
    No? Is it magic?

    No not magic.
    But on an air cond the liquid supply line is actualy full of saturated liquid that is being transfered to the evap so the heat transfer process can begin. That is why the smaller of the two lines is insulated, it prevents the heat transfer begining too early and therfore no liquid being left for the evap.
    The expansion device is on the outlet of the cond unit.

    Cheers taz.

  17. #17
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Frozen suction line

    Thanks taz. I'm an RE since ages, I know how HPs work. My comment was ironic.

  18. #18
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: Frozen suction line

    Quote Originally Posted by NoNickName View Post
    Thanks taz. I'm an RE since ages, I know how HPs work. My comment was ironic.

    opps I missed it sorry

    Cheers taz.

  19. #19
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: Frozen suction line

    Hi, If the unit is a Multi-split heat pump unit, then there will be one reversing valve but each circuit will have its own expansion device....on modern higher spec units these tend now to be electronic expansion valves rather than fixed orifice devices..

    Surely...the symptons suggest that one valve could be faulty (stuck open) causing a low pressure drop across EEV, therefore suction side (pressure & temp) will not be low enough, and there will be an excess of refrigerant on this circuit causing the frosting back. There will be less heat load on the system which will also lower the discharge pressure.

    The other unit on the system might still work to a degree but could be partially starved when they both try to run together.

    Needless to say with only one reversing valve both indoor units have to be selected to the same 'mode'.

    Adrian

  20. #20
    rbartlett's Avatar
    rbartlett Guest

    Re: Frozen suction line

    Quote Originally Posted by wolf View Post
    hhahahha richard you right 100% gas leak!!!

    thanks ;-)

    cheers

    richard

  21. #21
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Frozen suction line

    Just found this thread, didnt realise I did not update.

    Recovered charge, was found to be exact (holding charge plus what we added for 15m run) so no shortage of gas.
    On futher inspection of the indoor unit, found part of the plastic fan blade to be smashed, so around 30% of the blades were missing i.e. some idiot had been poking things in the wall mount, breaking the blades

    Fitted new fan rotor, system pressures back to normal and suction line had a nice sweat.

    However, got called back a few weeks later to 'room not cooling down and units leaking'.
    Went into room, room temp about 25degC, with the wall mount running flat out with a setpoint of 16degC. Louvre blades on wallmount had excessive sweating causing water to drip.
    These were installed in 2004 by myself, back then I was apprentice so didnt know much about sizing etc but turns out that we fitted them as subbies for a building company and thier 'architect' had claculated the load for the room at 2.5kW. (nominal) Room size approx. 6m x 4m, 18-20 people, (councelling room) three large south facing windows! Working this out now I'm getting at least 7kW!
    Spoke to Mitsi they said the sweating louvres were a sign of undersized system.