    oil not returning on 15 hp med temp refrigeration



    i have a problem with existing unit 15 hp 3 evap coil 3 tx valves 4ton external equillized suction from condensing unit on roof 1 3\8 liquid 5\8 reduced to 1 1\8 to one coil 7\8 to second coil oil not returning since we changed compressor copeland semi
    10 super heat but noticed suction pressure 55 psig at each coil but at compressor 45 psig there is a 10 psig drop and oil not returning to compressor
    changed oil in new compressor to mineral using r22 ***** 35 years in the trade my first defeat this system is a flooded system head master set at 200 psig sight glass clear no hunting or liquid flooding
    Last edited by circa1; 27-09-2006 at 02:26 PM.



  2. #2
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: oil not returning on 15 hp med temp refrigeration

    Hi Circa 1

    Have you changed it too R22 please clarify what refrigerant it was on before.

    Regards
    LRAC

  3. #3
    circa1's Avatar
    circa1 Guest

    Re: oil not returning on 15 hp med temp refrigeration

    r22 before and after no change

  4. #4
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: oil not returning on 15 hp med temp refrigeration

    Hi Circa 1
    On a system this size is there an oil seperator fitted.

  5. #5
    circa1's Avatar
    circa1 Guest

    Re: oil not returning on 15 hp med temp refrigeration

    no oil separator 5 c box med temp

    not needed

  6. #6
    Join Date
    Jul 2006
    Location
    New Berlin, Wisconsin, USA
    Age
    65
    Posts
    57
    Rep Power
    18

    Re: oil not returning on 15 hp med temp refrigeration

    Was there a viscosity change?

  7. #7
    circa1's Avatar
    circa1 Guest

    Re: oil not returning on 15 hp med temp refrigeration

    no modifications made compressor only changed tx valves no difference suppeheat 12 f

  8. #8
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: oil not returning on 15 hp med temp refrigeration

    As per your initial statement you said the condensing is located on the roof . Where are the evaporators located and what are the vertical heights of the suction and the liquid lines. Have you provided any loops in the liquid line. What are the sizes of the liquid lines and the capacities of the individual evaporators.

    Although at 5 Deg C Te Oil Separators are not required but in such installations where the condensing units are located higher than the evaporators, using oil seperators will be better. Moreover the piping has to be laid properly designed.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: oil not returning on 15 hp med temp refrigeration

    A couple of questions...

    Is the oil level slowly decreasing in the new compressor crankcase site glass?

    Where are you measuring the superheat? At the evaporator outlets or at the compressor suction?
    Last edited by US Iceman; 28-09-2006 at 11:25 PM. Reason: spelling

  10. #10
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: oil not returning on 15 hp med temp refrigeration

    i have a problem with existing unit 15 hp 3 evap coil 3 tx valves 4ton external equillized suction from condensing unit on roof 1 3\8 liquid 5\8 reduced to 1 1\8 to one coil 7\8 to second coil oil not returning since we changed compressor copeland semi
    I'm sorry. 1-3/8 liquid. You mean suction with a 5/8 liquid, correct? So you are feeding a 7/8 suction from the last coil to feed liquid, 1-1/8 after passing the second coil to feed liquid and 1-3/8 suction after the last coil to feed liquid.. and this 1-3/8 suction is trapped before rising to the compressor unit? Original piping?

    45 psig there is a 10 psig drop and oil not returning to compressor

    A lot of good questions being asked in this discussion. Here's my best guess not knowing those details. You could have a horizontal suction pipe that is either sagging or pitched incorrectly that is oil laden, causing the pressure drop and lack of oil return.

  11. #11
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: oil not returning on 15 hp med temp refrigeration

    Are all the tev's working? Ive seen low oil problems on ice builders when one of the tev's was faulty. They can flow enough to let refrigerant/oil in but theres not enough velocity to carry the oil back out of the evaporator. Ive also seen pipes squashed flat due to ice causing the same problems. Have you changed the oil from ester to mineral?

    When i did a lot of CFC conversion work for my old boss, the guys from castrol said the best refrigerant/oil combination was CFC/HCFC and ester oil. Ester oil lubricates better than mineral, and if you get any metal to metal contact the chlorine reacts with the hot metal to sort of case harden it.

    cheers Jon

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: oil not returning on 15 hp med temp refrigeration

    Quote Originally Posted by circa1
    oil not returning since we changed compressor copeland semi
    This was the original statement.

    If indeed there was no oil return problem before the compressor was changed, why would it start after the compressor is changed? If this holds true, I'd say the replacement compressor is a smaller displacement which establishes lower suction line velocity.

    On the other hand, perhaps this condition existed before the compressor was changed, and this was the cause of the initial failure.

    Dan was going with the same line of thought I was considering... oil logging in the system = no oil return & higher suction line pressure loss.
    Last edited by US Iceman; 01-10-2006 at 03:45 AM. Reason: editing

  13. #13
    Join Date
    Sep 2005
    Location
    UK
    Posts
    33
    Rep Power
    0

    Re: oil not returning on 15 hp med temp refrigeration

    Hi If the CU is on the roof then the evaporators are obviously lower than the CU. From the terminology used I am assuming that the system is cooling only. If so you should put some oil traps in the suction line or not only will you burn out compressors but eventualy you'll reduce the efficiency of the system as the evaporators will fill up with oil
    Regards Frostycold

  14. #14
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: oil not returning on 15 hp med temp refrigeration

    hi mate, was the compressor a new unit or rebuild?,if the later it might be just a bad one causing the problem,i would ditch the mineral oil out of the system and use a good semi synthetic that will mix with the residual mineral left trapped,also i would fit a seperator for good measure,as you know sometimes a change of compressor can bring more problems.

  15. #15
    Join Date
    Oct 2006
    Location
    Bucks, U.K.
    Age
    71
    Posts
    604
    Rep Power
    18

    Re: oil not returning on 15 hp med temp refrigeration

    Hi,
    All large R22 systems I've worked on have had oil separator fitted, even where theres very little difference in height between evaps and condensing unit. R22 is not very miscible with mineral oil. How about using Alkyl Benzyl oil as its recommended for use with a lot of R22 based 'drop ins'.

    Cheers Adrian