    Extrapolation #2



    Now the customer wants me to survey processing from 45degF to 36degF. So prior to going out and re-do the whole thing with a new survey, I'm gonna try to plug it with Fridgetech's formula:

    Safety factor is NOT included

    Processing Room

    ProductLoadOld = 14,700 btuh
    XmissionInfiltMisc LoadOld = 151,200,000 btuh

    45 RoomTempOld / 36 RoomTempNew * [151.2K XmissionInfiltMiscOld] = 189,000 btuh

    [40 ProdArrivTempNew - 36 RoomTempNew] / [50 ProdArrivTempOld - 45 RoomTempOld] * 14,000 ProdLoadOld = 14,000 btuh

    Load A + Load B = 203,000 btuh @ 18 hrs runtime

    Product into processing is to come from 28degF cooler, but I must apply SOME load for product.

    I'm heading out to take measurements, again.



  2. #2
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Just got back.

    Room is 38ft(W) x 45ft(L) x 12ft cieling, 8in concrete with 3in polurethane, concrete floor. wall 1(L) adjoining 28degF cooler, Wall 2 (W) adjoining (50% 75degF occupied space and 50% 36deg Dock) Wall 3 (L) adjoining 75degF occupied space, and Wall 4(W) adjoining 90deg dry storage

    30 horsepower equivalent (processing equipment)
    40 people
    All dock doors into equivalent or lower temp rooms EXCEPT one man door into occupied space
    140,000 pounds beef entering from 28degF cooler

    computer program results:

    Wall heat gains = 27,320 btuh
    Sens. infil. = 3,180
    Lat inf. = 1,518
    Prod Load = 0
    Misc. Load = 174,250 btuh

    total @18hr runtime = 206,268

    The Fridgetech Formula (you otta' Trademark that) = 203,000 btuh


    For the new application, I will adjust the system capacity to 16 hours runtime for assured off time for defrost.
    Last edited by herefishy; 02-03-2002 at 05:05 PM.

  3. #3
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    Originally posted by Fridgetech


    That expression would only be valid if we were starting with a temperature of 0°F and the load would be heating.

    I don't understand that.

    Are you suggesting "NewTemp/OldTemp? That would give a multiplier of (.8), and decrease load 20%.

    Hey! This don't work at Freezer from 0deg to -10deg.

    Now this seems to be more coincidental. You're messin' with me, aren't you!?

    One thing I did do, however in the freezer situation, was since the product load increase is based on the ratios of dT of the product (old and new) which is somewhat imperical, I applied that percentage of change to the old Load. That seemed to get it into the ballpark... I'll need to consider that some more.......
    Last edited by herefishy; 08-03-2002 at 11:34 PM.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •