Reverse fan defrost
Hi,
Having glycol cooler with separate cooling and heating coils, what do you think to use reverse fan blow for defrosting. Inlet glycol temp -9/-8C.
It is for vegetable cold store temp 0C/70%RH or 4C/85%RH
Best regards, Josip
It's impossible to make anything foolproof because fools are so ingenious...
Don't ever underestimate the power of stupid people when they are in large groups.
Please, don't teach me how to be stupid....
No job is as important as to jeopardize the safety of you or those that you work with.
-
24-09-2006, 03:15 PM #2
Re: Reverse fan defrost
Hi Josip,
I think the lowest coil temperature I would be comfortable with for air defrost would be about -1.6 C (29F). During normal operation at a reasonable load, the coil return bends will frost but the coil face seems to stay wet. As the load decreases the coil face tends to form some light frost which melts relatively quick (at least on refrigerant coils).
In this respect glycol coils may be able to tolerate slightly lower coil temperatures since during defrost the glycol will not evaporate like a common refrigerant (and help to keep the coil cold).
The air defrost would certainly help to maintain the humidity though.