    New install with pump down??



    Hi I am supposed to be fitting a remote unit to a new caravell chilled display,now i have been working on air con for the past 5 years and havent installed fridge for some time.
    My only worry is do I use a pump down system or put a contactor on the outdoor and wire the control through the controller.
    Also what is the best condensing unit to go for, a unit with everthing all included like a L'unite Silensys are a normal unit and fit it all on site.This system is on R404a and is evaporating at -7 and has a 3 kw coil.Thanks for reading



  2. #2
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: New install with pump down??

    Hi Justchillin'

    Post more details on site requirements-a standard pump down system is one of the easiest and effective methods.

    Kind regards Mark

  3. #3
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: New install with pump down??

    Quote Originally Posted by MarkFiddy View Post
    Hi Justchillin'

    Post more details on site requirements-a standard pump down system is one of the easiest and effective methods.

    Kind regards Mark
    With pumpdown no control wiring is need from indoor to outdoor just a mains to the condensing unit isolator.
    We use maneurope condensing units on such applications and find them relyable in service.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes: