    sizing up an orifice



    am i correct in saying if i was to size up an orifice i would have to take into consideration

    evap size
    capacity
    compresor size
    refrigerant type
    pipe sizes suction and liquid line

    this is to clear up an argument at work with another mechanic.

    if i am incorrect please advise.



  2. #2
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: sizing up an orifice

    In sizing the orifice which I presume is for the selection of the TEV, you have to know the following details.

    Refrigerant,Evaporator Size, Liquid temperature approaching the TEV, Suction Temperature. Pipe sizes have nothing to do with the selection of the TEV.

  3. #3
    Join Date
    Sep 2005
    Location
    Northern Ireland
    Age
    50
    Posts
    8
    Rep Power
    0

    Re: sizing up an orifice

    you need to know the evaporating temperature, duty and the refrigerant type for normal selection of a valve

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: sizing up an orifice

    Needed capacity, refrigerant, evaporating pressure, DP over the valve and amount of subcooling.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Jun 2006
    Location
    jiansu
    Posts
    38
    Rep Power
    0

    Re: sizing up an orifice

    orifice diameter =0.5X(F/N)^(1/2)
    F is evaporate area m^2
    N is the number of evaporate's tube

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: sizing up an orifice

    You don't mean this, don't you?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: sizing up an orifice

    If you are on service call and you have a faulty expansion valve on a previously working piece of equipment you dont always have the evaporator data so what I do is obtain all the information from the condensing unit, identify gas type, operating temperature of room, evaporating temperature and identify the duty of the condensing unit, with that same duty I then look down the selection chart for the expansion valves, once the valve is fitted you will soon see by what your gauges are doing if this selection is satisfactory.

    We had a grade 1 engineer on the last company that I worked for who could not size up a valve, instead he always insisting that it was a design engineers job and not a service engineers job, absolute nonesense. Too many people dabble with refrigeration equipment who shouldn't.

  8. #8
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: sizing up an orifice

    Quote Originally Posted by Andy W View Post
    If you are on service call and you have a faulty expansion valve on a previously working piece of equipment you dont always have the evaporator data so what I do is obtain all the information from the condensing unit, identify gas type, operating temperature of room, evaporating temperature and identify the duty of the condensing unit, with that same duty I then look down the selection chart for the expansion valves, once the valve is fitted you will soon see by what your gauges are doing if this selection is satisfactory.

    .
    You should always size the valve using the duty of the condensing unit NOT the evaporator. That way you will never over load the condensing unit.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  9. #9
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: sizing up an orifice

    Quote Originally Posted by Andy View Post
    You should always size the valve using the duty of the condensing unit NOT the evaporator. That way you will never over load the condensing unit.

    Kind Regards Andy
    Very true as the evaporator can have a lot of variables that as a fact a lot of engineers would not know or understand unless you have experience in selecting evaporators, just look at an evaporator chart for example, the same evap will give numerous duties at different evaporating temperatures and different td's.

  10. #10
    DANIEL ARYEE's Avatar
    DANIEL ARYEE Guest

    Re: sizing up an orifice

    Quote Originally Posted by Samarjit Sen View Post
    In sizing the orifice which I presume is for the selection of the TEV, you have to know the following details.

    Refrigerant,Evaporator Size, Liquid temperature approaching the TEV, Suction Temperature. Pipe sizes have nothing to do with the selection of the TEV.
    DEAR FRIEND, I THINK THE MOST IMPORTANT THING IS THE EVAPORATOR SIZE. IF YOU CHOOSE AN OVERSIZE ORIFFICE, THEN LIQUID WILL ENTER THE COMPRESSOR AT ALL COST. IT WILL EVEN BE BETTER IF THE EVERPORATOR IS A BIT BIGGER THAN THE ORIFFICE. THIS WILL ALLOW WELL SATURATED VAPOUR TO ENTER THE COMPRESSOR. REMEMBER THE COMPRESSOR IS NOT A LIQUID PUMP, BUT A VAPOUR PUMP.

  11. #11
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: sizing up an orifice

    Quote Originally Posted by DANIEL ARYEE View Post
    DEAR FRIEND, I THINK THE MOST IMPORTANT THING IS THE EVAPORATOR SIZE. IF YOU CHOOSE AN OVERSIZE ORIFFICE, THEN LIQUID WILL ENTER THE COMPRESSOR AT ALL COST. IT WILL EVEN BE BETTER IF THE EVERPORATOR IS A BIT BIGGER THAN THE ORIFFICE. THIS WILL ALLOW WELL SATURATED VAPOUR TO ENTER THE COMPRESSOR. REMEMBER THE COMPRESSOR IS NOT A LIQUID PUMP, BUT A VAPOUR PUMP.
    Sorry Daniel I would size the oriface to suit the compressor NOT the evaporator.If your evaporator does 6kW at the TD (Say 6K) and your compressor does 5kW at same TD, you need to fit an oriface to suit 5kW not 7kW, either that or the compressor is overloaded OR you evaporation is too high and your loose a large proportion of your Latent cooling AND you overload the compressor(more often on a condensing unit where the condenser is one fits all).

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  12. #12
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: sizing up an orifice

    Dear Andy,

    For selection of the orifice of the TEV . I feel that the size of the Evaporator plays the important role. TEV is a part of the whole system. While designing and selecting the refrigeration system, we have to balance all the components such as the Compressor, Condenser ( based on the Total heat Rejection of the system ) the Evaporator and the Controls. Some people tend to not to calculate the details and install units which do not match. This causes failures in the systems and one tend to blame either the Compressor or the TEV. This is wrong. Condensing unit is important as when you size the TEV and the orifice , among the other factors as stated by me , the temperature of liquid approaching the TEV is also considered. But then the capacity of the Evaporator has to be taken into consideration. I have been following this system of selecting the components and ( God Willing ) till now have never faced any problems.

    With best wishes,
    Last edited by Samarjit Sen; 28-09-2006 at 07:06 PM.

  13. #13
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: sizing up an orifice

    If you are designing the coil to start with, you need to first determine the proper circuiting. Now you neeed to look distributor tube length and diameter. To select the proper orifice, you need to first balance the condensing unit with the coil and get the load and ET at the balance point. Use this load and ET as well as CT for the design point and select an orifice and TXV to all match. Now comes the trick, rerun the selction and allow the CT and liquid temperasture to drop to the lowest ambinet conditoins you pan to run. The pressure differentila is lower, but the subcooling is much higher, especially if you are flooding the condenser coil. You nay find the orifice too large due to the subcooling and have to take a bit more PD at the orifice when you are at design.

    Get a copy of the SDporland program and run a few cases at design and at low ambient design.

    Ken

  14. #14
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: sizing up an orifice

    Quote Originally Posted by Samarjit Sen View Post
    Dear Andy,

    For selection of the orifice of the TEV . I feel that the size of the Evaporator plays the important role. TEV is a part of the whole system. While designing and selecting the refrigeration system, we have to balance all the components such as the Compressor, Condenser ( based on the Total heat Rejection of the system ) the Evaporator and the Controls. Some people tend to not to calculate the details and install units which do not match.
    With best wishes,
    I would say any system is a compromise. But the balance point in the system is acheived by basing the TEV selection on the condensing unit capacity. The evaporator has to be selected for the correct duty, or as near as possible

    The governing factor is the condenser/ compressor capacity not the evaporator


    Kind Regards Andy