Page 1 of 2 12 LastLast
Results 1 to 50 of 63
Thread: Server rooms.
    Dec 2004
    Australia
    52
    519
    Question Server rooms.
    G'day all
    Was wondering if anyone can give me an explanation as to why you can not use Daikin inverter wall mounts in computer or server rooms, where there is going to be a call for cooling even if the outdoor ambient is low.
    I remember reading or hearing somewhere that in low ambient conditions on cooling that the compressor speed is restricted, but can not think of why.I know that if the indoor thermistor senses a pending freeze up of the indoor unit that this will cause the compressor speed to drop in an attempt to combat it, but I am sure there is another reason.
    Thanks in advance.
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    A speed reduction while ambient t is low will cause a further reduction in condensing pressure. Condensing fan speed must be reduced instead.
    Also, this solution is pretty much energy-hungry. A Free Cooling (shelter or chilled water) would be much better.
    Besides, a split unit will not control humidity, while a close control will.
    Sep 2006
    New Zealand
    54
    Smile Re: Server rooms.
    I currently work on computer server rooms that have inverter units in them and find they work very well.Obviously a specialist computer room a/c unit would be the best option but a lot of small companys dont have the funds to justify the expense.The inverter models tend to work well due to the fact that they hold the room at a consistent temp and and are cheap to run because they are variable speed.You will also find that the condenser fan cycles in low ambients and that they are less prone to outdoor icing because they are only just running, if you know what i mean.The other bonus we have found is that the building owner can buy two units for the price of a speacialist system and have 100% back up in the case of a unit failing.
    Hope this helps.
    Apr 2001
    2,099
    27
    Re: Server rooms.
    Quote Originally Posted by NoNickName View Post
    No Nick
    Please could you tell me what is a close control system
    Thx
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    close control units, aka CCU, are upright standing cabinets, from 5 to 100kW of cooling capacity, having 1 or 2 dx circuits, either air cooled or water cooled, or with chilled water coil.
    They monitor temperature and humidity, and are able to cool, heat, humidify and dehumidify.
    Heating is done via electric heaters, hot gas injection or warm water.
    Cooling plus heating performs dehumidification.
    Humidification is done via an immersed electrodes boiler with steam distribution in the air flow, or by other means of water dispersion, either cool water or hot water. Hot water is preferred to avoid bacteria proliferation.
    Eg of close control unit
    Air discharge can be from the top (aka as OVER when no false floor is available) with front air intake, or bottom (aka as UNDER) with top air intake. In the image an OVER unit is shown.
    Few units are so called "displacement CCU", with top air intake and front air discharge.
    Shelters units are not strictly CCU, but they have an air damper to provide free cooling.
    Free cooling can also be achieved with water cooled dx units, and diverting cold water to a water coil instead than into the condenser in winter time.
    Oct 2003
    5,630
    34
    Re: Server rooms.
    We have some standard AC's running in server rooms in a hospital, in a big factory, in a telecoms company...and had never had problems with it.
    One is even running in a company who's running the telecoms service in Brussels for the Belgium Parliament.
    Nowadays computers can work within a wide range of humidity and the time that humidity had to be kept at a certain high level is almost nonexistent.
    This was mainly a demand to prevent static electricity in the machines.
    If you see in what a rough industrial environment some computers have to work these days.
    Dec 2005
    Zagreb
    190
    Talking Re: Server rooms.
    No electronic cant work in all conditons.They can but they life is then much shorter becose electric condenser react very badly to dry envirement.They simply lose they capaciti.Also the circuit board reacts badly to dry air.Some versions of EPROM start to mulfunction on long period dry air condition.Belive i know we maintain sites for mobil phone company.
    Renato
    Apr 2001
    2,099
    27
    Re: Server rooms.
    Thank you Nick for your posting
    Its very informative
    Best regards
    Abe
    Jun 2006
    British West Indies
    543
    Re: Server rooms.
    here is a redundant pair of 40 ton units,
    they failed capitalize on the built in piping chase of one
    Oct 2003
    5,630
    34
    Re: Server rooms.
    These are installed in the VRT, the digital center of the Belgium television broadcating company.
    Oct 2001
    Nottingham UK
    5,668
    Re: Server rooms.
    Quote Originally Posted by Temprite View Post
    G'day all
    Thanks in advance.
    I also heard of this but didn't get the full explanation. From memory it was due to a batch of problems associated with the control logic in the electronics and the high sensible loads associated with Server room applications.
    I think Daikin had a lot of complaints about units failing to control properly in these environments.
    Apr 2006
    Brisbane, Australia
    28
    Re: Server rooms.
    G'day mate.
    I'm not 100% sure about wall mounted Daikin's used for server/computer room application but it is possible to use Daikin FFB (600 by 600) R410A skyair cassettes for this application. It is however necessary to change a field code setting to alter the freeze prevention parameters due the low humidy of this appication. I guess this would apply for the wall mount FCU's as well.
    Apr 2006
    Essex
    55
    21
    Re: Server rooms.
    In my experience the last thing you would require in a dedicated data centre / comms room would be a potential source of water above servers which is exactly what a cassette is - be it failed lift up pump or coil icing over due to high heat loads especially with the new generation of 'blade ' servers which can go up to 7-9 kw per cabinet. Also bear in mind close control units generally offer a lot higher filtration qualities then a split (disposable EU spec box filters) and put the cooling where its required - say under the floor to be pulled through the cabinet via its own fan module. Im prepared to be convinced otherwise but horses for courses - 24/7 365 days a year operation in critical applications is not for split a/c but dedicated close control equipment.
    Andy
    Oct 2001
    Nottingham UK
    5,668
    Re: Server rooms.
    Quote Originally Posted by Ross View Post
    They are called FFQ cassettes in the UK.
    You cannot alter the operating parameters on wall fan coils with infra red controllers, only on units with hard wired controllers and these start at size 7kw upwards
    Feb 2005
    Aberdeen
    48
    168
    Re: Server rooms.
    I encountered a problem with a wall mount FAYP100 (non-inverter) once. Unit was installed in a small server room. The unit kept frosting back to the compressor and at one polint had lost 2 compressors within 4 weeks.
    I ended up sticking a couple of kettles into the room to increase the humidity and this seemed to do the trick.
    In the end a remote sensor was fitted in another part of the room and a few jiggery pokery of the settings was carried out. I was told by Daikin that they sell units designated for server applications, but nothing was ever followed up. Anyone know of this?
    BTW took the kettles out of room!
    Jase
    Mar 2006
    Glasgow, Scotland
    177
    Re: Server rooms.
    The problem with using the split type units in a server room is that they are not designed to operate in low latent heat applications i.e server rooms. This was a problem with Daikin units and as already pointed out the units would go out on freeze protection and by the time it reset the server room would be over heating. Daikin started to change the control strategy of the B series 407c Sky air units, which entailed changing PCB's and field settings. The new Sky air range RZQ units offer what Daikin call EDP setting (Electronic Data Processing) Setting which alters freeze protection settings to prevent any problems.
    May 2006
    Sussex
    362
    21
    Re: Server rooms.
    The Daikin design change is very interesting. (Strange they did not start with the wall-mount, which is more appropriate in server rooms.)
    Before reading Puddleboy’s post, I would have said that the reason one would not (ideally) select a split for a Server Room is that it will drag the RH right down, often below 50%. You can see this best on a psychometric chart.
    And as stated above, electronic equipment does not like a very dry space, preferring 50-75% RH, as a generality.
    The alternative is a more expensive chilled water system.
    Jun 2006
    British West Indies
    543
    Re: Server rooms.
    Out of curiosity, server rooms are usually almost all sensible cooling. Maybe some latent load from ventialtion air.
    So when you have a big sensible load, you need a very high air flow rate per unit cooling. In imperial units, it could be 600 to 700 CFM per ton and it works the best when it is a blow through process, allowing the cooling coil to remove the blower heat.
    Something that does not move this amount of air and is draw through is forced to over 'dehumidify' the air in an attempt to control temperature.
    Not always the best bang for the buck, although every leibert I have seen is draw through.
  19. #19
    Apr 2006
    Brisbane, Australia
    28
    Re: Server rooms.
    Hi guys.
    What about the new Daikin Ururu / Sarara for computer room / server room applications? Should be now available from Daikin UK but not sure about Daikin Oz Temprite. A much cheaper alternative to other specialised systems. Should be a info on the Daikin UK website.
  20. #20
    Dec 2004
    Australia
    52
    519
    Re: Server rooms.
    Thanks for all the responses everyone.
    The reason I started this thread was because someone I know was looking to put an inverter wall mount in a computer room and I mentioned to him that it was not satisfactory for that application, but could not remember exactly why.
    Instead of a wall mount they put in a ceiling cassette inverter model.Have not spoken to him recently but I assume all was ok
    Hi guys.
    I dont think this unit is available in oz.
  21. #21
    May 2006
    Sussex
    362
    21
    Re: Server rooms.
    Regarding the “Ururu Sarara”, the equipment has a design problem that needs sorting out yet. ie, these units will not cool below 21 degrees C (making them useless for Comms Room applications). However, there will be a revision to the outdoor unit in January that will enable the condenser to cool down to minus-10 degrees C, so that should resolve this issue.
    Units only come in the following sizes 2.8kW (£732 trade), 4.2kW (£852 trade) and 5kW (£1133 trade).
  22. #22
    Dec 2005
    Zagreb
    190
    Emerson-Liebert Hiross SE+SC10 is best solution.Or TD10 there are some mount 1998 in my region.Carly compressors,alco TEV,realy good design.Controls humidity,fresh air and do everyting you want.I have 75 machines on maintance and replace 3 compressors in 4 years.
    Best regrds,
    Renato
  23. #23
    Apr 2006
    Essex
    55
    21
    Re: Server rooms.
    So let get me this straight....
    to cure your low humidity issues in a server room you ducted untreated / unfiltered air straight in?
    What are we dealing with here? Cooling a small room with a couple of comms cabs via everyday split a/c or proper close control, there is a difference.. temp control / humidity control via hum/dehum
    And also regarding the Liebert comment fine but you obviously havent worked on Isovel products - designed by an engineer for engineers - Airedale /denco etc etc all make or have made worthy products particulary when based round the maneurop MT/MTZ compressor which can take a huge amount of abuse when compared to copeland scrolls in the same application
  24. #24
    Feb 2005
    Aberdeen
    48
    168
    Re: Server rooms.
    Quote Originally Posted by quiksilva View Post
    You will probably find that Airedale are using copeland scrolls now! What advantages are there with the Isovel equipment?
    Jase
  25. #25
    rbartlett's Avatar
    rbartlett Guest
    Re: Server rooms.
    We have just lost 2 out of 3 wall mount 10kw Daikin cooling only non inverter systems -compressor seized.
    I have had a 1/2 hr chat with Daikin technical and the latest is the you should fit INVERTERS to server rooms but make sure you adjust the PCB for data room application.
    The old 407a inverters were the ones which caused problems but these are obsolete so that 'no inverter' advice is out of date.
    The problem of non inveters is exacerbated by the fact that on 410a units Daikin removed the accumulators and hence any prolonged low temperature running increases the risk of liq return back and washing out of the oil .
    We are currently considering a swap out to RZQ inverters to get over this.
    However some advice for those with non inverters
    1. if pipe length is less than precharged max REMOVE a % to lower the risk of flooding
    2 Ensure the controller cannot be set lower than 20 but ideally 21/22
    3 fit a suction accumulator
    Richard
  26. #26
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    What about fitting real full-function close control units, instead than those low cost consumer wall mounts?
  27. #27
    rbartlett's Avatar
    rbartlett Guest
    Re: Server rooms.
    firstly you answered your own question but frankly 99% of rooms simply do not need anything like the old computers did. I can remember looking after a room with 6 big Lieberts cooling the air and the computer had a 15 stage water cooler for it's insides.
    Frankly it's the air conditioning which seems to suffer not the servers now. The days of close control as a necessity has pretty much gone and only those old fashioned computer guys who think a room should be kept at 16 deg's C are left. The UK had a big market in the manufacturer of CC units -denco,Isovel etc and most have long gone.
    Times have changed and kit moves on specialist computers like the Kray may need a proper climate but these rack server blades are pretty robust.
    I think 22 c is more than adequate for most rooms with good air circulation and if we could only convince Mr IT man our a/c would prefer it too..!!
    Richard
  28. #28
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    That doesn't answer my question. Or, put it in other words: why should anybody bother intaking fresh air for preventing coil freezing, while more professional units will not suffer from absence of latent heat. CCU are already designed for all sensible. I'm afraid it is not Mr IT's fault, it is Mr RE who wants to simplify because lacking proper know how.
  29. #29
    Oct 2006
    Bristol
    11
    Re: Server rooms.
    A Server room with any ac unit in with no fresh air or humidification will have a low humidity level and if you look at the design spec most ac units these will not work well under 35-40% RH. If you look at the Daikin non inverter equipment depending on the gas will have freeze up problems under these humidity levels as it floods the evaporator sending the unit into a frost protection and the possibility of liquid flooding back to the compressor. If you use an inverter type unit (R410A) this will help by reducing compressor and fan frequency in doing so reducing capacity to reduce the last two problems but where you might have a 7kw unit it is more likely to work as a 5kw unit.
    Solutions don’t use ac units in comms rooms, make sure fresh air is supplied to increase humidity, increase the humidity, and tell the end-user not to run ac units below 22C.
    There is a code for Daikin to stop the end user turning the controller below 20C on new kit setting 14-7-02.
    I hope this helps.
  30. #30
    Apr 2006
    Essex
    55
    21
    Re: Server rooms.
    In all the posts so far regarding splits dont tell me they can approach the filtration levels dedicated CCU with disposable EU spec filters achieve. To be honest i havent noticed data centres ripping out ccus to go down the inverter split route - as mentioned in one of the above posts no accumulators on the latest 410 units etc do this and they will work sort of... sorry i dont buy into it, yes a split will cool a room down and with some fancy programming may manage humidity to some extent but a full house CCu with dx/chilled water/water cooled/ free cooling options is a damn site safer bet, reports of their demise may be premature
  31. #31
    Oct 2006
    Bristol
    11
    Re: Server rooms.
    without doubt the correct unit for the job. but if it is a small customer without out that sort of money to spend what is the sales person going to sell?
  32. #32
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    Well, I've been reading threads complaining about customers not buying the appropriate equipment for their needs. What about starting advising the CCU to be the right solution for their problem? Then, he will be the only to blame whether will opt out for anything inappropriate...
    A DX CCU of 5kW or 7kW will cost approx 2000 euro more than a consumer split. What about teaching the sales person what ROE is?
  33. #33
    Oct 2003
    5,630
    34
    Re: Server rooms.
    Nobody mentioned - as far as I have read this thread - the selection of a one size bigger indoor unit then the outdoor unit.
    Had a similar experience in the past like Richard with 5 Lieberts in a big computer room of a company almost in my backyard (+/- 2500 peoples working there, a subsidary of Fiat)
    Most of the units are replaced with conventional splits and this works very well.
    Like said in the beginning of this thread: we installed the cooling (Mitsubishi splits) in one of the communication centers (stacked full of computers, huge UPS, srvers, switchers,...) of the Belgium Parliament, years ago and all the units are still running and it works fine.
    In the past, a too low humidity was a problem due to static electricty but all these problems are gone now.
    Look how many standard computers you see in very greasy, dirty environments and they're still working.
  34. #34
    Oct 2001
    Nottingham UK
    5,668
    Re: Server rooms.
    Of course, you should always select the 'split' type conditioner based on the Sensible load only from manufacturers tables. Problems seem to appear when the 'Total' cooling load is selected.
  35. #35
    Oct 2006
    Bristol
    11
    Re: Server rooms.
    if you were to use a size up indoor unit this would probably solve the problems. but when you tell the customer they wont get any warranty on the unit see what they say?
  36. #36
    Mar 2005
    u.a.e
    68
    169
    Re: Server rooms.
    Okay question for those who are in favour of a commercial split installation in data rooms,
    If humidity decrease up to low levels, How a commercial split can increase it if mean time there is also a cooling demand, and if required an under floor air flow directly enters in the cabinets from bottom then which type of unit will be fixed,
    Actually this is same as to take a common pain killer for all types of body pains,
    A one type of unit fix it every where for just for sake of a CLIENT because he can invest in computers data system a huge amount but for a proper A.C CCU system he is going for cheaper solutions'
    Have very bad experience with commercial splits used in Data rooms,
    malik55
  37. #37
    rbartlett's Avatar
    rbartlett Guest
    Re: Server rooms.
    Assuming you mean me..
    You're splitting what I said but the rise of computers have been iinversely preportional to the demise of specialist computer room air conditioner manufacturers.
    Whatever you feel about them splits are the way forward for most applications and the few left will have 'proper' a.c.
    These are the data rooms with big servers etc which may -or may not- need specialist a/c. I remember speaking to a HP eng who said their kit runs happily at 30 deg C but he couldn't convince the resi IT guy!!.
    It has always been that the major problem is not the heat/humidity that kills comuters it's the rate of rise. This is why the stuff hits the fan when the a/c goes down as a 10 deg rise over 10 days will have not effect on the computers but a 10 deg rise in 2 hours causes the c.b's to flex and expand and this is why joint failure occurs.
    Filtration is another red herring as these rooms are naturally very clean so why the need to be extra clean/?Again it all harks back to the olden times when computers were so unreliable that they over spec'ed everything as a 'just in case' get out. This is akin to the romans building bridges which which will stand for 1000's+ of years
    Why?? well because they did not have the skills to engineer it down enough so just kept doubling and doubling the thickness for the 'feel good' factor.
    As the late Colin Chapman said
    "any one can build a bridge which stands up nly an engineer can build a bridge which stands up -just"
    Richard
  38. #38
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    It goes by itself, I don't agree with the latest comments. Of course a Mitsi split goes well. I'm not implying splits are rubbish and CCU's are golden. I just would like to stress the fact the using splits in a server room is an improper usage of a comfort air conditioner.
    There was a time back in 2000, prior to .com explosion, when consultants were advising that in the short time, based on Moore's law principle, computers will be doubling their computing capability in half the space, and this would end up in quadriplying the cooling demand per square meter.
    At that time we were around 1.5-2kW/m2.
    How would you guys cope with a 8kW/m2 heating, on a 50m2 server room?
    With splits?
    And what about a backbone landing in Amsterdam, with 10000m2 filled up with optic fibers interfaces, amplifiers, modems, switches, etc?
    Not mentioning the newest water cooled blade server racks... it seems to me that RE are taking advantage of big supplies of chinese low-cost splits, and whatever happens either install them in houses, offices, or server rooms.
    If it breaks, replace it.
    This is not the road to go.
  39. #39
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    Oh, and I forgot to add: no, HP servers will not run happily at 30°C, assuming that 30°C in the room will correspond to 60°C in the rack.
    Here I'm writing this email at 21°C temperature, and the CPU is 48°C thanks to a bigger fan by Arctic. It was 66°C with OEM Intel fan.
    HP engineers do not know what they are talking about when speaking about air circulation, local pockets of warmer air, pressure drops across false floors and the like.
    Real applications are different than testing a single 4U in a controlled environment.
    Infact, manuals of servers read: "operating temperature -15 to +40°C". Then, why not keeping the window open or just filtering ambient air through an inlet louver?
  40. #40
    Oct 2003
    5,630
    34
    Re: Server rooms.
    But has Moore taken in account that computers nowadays uses less energy for a lot more tasks?
  41. #41
    Apr 2006
    Essex
    55
    21
    Re: Server rooms.
    As an owner of one of his cars aint that the truth!
    Back to thread though generally if you lose a fridge circuit on a DX CCu you normally would have between 1 to 3 remaining circuits still operating which when correctly sized will keep the equipment running happily. Now take a split a/c - single point of failure when compressor goes t*ts up and you lose the room, Generally most of the SUN/Compaq/HP gear will automatically start winding down at anything over 37 degrees. Belts and braces i know but also with the added benefit of additional capacity which can in a lot of cases take the strain of switching from standard racks to next generation blades with no upgrade of existing a/c equipment.
  42. #42
    Oct 2003
    5,630
    34
    Re: Server rooms.
    Explain why you still have 1 to 3 remaining circuits in a DC CCU when one fails? Only if this unit is fitted with 3 independant circuits of course.
    Well, then you have to compare it the same way for splits: you need to install for 50 kW heatload, 3 independant units of 25 kW of course.
    This is how we do it for a nearly fail-safe operation.
  43. #43
    rbartlett's Avatar
    rbartlett Guest
    Re: Server rooms.
    Ah but you're being disingenious. You state a multi CCu system but a single split.why not compare a single stage CCu and a room with two splits??
    Richard
    P.S I must admit CC comment is laughable given the heaps of rubbish that came out of East Anglia!!
  44. #44
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    2 splits do not match with 2 circuits CCU, in terms of efficiency, proportional band sharing, rotation and back up. They simply start and stop following a thermostat, even uselessly at the same time.
  45. #45
    Mar 2006
    Merate (LC) - Italy
    2,549
    Re: Server rooms.
    No, but in fact there no 8kW/sqm yet.
  46. #46
    Oct 2006
    Bristol
    11
    Re: Server rooms.
    I know Daikin have allowed the use of DX coils on there skyair range. and I've seen a system designed with two Denco down flow units with close control and humidification 2 stage on 4 RZQ250 With M pipe run witch kept the room a + - 2C 50% RH system worked treat. but still considering cost what can do a job and is cheaper? that system I've just said or a system with the equivalent duty of fresh air (to help keep the space a moderate temperature) and Splits to cool the racks you could even double up the splits for a cheaper price! but lets face it IT people always want the room to cold, I'm also an electronics engineer and i know for a fact most CPU's we'll happily run into C with no affect the problem is getting the cooling where it is required, with the new racks this has helped us use splits preferable a cassette above the racks.
    oh by the way I've also so seen VRV VRF equipment in Com's rooms OH NO! but had no problems.
  47. #47
    Dec 2003
    Rome Italy
    56
    29
    Re: Server rooms.
    there's no way you can compare porpouse built industrial units with silly split units builtfor comfort.Without mentioning better performance(i totally agree with no nick)
    on industrial units you can wire all sorts of optionals like water leak detectors,fire detectors,you can put many units on a net system with cascade,stand by and so on.
    Not to mention the air speed....a wall mount is designed for cooling mrs Smith's bedroom while she's asleep not for a 30 metres wide room,in the middle you would cook an egg!
  48. #48
    Double bubble's Avatar
    Double bubble Guest
    Re: Server rooms.
    Both Daikin and Mitsubishi Electric are nervous about their inverter systems being used in computer rooms. Ideally, they'd tell you why themselves of course but i believe that the low load of a computer room (low latent anyway), means that the compressor can be slowed down to compensate - particularly in low ambient conditions. This conflicts with their required refrigerant flow to keep the indoor heat exchanger free of oil - the alternative is to risk an indoor coil freeze-up.
    That's my understanding anyway. As i said, the real answer should be coming from them.
    G'day all
    Thanks in advance.
  49. #49
    Oct 2006
    57
    165
    Re: Server rooms.
    G'day all
    Thanks in advance.
    What is the model number? is it R407C or R410A?
    Obi Wan
  50. #50
    Dec 2004
    Australia
    52
    519
    Re: Server rooms.
    G'day Obi Wan.
    No particular model number, I was just refering to wall mounts.