    Ammonia system design



    I need some info about NH3 design, features...

    Where can i get this info?, it could be a manual o a summary. I need a insulation desing for Ammonia pipes.



  2. #2
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Ammonia system design

    Several places to look.

    Firsyt look in the ASHRAE Handbooks, there is a chapter on ammonia piping practices.

    Next check out IIAR (International Institute of Ammonia Refigeration). I believe they have some Spanish language booklets.

    Next check some vendors such as Vilter, Mycom or Hasegawa.

    I don't have the web addresses, but you can easily do a Google Search.

    Ken

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ammonia system design

    Quote Originally Posted by ingherrera
    I need a insulation desing for Ammonia pipes.
    Installation or insulation design???

    IIAR has a piping handbook that is pretty good for getting started. https://www.iiar.org/f-store.cfm

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia system design

    Hi, ingherrera

    Quote Originally Posted by ingherrera View Post
    I need some info about NH3 design, features...

    Where can i get this info?, it could be a manual o a summary. I need a insulation desing for Ammonia pipes.
    What you need about insulation?

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Ammonia system design

    Are you asking about installation or insulation for piping. ASHRAE Handbooks have a chapter in insulation of piping for generic insulation. As for specific insulation data, you will need to contact an insulation manufacturer for specific thickness and applications. You will need to decide about vapor barrier, insulation material (urethane, styrofoam, foam glass, wool, etc). Most of the work we do is with urethane. The insulation will also require a protective jacket of metal or vinyl.

    Insulation thickness will be dependent on pipe temperature, ambient air movement and ambient wet bulb temperature.

    All of the insulation manufacturers have design/installation guide handbooks.

    Ken

  6. #6
    Join Date
    Dec 2005
    Location
    Centroamérica
    Posts
    12
    Rep Power
    0

    Re: Ammonia system design

    I need to find the right insulation for a system. Here in Costa Rica a client installed a system five year ago, Sollie designed the system; about one year ago the insulation fault and small drops appeared at the bottom of the pipes. That’s why I am looking for guidelines for ammonia insulation.

  7. #7
    Join Date
    Aug 2006
    Location
    Scotland
    Posts
    104
    Rep Power
    18

    Re: Ammonia system design

    If the insulation was OK originally and then deteriorated then it sounds like it is the vapour seal which is at fault - probably the most common mistake when insulators work on cold systems. The cold pipe attracts moisture so if you don't put a waterproof barrier round the outside of the insulating material it will soak up like a sponge. Metal cladding doesn't count! (it is full of holes)

    cheers
    Andy P

  8. #8
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia system design

    Hi, Ingherrera

    Quote Originally Posted by ingherrera View Post
    I need to find the right insulation for a system. Here in Costa Rica a client installed a system five year ago, Sollie designed the system; about one year ago the insulation fault and small drops appeared at the bottom of the pipes. That’s why I am looking for guidelines for ammonia insulation.
    I am sorry to hear you have some problems with insulation. That is Dos Pinos. Can you, please, tell exactly what happen, can you send some photos about. Drops are water or PU. What system is that +3, -10, -35 or -45. Is that down in compressor room or upstairs in separator room or outside on the bridge?

    In your documentation you can find all about insulation thickness for each system or I can send a copy to you. Send me PM with your email address.

    The best is still the same you have on your plant, injected PU in aluminium cladding, but something strange happen there.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  9. #9
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia system design

    Quote Originally Posted by TXiceman View Post

    Insulation thickness will be dependent on pipe temperature, ambient air movement and ambient wet bulb temperature.


    Ken
    agreed with all said

    ...and pipe DN

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  10. #10
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ammonia system design

    This certainly sounds like insulation system failure, or poor installation techniques. Insulating pipes is an art, along with some science.

    Obviously the vapor barrier has failed. This is the most critical part of insulation systems. It is not uncommon to find a metal jacket on exterior piping with screws used to hold the jacket in place. The screws puncture the vapor barrier and it is only a matter of time before the insulation is saturated.

    Here is a link that shows some of the recommended installation techniques.
    http://www.dow.com/PublishedLiteratu...ge=BasicSearch

    And a link to other ideas to consider.
    http://www.dow.com/styrofoam/na/dowpipe/library/

  11. #11
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia system design

    Hi,

    I think I know the cause of the problem (not sure but we can discuss it), but still waiting for additional info from Ingherrera, about exact places of insulation faults.


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  12. #12
    Join Date
    Dec 2005
    Location
    Centroamérica
    Posts
    12
    Rep Power
    0

    Re: Ammonia system design

    Hi

    Thank you for all your advices.

    The problems are in all liquid and gas pipes in lines -35 C and -45C.

  13. #13
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Ammonia system design

    Quote Originally Posted by Josip
    but still waiting for additional info from Ingherrera, about exact places of insulation faults
    ingherrera, I think the information Josip is wanting to hear about is where are the major problems with ice and water forming on the pipes. I know you said earlier the water was forming on the bottom, but that is the logical place to see the water.

    I believe the locations Josip is thinking of are the insulation joints in the piping (next to valves, or fittings) and what I call "vapor stops".

    A vapor stop is where the butt-end of the insulation terminates into a bare pipe (say next to a valve station, or at compressor suciotn valves).

    Quote Originally Posted by ingherrera
    I need to find the right insulation for a system.
    I would make sure any type of glass fiber was not used for the insulation. This is only for hot service, not cold.

    Just about any of the extruded foam insulations are OK.

  14. #14
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Ammonia system design

    Since thread is on Ammonia System Design, I would like to aske you that if the system is a liquid overfeed system and there are a number of Evaporator units, then do one take seperate liquid lines from a liquid header. How do I design the header.Is it possible to provide me a sketch of the system.

    I am really grateful to the engineers in the forum to have helped me to learn about Ammonia System which I have not been used to.It is a great forum.

    With best wishes,

  15. #15
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Ammonia system design

    Samarjit Sen, best place for info on the piping is the ASHRAE Handbooks for ammonia piping practices. Next look for some old info from York, Frick and vilter.

    you need to know the flow rate and size the lines accordingly for velocity and pressure drop.

    Ken

  16. #16
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Ammonia system design

    Thanks Ken, I will do just what you advised. I have been able locate some details and more I presume I will get from Ashrae.

  17. #17
    Join Date
    Mar 2007
    Location
    UAE
    Age
    43
    Posts
    78
    Rep Power
    18

    Re: Ammonia system design

    Hi friends,