Results 1 to 13 of 13
Thread: ice rink
21-02-2002, 02:28 AM #1
ice rink
mjakub76@hotmail.com
I'm looking for an information about ice rinks, different refrigeration systems etc. if you now where i can find something about it, please e-mail me .
P.S. I'm a student and I need this information because I 'm going to make project about refrigeration system for ice rink. In this case I'm looking for any article, book or web site where I can find it.Last edited by mjakub; 22-02-2002 at 04:21 AM.
16-03-2002, 01:02 AM #2
Try www.burleys.com for starters. Give me some time and I'll find the others I have.
Mike Hopkins
18-03-2002, 12:04 AM #3
thanks for help
18-03-2002, 01:50 PM #4
Hi, try these two sites. http://star-ref.co.uk or http://cimcorefrigeration.com
I some of you already know I work for Star Refrigeration, we would fit the majority of Ice Rinks in the UK. Cimco fit Ice Rinks worldwide, mostly though in North America.
Regards. Andy.
24-03-2002, 02:59 PM #5
Hai Mjacub , Look on ASHRAE Refrigeration Handbook . Ice
Rings have been dealth Nicely in that book.
Best of Luck.
R.Sivakumar
28-03-2002, 03:44 AM #6
thaks, that's what i did, and it was good idea. i found a lot of informations there. now i'm looking for, how to calculate heat gain for ice rink, and something about freezing protection.
06-04-2005, 01:13 PM #7
Re: ice rink
You can find very usefull information in YORK`s - Artifical iccerink manual.
24-04-2007, 07:29 PM #8
Re: ice rink
Hi Guys, new here to RE so be nice!!!!
Im think ing of building a 'small ice rink pad' in a pro shop that im going to open, ill be looking at a size of around 6m width and 10m length.
What size chiller unit would you recommend for this type of install. Also what type of piping would you use to keep the ice cool?
Ive been doing some research on but only found the likes of calmac's ice mat, and that fold out ice rink the aluminium type, some people use rubber piping and plastic piping. There is a company here in the UK that uses a system called 'Mitra' which uses pipe which looks like plastic electrical flexible conduit!
As much information as possible would be great.
24-04-2007, 10:00 PM #9
Re: ice rink
Most rinks in the US have been going in with glycol chillers and plastic pipes in the floor. You can have a concrete floor or a sand floor.
The chiller needs to be sized based on the rink use and ambients. Waht do you intend to do about scraping or shaving the ice? It has to be done on a regular basis. The ice is also usually dumped in a slush pit that uses compressor heat to melt the ice. The rinks wea re servicing here are all ammonia refrigerant.
Yo also need to consider some reduntancy in the compressors so that if you loose a compressorm you are not out of business.
If I were you, I'd look for a small independent consulting engineer to guide you through all of the design parameters
26-04-2007, 07:31 PM #10
09-05-2007, 02:30 PM #11
Re: ice rink
what is small, insulated floor? , room temp etc
15-05-2007, 07:13 PM #12
Re: ice rink
Yeah its going to be small around 6m width and 10m length.
The existing shop floor is concrete, so was going to build a wood grid, plywood level the structure off, insulation boards, then put plastic sheet down the build up from there.
So need a chiller for that purpose.
Not sure on what the room temperature would be at the moment.
I saw a calculation from a company which does outside rinks and their calculation was you nedd 300w per meter square.
15-05-2007, 07:14 PM #13
Re: ice rink
Has anybody heard of this mitra rink grid piping system?
A certain company uses it here in the uk, ive asked for information, but yet no reply.
Ice Rinks
By Andy in forum IndustrialReplies: 44Last Post: 18-04-2009, 02:02 PM -
need a valid explanation
By giovanni in forum Technical DiscussionsReplies: 28Last Post: 22-11-2007, 12:21 AM -
ice rink design
By jteixiera in forum Technical DiscussionsReplies: 11Last Post: 15-11-2007, 08:36 AM -
Swimming pool and ice rink is this a match made in heaven
By chuffin in forum FundamentalsReplies: 1Last Post: 29-07-2006, 12:09 PM