    Talking Discharge Superheat



    Hiya people,
    I'm wondering if anyone has a good source of information on Discharge Superheat. I need to know the technical details.
    Thanks,
    Muzic
    Last edited by Muzic; 17-09-2006 at 09:16 PM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Discharge Superheat

    Hi Muzic and welcome to the forum.

    Have a look at a previous post on the subject...
    http://www.refrigeration-engineer.co...read.php?t=708
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Discharge Superheat

    Hi Muzic,

    Welcome to the RE forums.

    For the discharge superheat you use a similar process as finding the suction superheat, except you want to use the discharge data from the compressor.

    Discharge pressure and temperature.

    What else are you looking for, and why I suppose?

  4. #4
    Muzic's Avatar
    Muzic Guest

    Smile Re: Discharge Superheat

    The reason I ask is this...
    I work on Chillers all the time, and some of them are required to be charged by Discharge Superheat. This is something that, untl approx 5 years ago, I had never seen.
    I can find nothing on it in the way of explanations (until Brian_UK offered the link) as to why it is significant and how/why it changes with changing conditions.
    I'm the kind of guy that needs to know why as well as how heh.
    Thanks for sharing your knowledge.
    This is a great forum for pooling knowledge. It is a great resource.
    Muzic

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: Discharge Superheat

    Quote Originally Posted by Muzic
    and some of them are required to be charged by Discharge Superheat.


    Sounds like flooded chillers.

    The discharge superheat is a good technique to have in your bag of tricks. You need to know this for screw compressors to prevent oil dilution problems, and it comes in handy for troubleshooting leaking discharge valves on recip. compressors too.