    Expansion Valves



    Hi,
    I would like to place one question does expansion valve function differe on the use of different gases for example system working on R22 and would to switch to R404 please do advice for the expansion of the gases



  2. #2
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Expansion Valves

    Every gas has it's own valve.

    They are all labeled as such.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  3. #3
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Expansion Valves

    Chillin out is right,but in an emergency you can use a R22 valve to get you back up and running but only until the correct valve is available.

  4. #4
    Join Date
    Sep 2006
    Location
    Manila
    Posts
    12
    Rep Power
    0

    Re: Expansion Valves

    All refrigerants have different properties. You need to size up expansion valve based on capacity, refrigerant charge, pressure drop, and fitting sizes.

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Expansion Valves

    The capacity of the Expansion Valves are based on the properties of the refrigerant being used. Since the properties varies for different refrigerants, you have to use the Expansion Valve specifically designed for that particular refrigerant.

    An expansion valve designed for R 22 will not function with R 404A. So please do not try this. The bulb of the expansion valve will not be able to operate with a different refrigerant due to which the valve will become inoperative.

    If you want a detail information on TEV application and working, please send me your e mail address. I tried to upload on this post, but the forum"s capacity is limited to 100 kb. You may contact me at samarjitsen@unirefeng.com .
    Last edited by Samarjit Sen; 18-09-2006 at 01:43 PM. Reason: Wanted to upload some document

  6. #6
    Join Date
    Aug 2006
    Location
    Ireland
    Age
    47
    Posts
    26
    Rep Power
    0

    Re: Expansion Valves

    An r22 valve WILL work on a r404 system.
    One should only do so to get out of trouble though, but it will still work.

    An r22 valve has r22 gas in it, same with an r404 valve having r404 gas in it. Pressures arent that different so it will do the job till a proper valve is fitted.

  7. #7
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Expansion Valves

    Dear Langer,

    All expansion valves have the refrigerant for which it is rated , charged into its valve. R 22 is a pure refrigerant whereas R 404A is a mixture of gases. The properties may be somewhat similar but are different.
    A number of people had tried to use the R 22 TEV for R 404A, but failed to get the performance.

    As you rightly say that it can be for temporay use, but during that period the performance and the overall capacity of the system would be quite different.