    Oversized System



    I've got a customer that wants to move an existing wall mount, cooling only, fixed speed, with a capacity of 3.6kw (2.7kw sensible) into a room 2.8m x 3.8m. (2.4m h)

    For a new installation for this room size we would install a 2.0-2.5kw system. So, apart from the unit short-cycling, what other disadvantages would there be from installing the 3.6kw? Or would it just be better in the long run to install a new 2.0kw?



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Oversized System

    You seem to have answered your own question, Slim.
    ________
    Mercury Topaz specifications
    Last edited by Argus; 07-02-2011 at 09:26 AM.

  3. #3
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Oversized System

    I see what you mean but as always its the cost that may stop a new install.
    From a customers point of view they have a 2yr old panasonic split in perfect working order and just want to move it, spending over a grand on a new install was not on there mind.
    My question is has anybody had experience in fitting units this size into small rooms (normal office conditions) and whats the worst that could happen??
    Iv'e seen on another site a 10kw LG cassette that was moved to a new reception area which needed 5-6kw and the coil froze up because they had set it on 18deg, an engineer had to put it on heating to defrost. (or was that just because it was an LG!)

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Oversized System

    .

    You've done it again. Slim - answered your own question, that is!

    An oversized system is prone to short cycling and poor evaporation which will make a bad situation worse.

    You will probably rue the day that you proceeded against your better judgement if you reinstall the thing, because when it breaks down repetitively it is you who will be picking up the tab.

    Look at the intended the new position, do the sums, size the kit and if it is seriously over the top quote a new system. If the customer won't have it, walk away. What's the point in installing something that will cost you your profit?

    .
    ________
    Ford D3 platform history
    Last edited by Argus; 07-02-2011 at 09:26 AM.

  5. #5
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Oversized System

    Thanks for the advice, Argus, I've made my mind up and Im sure you can guess what it is!

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Oversized System

    Another possible aspect Slim would be excessive airflow from the oversized unit.

    If it is an office environment then your customer could start getting complaints from the staff and quoting Health and Safety type regulations may be useful.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Oversized System

    .

    Absolutely.

    There's no point putting in something that just ain't right.

    You'll end up buying a pup.

    .
    ________
    vaporizer answer
    Last edited by Argus; 07-02-2011 at 09:26 AM.

  8. #8
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: Oversized System

    You could be right.........but it's not so much the size of room but more the actual cooling load. That might be worth checking into to see if the 3.5kW system is not so over the top.

    Could be there is a lot of solar and a couple of computers etc, which might just leave a dinky unit straining away.

  9. #9
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Oversized System

    Another important consideration is humidity control. An oversized unit will accomplish the sensible cooling in such quick order that you will not dehumidify the room. Long run times are required to wring the greatest amount of moisture and achieve comfort levels of RH. Thus you might have a dank muggy and moldy room.

  10. #10
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Oversized System

    I get a little leary of anytime an AC is sized based on an area.

    The warning of too much cooling and not enough dehumidification usually materializes when ambient dewpoints exceed say 17C.

    I sold a lot of geothermal in Canada sized for heating and often 100% oversized for cooling and no humidity problems beacuse the ambient humidity was not that high.

    Take that same approach in a more humid climate and you have a good envirnoment for hanging meat carcasses

  11. #11
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18

    Re: Oversized System

    Abby Normal:
    I get a little leary of anytime an AC is sized based on an area.

    The warning of too much cooling and not enough dehumidification usually materializes when ambient dewpoints exceed say 17C.
    Abby Normal:
    Take that same approach in a more humid climate and you have a good envirnoment for hanging meat carcasses
    Lately (since mid 90s) a lot of engineers just do an AREA measurement and calculation then divide it with a MAGIC NUMBER and immediately advise the customer the required equipment size.
    Even with free software and cheap computers, most does not even run the software for cooling load calculations before suggesting an eqpt size.

    I still remember the old days (me working 20+years ago as a newbie in maintenance dept. of US naval base in Subic), when we have to survey an office count the no. of men and women, check/interview the end user for latent heat loads, sensible loads, open a book to get CFM/person required by NavFac regulations.
    And then with the help of manuals, books, a cooling load form (Trane or Carrier), scientific calculator, we will be able to come up with capacity in BTUHs, CFMs, Sensible heat load factor, fan static pressure, etc. etc. etc. . .

    Our boss (Fil-Am) will even review it before submitting a budgetary costing which maybe delivered in a year (if urgent).

    Past forward Now in my part of the tropics. . .
    we always find oversized/undersized eqpt in a lot of fairly sized office. . .
    with electronic thermostat that is adjusted by women and again re adjusted by men.
    We then need to explain that the men and women have different cooling load requirement.

    Maybe this is the price we have to pay:

    Be a magician with numbers in times of easy access: mobile phone, internet connection, SMS. . .

  12. #12
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Oversized System

    worst design scenario know to man is three women and one thermostat

    One will be fine, one too hot and the other too cold. The next day the fine one is cold, the cold one is hot, and the hot one is in my bed

  13. #13
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Oversized System

    You can do as many calculations as you like to find the required heat load.

    But if you ore only quoting on a wall hung split unit you have to draw the line somewhere.

    Whats the point of working out the exact R value of every single wall, area of every window and as many other particulars you can think of if you dont get the job.

    Having a rule of thumb is OK in my book for small jobs as long as some common sense goes along with it.
    Last edited by Temprite; 25-09-2006 at 03:01 AM. Reason: spelling

  14. #14
    Join Date
    Sep 2006
    Location
    Manila
    Posts
    12
    Rep Power
    0

    Re: Oversized System

    Maybe you dont get the point of Mr Slim. I would suggest a capacity control for his system.

  15. #15
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Oversized System

    Quote Originally Posted by Temprite View Post
    You can do as many calculations as you like to find the required heat load.

    But if you ore only quoting on a wall hung split unit you have to draw the line somewhere.

    Whats the point of working out the exact R value of every single wall, area of every window and as many other particulars you can think of if you dont get the job.

    Having a rule of thumb is OK in my book for small jobs as long as some common sense goes along with it.
    In heating, if you are quoting a replacement in a subdivision, or a home built during a known code cycle, you can ball park the HEATING pretty easily, and worry about which room was always too cold etc after you get the job.

    In cooling you can ballpark it high if you do not want to put the time in when bidding. But with cooling, orientation with respect to the sun is everything. Identical houses orientated differently will have different cooling loads.

    Here, it does not really matter how hot is outside, what matters is whether it is sunny or not and what the humidity level is.

    Your avatar looks 'arid' and as I have said, the woes of oversizing are not going to bite you in the ass when the ambient dewpoints are low.

  16. #16
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Oversized System

    Quote Originally Posted by Abby Normal View Post
    In cooling you can ballpark it high if you do not want to put the time in when bidding. But with cooling, orientation with respect to the sun is everything. Identical houses orientated differently will have different cooling loads.

    Here, it does not really matter how hot is outside, what matters is whether it is sunny or not and what the humidity level is.
    G'day Abby.
    I Agree with everything that you have said here. When I said that a rule of thumb is OK for wallmounts I also said that common sense has to be used as well. Any system larger than this and I would spend more time to find the required load. Some people think rule of thumb will work for every install this is obviously not true.

    Your avatar looks 'arid' and as I have said, the woes of oversizing are not going to bite you in the ass when the ambient dewpoints are low.
    This was a painting done by my great grandfather. He lived in England and painted landscapes so I would say this is an English landscape. I live on the coast there is not a huge amount of really humid days here.

  17. #17
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Oversized System

    Some interesting points made here,

    The customer has decided he wants the existing system installing. I've made aware of the short-cyling and draughts so that they cannot complain at a later date in the future.

    I am still thinking along the lines of tyring to reduce the systems capacity. The outdoor unit will be sited on a mezzenaine (sp) inside a building, well ventilated, no real heat gains, roof height is something like 10m.

  18. #18
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Oversized System

    Quote Originally Posted by Slim R410a View Post
    mezzenaine (sp)
    Hi Slim

    Mezzanine

  19. #19
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: Oversized System

    Hi Fredy,

    When i used to calculate the heat load about 40 years ago, we used to refer to Carrier Handbook and Trane Handbook and use a slide rule, which I still have. In my experience a slightly oversized AC unit will not have any adverse effect. Further a detail load assessment has not been made, which I feel is very important in case of finding the heat loads wether it is for air conditioning or refrigeration. Thumb rules will always get you in trouble.

  20. #20
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18

    Re: Oversized System

    Samarjit:
    Thumb rules will always get you in trouble.
    That's usually what i preach to the young guns. Always reminding them that rule of thumb are for checking only.
    Also, it can be use judiciously by anyone near your length of experience (in A/C & Refrigeration) but not for those that are just starting in the trade.

    But there will always be in our midst those that are trying to look and sound smart. . .
    These are the one's that we should be LEERY (just have to borrow this word, does it sound nice Abby?).
    I really enjoy reading posts by westerners, it always sound nice and sometimes poetic.
    Last edited by winfred.dela; 29-09-2006 at 12:16 AM. Reason: spelling correction

  21. #21
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Oversized System

    Have you ever been as leary as timothy?

  22. #22
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18

    Re: Oversized System

    Abby Normal:
    Have you ever been as leary as timothy?
    Timothy? Do not know any Timothy.
    Leary? or Leery?

    Maybe, i need to study English Literature in my free time so i can answer appropriately.

    But i doubt if i can find extra time, I kind of need more than the 24 hours of each day coz around 1/4 of the day is spent here in RE forum. . .

  23. #23
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Oversized System

    Search Timothy Leary

  24. #24
    Join Date
    Sep 2006
    Location
    Mindanao, Phils.
    Age
    62
    Posts
    257
    Rep Power
    18

    Re: Oversized System

    Thanks Abby.
    Have found the guy. Now, i know something about Timothy Leary.

    Need to read some of his works before i can answer your question.
    Have you ever been as leary as timothy?

  25. #25
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Oversized System

    lol, would be consuming something and not reading. He had a fondness for LSD

  26. #26
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: Oversized System

    Quote Originally Posted by Slim R410a View Post

    The customer has decided he wants the existing system installing. I've made aware of the short-cycling and draughts so that they cannot complain at a later date in the future. I am still thinking along the lines of trying to reduce the systems capacity.


    Suggest you note the potential problems in your quote, also. {You do write quotes, yes?}

    As for reducing capacity, whatever you plan on that, offer it as a phase-2, which you can go ahead with, if needed.

    That way you have done all you can, and customer takes the responsibility for any oversizing problems that might show up.



    QUESTION… If one exceeds the run length, the duty of the system will start to reduce. That is well known, but can any damage / excessive wear occur in that scenario?

    Thinking sideways on this OP, one way of reducing output would be to increase the run-length outside correct limit. But, I guess it’s not quite a easy as that, eh?