Results 1 to 10 of 10

Thread: High Disc Temp

  1. #1
    Join Date
    Sep 2006
    Location
    iowa
    Posts
    6
    Rep Power
    0

    High Disc Temp



    I am fighting a high disc temp what causes this and what should I do. This is on a 1000 ton york chiller.

    ROAD



  2. #2
    Join Date
    Sep 2006
    Location
    Londrina
    Age
    59
    Posts
    20
    Rep Power
    0

    Re: High Disc Temp

    mornig, Road 31
    Which or modelo I give seu compressor? Which pressao de trabalho? which or superaquecimento? é resfriado to ar ou to água?
    Mauro

  3. #3
    Join Date
    Sep 2006
    Location
    Londrina
    Age
    59
    Posts
    20
    Rep Power
    0

    Re: High Disc Temp

    sorry;
    Which the model of its compressor? Which pressao of work? which the overheating? is cooled to air or the water?
    Mauro

  4. #4
    Join Date
    Sep 2006
    Location
    iowa
    Posts
    6
    Rep Power
    0

    Re: High Disc Temp

    It is a screw compressor model ys nn nn s7 york.

    chilled water and tower water for condensor side.

  5. #5
    Join Date
    Sep 2006
    Location
    iowa
    Posts
    6
    Rep Power
    0

    Re: High Disc Temp

    It shuts down on high disc temp

  6. #6
    Join Date
    Sep 2006
    Location
    Londrina
    Age
    59
    Posts
    20
    Rep Power
    0

    Re: High Disc Temp

    sorry, friend
    but I will not be able helps it therefore I do not have much esperiencia with this type of comporessor, enters in the site of “York”.
    mauro

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: High Disc Temp

    Is it a centrifugal chiller? What are the superheating (if not flooded evap) and subcooling?

  8. #8
    Join Date
    Sep 2006
    Location
    iowa
    Posts
    6
    Rep Power
    0

    Re: High Disc Temp

    its a screw compressor, would this happen at a low load and also if air temp was low

  9. #9
    Join Date
    Jul 2006
    Location
    New Berlin, Wisconsin, USA
    Age
    65
    Posts
    57
    Rep Power
    18

    Re: High Disc Temp

    At low flow rates you are not moving alot of refrigerant through the compressor and you are relying on the oil to cool the compressor, what is the oil temperature when it goes down? It could be either your oil temp is too high (what type of oil cooling?) or your oil injection flow rate is restricted.

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: High Disc Temp

    At low load, screw compressors are prone to high discharge temp. Unless superheating can be reduced so that discharge temp can reduce, I would suggest liquid injection to cool the windings.