Results 1 to 7 of 7

Thread: Bulkhead units

  1. #1
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Bulkhead units



    G'day all.

    Was wondering if anyone here had installed the Daikin low static CDX bulkhead units for the super multi or super multi plus.

    Can you install a small length of ductwork to the return and supply air and still get adequate air supply.

    Have any members ever installed them in this way and if so was it a success.

    Thanks in advance.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Bulkhead units

    Can't say that I have Temprite. Do you have a link to the CDX unit. It's not one I've come across.

    All of the ducted Daikin units in the UK have the facility to increase static pressure settings through the controller.

  3. #3
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Bulkhead units

    Hi there, going by the install manuals and the databook this unit is only available in the multisplit family. The unit it self looks more like a hotel application unit that has no ducting just a grille. By the sound of things a FDNQ low static unit maybe a better option for you that you could fit ducting too and as frank says adjust the static pressure through remote controller field settings. I have the manuals on the CDX unit and the FDNQ, UK version. Just let me know and i'll send you them. Hope this helps!

  4. #4
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Bulkhead units

    Thanks for the replies chaps.

    Try this.

    www.daikin.com.au/product.asp?pid=206

  5. #5
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Bulkhead units

    Checked out the link, the CDX unit down under looks just like the UK FDNQ. Cant work out why they dont just keep the same model numbers?

  6. #6
    rbartlett's Avatar
    rbartlett Guest

    Re: Bulkhead units

    yes we've used these models with a short run of ducting -no problems

    cheers

    richard

  7. #7
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Bulkhead units

    Thanks everyone.