    Whad do you think about acid away?Eny experience with that caind of purifaying oil?

    Renato



  2. #2
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Acid away

    most discussions on it end up with the conclusion that only refrigerant and oil should be inside a system

  3. #3
    Join Date
    Jul 2006
    Location
    New Berlin, Wisconsin, USA
    Age
    65
    Posts
    57
    Rep Power
    18

    Re: Acid away

    I agree with Abby Normal, in order to get rid of the acid chemically you have to add a base, then you get a reaction that will more than likely result in precipitates, which depending on the chemistry can cause more problems than the acid.

    Some people swear by purifying the oil through filters and such, it does just that it may purify it only. Used oil has lost some of its components over time and these can include, antifoaming agents, anti-oxidents, viscocity index improvers and anti-wear additives, when you purify used oil you end up with an oil lacking these components and while it tests out fine for acid content and particulates, it lacks the important stuff you want in the oil.

  4. #4
    Join Date
    Aug 2006
    Location
    United States
    Posts
    7
    Rep Power
    0

    Re: Acid away

    My company manufactures an acid treatment that uses the filter drier and not a dangerous chemical reaction to treat acid. This forum was making me laugh because in our marketing meetings some of the head honchos keep repeating that "we need to educate the consumer that the competing products cause dangerous chemical reactions blah blah blah etc. etc." So I see this forum and it looks like everyone realizes exactly what is going on lol. Anyways take a look at it at qwik.com under the products section. this treatment does not neutralize the acid or cause a chemical reaction. It just moves it all to the filter-drier really quickly, the only set-back is that it has to be hermetically injected rather then just dumped in like "acid-away".

  5. #5
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Acid away

    Ive had a few systems that have had burnt out compressors on them and tested for high levels of acid. When new compressor fitted with burn out drier in toe after a few days oil tested again and shown signs of acid, had to go down the line of adding acid away and eventually changing the oil a couple of times and replacing the core from the burn out drier at each oil change to finally get rid of acid.

  6. #6
    rbartlett's Avatar
    rbartlett Guest

    Re: Acid away

    Some mitsubishi splits allow you to re-use the old R22 pipe as they say their oil neturalises the chlorine in the old oil.

    Cheers

    Richard

  7. #7
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Acid away

    Have you ever used these systems? If so any problems? I know that Daikin RZQ units can use old R22 pipework, but there is a long checklist that has to be ticked off before you can consider it. With things on it like the system must be able to run in cooling for 30min then be pumped down, and never in the history of the unit had a burn out. So not much use unless you are just upgrading a system which nine times out of ten you only want to change it cos its U/S

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Acid away

    2 years ago we took out a couple of old R22 Daikin cassettes and installed new R407C cassettes with full speed compressors and we decided to re-use the existing pipework as it was a difficult task to replace it.

    We used, for the first time, one of the recommended flushing fluids to clean out any mineral oil in the pipework.

    Long story short, but we lost a compressor this week - don't know the cause yet as we haven't swopped out. This system has been troublesome from the start while the other unit continues to run without any sign of problems.

    Is it too early to blame the flushing fluid do you think?

  9. #9
    Join Date
    Feb 2001
    Location
    phoenix,arizona
    Age
    72
    Posts
    103
    Rep Power
    24

    Re: Acid away

    A vote of confident. I've used acid away on many, many, compressor burn out / replacement. air andition and refrigeration systems. No problem.
    Be Happy

  10. #10
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Angry Re: Acid away

    My suplier claims that I need to detect acid level in oil.There is 3 posible levels mild,midle and severe.When I detect I need to put 3 bothles in sistem when I have severe acid in oil.After this procedure I have eqperience oil diferential alarm for few days.After I replace oil the problem no longer exsists.This were on heat pump with _Bitzer 100HP.That whos my first experience so I am sceptic now.

    Renato

  11. #11
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: Acid away

    I had severe acid problems in a large parallel rack application. After using the prescribed acid removal driers such as the Sporlan HH series, and doing oil changes, I still had high acid content. After 4 frustrating weeks of recurring high acid readings, I used 2 applications of Acid Away and finally won control of the Ph in the system.

    I think that the sooner you can neutralize an acidic system, the better. I don't care about some salty dust that a filter can collect. I will be quicker to use Acid Away or an equivalent if confronted with a similar dilemma in the future.

  12. #12
    Join Date
    Feb 2001
    Location
    phoenix,arizona
    Age
    72
    Posts
    103
    Rep Power
    24

    Re: Acid away

    I would like to hear from the manufacturer(s) of acid away or the like. In particular; I like to see some pure test data, how many units tested, how many got better, how many got worest, etc... ( Please, no sale pitch. We got the greatest product that can solve all u r problem...etc... no bull **** Please)
    Be Happy

  13. #13
    Join Date
    Aug 2006
    Location
    United States
    Posts
    7
    Rep Power
    0

    Re: Acid away

    If you visit qwik.com the acid treatment my company manufactures can be found under the products section. It is QwikShot Acid Flush. Posting a direct link to the product is not allowed on this forum but If you want to look at some of the data on this product I recommend reading Press Release 2 inside of the QwikShot product's description at qwik.com. Comments on what you think about QwikShot are very appreciated, thanks.

  14. #14
    Join Date
    Jul 2004
    Location
    england
    Age
    52
    Posts
    64
    Rep Power
    20

    Re: Acid away

    Have used Quickshot on all recip compressors on water chillers with no problems at all. Used on Dakin split R407c and on Mitsi splits with no recall to faulty comps, works with mineral and synthetic oil i'm happy with it its very easy to use .

  15. #15
    Join Date
    Feb 2001
    Location
    phoenix,arizona
    Age
    72
    Posts
    103
    Rep Power
    24

    Re: Acid away

    I've also used Quickshot - no problem.
    Be Happy

  16. #16
    william_wye's Avatar
    william_wye Guest

    Re: Acid away

    I also recommend Quickshot-real easy

  17. #17
    Join Date
    Aug 2006
    Location
    United States
    Posts
    7
    Rep Power
    0

    Re: Acid away

    Well I feel proud guys! Thanks a lot!

  18. #18
    Join Date
    Nov 2006
    Location
    Melbourne, FL
    Posts
    5
    Rep Power
    0

    Re: Acid away

    I used to use acid away until just recently I heard about qwikshot and did some research on it (including questioning this forum).

    I used qwikshot last week. It was much easier for me than acid-away, the actual chemical used to remove the acid doesn't stay in the system, and it took about 10 minutes of my time (and I'm slow).

    All I did then was wait and test (the test took 5 sec --qwikcheck also offered by the same CO as qwikshot)

    Cake.

    --kDawg

  19. #19
    Join Date
    Feb 2007
    Location
    north of england
    Posts
    5
    Rep Power
    0

    Re: Acid away

    I have been using acid aawy for about 10 years no problems to report, never had to change the oil again.
    Last edited by snowman69; 15-02-2007 at 09:13 AM.