    Heated R134A ??



    afternoon ppl, I used to work for a large refrigeration company in edinburgh b4 i start my own company but i have a question that id like to ask.

    a few years ago i was at job were the condensor fan motor was faulty causing the system to run EXTEREMLY hot, gas used was R134A. Now the question i ask is after i replaced the fan motor, i place my gauges on to find that system appeared to be short of gas. pressure tested system with ofn to find no leak what so ever.

    now id put it down to the R134A being heated up that much that it had lost its propertes in which it is made up from causing to appear short of gas.

    sooooo i had a little talk with my service manager and he basically laff at me but to this day the system has never lost its gas (as i now have the customer ) and works perfect.

    iv i just lost the plot or am i right???



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Heated R134A ??

    I would have to ask - how much gas did you take out of the system and how much did you put back in after pressure testing?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Heated R134A ??

    Also, did you happen to change the (blocked) drier at the same time??

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Nov 2006
    Location
    UK
    Age
    63
    Posts
    392
    Rep Power
    18

    Re: Heated R134A ??

    R134A is a pure refrigerant and does not lose its properties, ot is either there or it has escaped. There may have been a leak as pressure testing with OFN when using R134A is a waste of time as iits molecular size is approximately one tenth of that of OFN, you should have used helium which has a similar molecular size.

    Ian

  5. #5
    Join Date
    Jun 2001
    Location
    Gloucestershire
    Posts
    13
    Rep Power
    0

    Re: Heated R134A ??

    [QUOTE=Pooh;81584]pressure testing with OFN when using R134A is a waste of time as iits molecular size is approximately one tenth of that of OFN, you should have used helium which has a similar molecular size.

    QUOTE]

    Ian,
    Sorry mate 134a molecule is not the same size as helium and is also larger than OFN.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Thumbs up Re: Heated R134A ??

    Quote Originally Posted by craigpcg View Post
    afternoon ppl, I used to work for a large refrigeration company in edinburgh b4 i start my own company but i have a question that id like to ask.

    a few years ago i was at job were the condensor fan motor was faulty causing the system to run EXTEREMLY hot, gas used was R134A. Now the question i ask is after i replaced the fan motor, i place my gauges on to find that system appeared to be short of gas. pressure tested system with ofn to find no leak what so ever.

    now id put it down to the R134A being heated up that much that it had lost its propertes in which it is made up from causing to appear short of gas.

    sooooo i had a little talk with my service manager and he basically laff at me but to this day the system has never lost its gas (as i now have the customer ) and works perfect.

    iv i just lost the plot or am i right???
    Craig.
    Could it not just be that when you replaced the condenser fan.
    The unit condenced more efficiently, lowering the liquid line and suction pressures.
    Fundermental mistake to assume low suction pressure means gas shortage.
    I can only assume that you were refering to a lower suction pressure when using your gauges to diagnose a refrigerant shortage?? Or have I missed something?
    Grizzly

  7. #7
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: Heated R134A ??

    Ian,
    Sorry mate 134a molecule is not the same size as helium and is also larger than OFN.[/quote]

    Can you back this up with a reference ?

    I've always been shown that R134a has a much smaller molecule size, hence we use a 10% helium/nitrogen mix for pressure testing.

  8. #8
    Join Date
    Jun 2001
    Location
    Gloucestershire
    Posts
    13
    Rep Power
    0

    Re: Heated R134A ??

    Nitrogen or OFN is a much smaller molecule than refrigerants which is one of the reasons it is used for leak testing.
    Helium is a smaller molecule than Nitrogen hence a 10% Helium /Nitrogen mixture will find smaller leaks than just OFN. It has nothing to do with the size of the 134a molecule. In fact water is a smaller molecule than 134a which is well documented in filter drier literature.

Similar Threads

  1. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 12:44 AM
  2. r134a as a substitute for r22?
    By m-nelson in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 24-08-2007, 11:16 PM
  3. Pressure Transmitter R134a Setpoints
    By cooltrain in forum Technical Speculations
    Replies: 0
    Last Post: 28-02-2005, 09:05 AM