    what is suitable water flow velocity in Evaporator?



    we are dealing with Hstars Brand heat exchangers, our water flow velocity in evaporator is about 2m/s, however, one of our customer told us that the speed is too much, that will cause cooper vibration, he told me a good and easy solution to reduce velocity at inlets is to increase the nozzle size.

    However, I donot think 2m/s is too fast, anyone tell me what is the right velocity of flow rate?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: what is suitable water flow velocity in Evaporator?

    2 m/s is not too fast. Ask the customer what speed he's fine with, and sell that evaporator to him, under written acceptance of responsibility.

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: what is suitable water flow velocity in Evaporator?

    HELLO CHISTINE,

    We meet again. The velocity of 2 m/s is within the admissable limit. The velocity will also depend on the flow rate. The user has to maintain the parameters. I do not think that there is any need to make any changes to your heat exchangers.

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: what is suitable water flow velocity in Evaporator?

    Quote Originally Posted by chistine
    ...he told me a good and easy solution to reduce velocity at inlets is to increase the nozzle size.
    Are you talking about the tube velocity or the nozzle velocity?
    Last edited by US Iceman; 09-09-2006 at 04:12 PM. Reason: font edit

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: what is suitable water flow velocity in Evaporator?

    Hi,

    Suitable velocities of water in pipes for various types of installation:

    Water:
    - city supply 0,6-1,5 m/s
    - general supply 1,5 - 3,0 m/s
    - boiler supply 2,0 - 3,0 m/s
    - supply of suction pumps
    and disposl pipe-lines 0,75 - 1,5 m/s
    - hydraulic fluid up to 12 m/s

    Hope this will help

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    Join Date
    Nov 2004
    Location
    Sri Lanka
    Age
    77
    Posts
    18
    Rep Power
    0

    Re: what is suitable water flow velocity in Evaporator?

    Hi My Friend,
    The water velocities are clearly defined in the Carrier Air Conditioning Design hand book chapter 3-21.
    Max. water vel. to minimise erosion

    operation Velocity
    hr/year fps

    1500 15
    2000 14
    3000 13
    4000 12
    6000 10
    8000 08

    So 2 m/sec. is not so high (6.6 fps)

    patrickj

  7. #7
    Join Date
    Aug 2006
    Location
    China
    Posts
    15
    Rep Power
    0

    Re: what is suitable water flow velocity in Evaporator?

    Hi, Samarjit Sen,nice to see you here, and thank you Nonickname and partrikj, Thank you all,now I am clear about the water velocity in the Evaporator,however, Mr iceman, I mean the tube velocity,and I actually, want to listen to your opion about the difference about the tube velocity and nozzle velocity.

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: what is suitable water flow velocity in Evaporator?

    The nozzle velocity is wht you find in the water inlet & outlet nozzles to the heat exchanger. On a DX chiller the nozzle velocity may also impact (literally) the tubes. In some designs you may find an impingement plate to provide some protection of the tubes from this.

    Likewise, the tube velocity has several considerations; erosion, keeping the tube clean, or vibration.

    Part of the issue with vibration related issues may be due to the tolernaces of the tubes in the baffles or tube supports too.

    Needless to say there is a lot more more to shell & tube exchanger design than film coefficients or pressure drop.

    Heat transfer is only one function. The mechanical design is a second criteria.