    water cooler



    could u help to design this water cooler:

    *Storage temp 10 c
    *Inlet of water Temp 40 c

    I want to know how to estimate the load (transmission & water) of 2 gallon of water



  2. #2
    Join Date
    May 2006
    Location
    Xi an, China
    Age
    51
    Posts
    65
    Rep Power
    18

    Re: water cooler

    You need to give more parameter as both sides flow, temperature, load to design the chiller, and more info to estimate the load

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: water cooler

    In order to cool 2 US gallons of water (7.57 liters) or 2 UK gallons of water (9.09 liters) from 40°C to 10°C you need 1 Kcal/Kg approx

    Case 1) 7.57 Kcal/°C or 30 BTU/°C
    Case 2) 9.09 Kcal/°C or 36 BTU/°C

    dt = 30°C then

    Case 1) 227.1 Kcal or 900 BTU
    Case 2) 272.7 Kcal or 1080 BTU

    Note this is not cooling capacity: this is ENERGY

  4. #4
    amaryta's Avatar
    amaryta Guest

    Re: water cooler

    *The water cooler is for drinking.
    *This tank will be a product tank or Per cooling tank and it will supply Another tank to be stored there.
    *The comressor run time is 1/2 hour.
    *Desine ambient temp is 46 C 115 F.

    My questions are:
    1-Will i calculate the transmission heat if it is insulated with fiberglass insulation .
    2-How i will select the equipments
    Last edited by amaryta; 11-09-2006 at 04:39 PM.

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: water cooler

    First of all add the heat gain from ambient, considering your insulation.
    Then you have to consider the hourly water consumption.
    Then the desired chilling time must be considered as well.

  6. #6
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: water cooler

    Quote Originally Posted by amaryta View Post
    *
    My questions are:
    1-Will i calculate the transmission heat if it is insulated with fiberglass insulation .
    Hi amaryta , first of all you must choose the thikness of the fiberglass , let say you want a heat transmission of X w/m^2 , you do the calculation and you will have a thikness , if the calculated thikness Y doesn't exist on the market you choose the closest and you do a reverse calculation to see what the new transmission is X' w/m^2 and so on you continue your calculation.

    Remeber insulation will not draw the heat transmission to zero.

    Respects and regards
    Botrous
    Last edited by botrous; 11-09-2006 at 10:46 PM. Reason: Typing errors
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  7. #7
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: water cooler

    could u help to design this water cooler:

    *Storage temp 10 c
    *Inlet of water Temp 40 c

    I want to know how to estimate the load (transmission & water) of 2 gallon of water
    Quote Originally Posted by amaryta View Post
    *The water cooler is for drinking.
    *This tank will be a product tank or Per cooling tank and it will supply Another tank to be stored there.
    *The comressor run time is 1/2 hour.
    *Desine ambient temp is 46 C 115 F.

    My questions are:
    1-Will i calculate the transmission heat if it is insulated with fiberglass insulation .
    2-How i will select the equipments
    First of all calculate the need to cool the water from 40 C to 10 C.
    Q=m * c * deltaT
    m = mass of water to be cooled
    c = thermal coefficient of water
    deltaT = T_entry - T_exit
    Q= the ammount of energy you need to substract from the water

    then do the heat transmission of the tank (it depends of the time you want to store the water in at T=10C)

    If you need accurate results you should also calculate the heat transmission over the pipes.

    We need more details to give you details on how to calculate the compressor capacity. maybe a sketch drawing of your design will help.

    Respects and regards
    Botrous
    Engineering, sciences, math, physics and my brain will generate "not responding " soon