    trane chiller



    was working on a trane chiller model=ECGAL600 system 2 was showing a fault ACKT2 limiting then it cleared it"s self.running pressures look ok. 4bar and 10 half bar i think that fault code means water temp has past set point.am i close to meaning or miles away??



  2. #2
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: trane chiller

    It means load of compressor is limited due to high water temperature to protect itself!

  3. #3
    Join Date
    Feb 2006
    Location
    scotland
    Posts
    13
    Rep Power
    0

    Re: trane chiller

    So it could have shown this reading as a warning.the chiller was swicthed on after being off for a few weeks.thanks for the information

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    621
    Rep Power
    21

    Re: trane chiller

    When the temperature is too high the machine will protect itself, because the pressure will get too high!