    Hitachi



    Hi,
    I have a problem with a Hitachi multizone unit:
    RAM65QH5 (inverter) with three indoor units RAK18NH5

    The unit do not give correct cooling capacity the different between inlet temp and outlet temp. on the indoor units is: in 22°C out 17,5°C. The set temp is 16°C. With that different between indoor and set temp. shall the speed on the unit be around 4000 rpm but it just give 2000 rpm. I have try to replace the outdoor unit, and fill it up with correct amount refrigerant. But nothing of this have helped.

    Any idés?



  2. #2
    Join Date
    Dec 2003
    Location
    uk
    Age
    51
    Posts
    62
    Rep Power
    21

    Re: Hitachi

    If there is a fault the led on both indoor and outdoor unit should flash in a certain sequance.

    The electric cover on outdoor unit has diagnosis chart to help determine the fault.

    If you are not getting a fault led then i would look at the cappacity / load of the room and compare to see if the indoor unit is too small for the job.

    Try it in heating mode on full for 20 mins, What are the results?

    Charge is very critical so did you weigh the gas..

    Also are all indoor units doing the same or is it just on or two?

    How many compressors? one or two, Its been a while since i looked at the multizone.

    Good luck

  3. #3
    Join Date
    May 2005
    Location
    sweden
    Posts
    5
    Rep Power
    0

    Re: Hitachi

    Hi chilly,
    Thanks for your answer. There is just one compressor and all indoor units are the doing the same. There is no leds falshing. Anyway I will go to the site this week and recharge the unit this time by weight.

    I have to succed the owner is not so happy.

    Thank You

  4. #4
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: Hitachi

    how meny indors dose the unit have, it migth be that the total indoor capacity is grater then the outdor , at list at DAIKIN this is posible , and if u have started all the indors, the outdor can't get all the indoors covered

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Hitachi

    It's got to beg the question - is it sized correctly for the indoor load?

    The system appears to be OK with 54000btu indoor units coupled to 65000btu outdoor unit but the small dt on the indoor leads me to think that the indoor load is too high.

  6. #6
    Join Date
    Jul 2006
    Location
    uk
    Age
    45
    Posts
    49
    Rep Power
    0

    Re: Hitachi

    I used to work for one of hitachi's main distributors and i was told a few years ago that although the controller could be set at 17 the unit would only control to 19. This is on the older ras range of equipment though. I also agree with chilly, charge is critical on these units.

  7. #7
    Join Date
    May 2005
    Location
    sweden
    Posts
    5
    Rep Power
    0

    Re: Hitachi

    Hello friends,
    The problen is solved it was the charged of refrigerant.

    Thanks for all your help

  8. #8
    Join Date
    Dec 2003
    Location
    uk
    Age
    51
    Posts
    62
    Rep Power
    21

    Re: Hitachi

    Back of the net

Similar Threads

  1. Hitachi Air-con Problem
    By oddjob in forum Air Conditioning
    Replies: 10
    Last Post: 12-05-2008, 01:46 AM
  2. Hitachi Details
    By Slim R410a in forum Air Conditioning
    Replies: 4
    Last Post: 29-06-2006, 10:20 AM
  3. hitachi utopia g7 r404a not up to cooling
    By peter1927 in forum Trouble Shooting
    Replies: 12
    Last Post: 16-01-2006, 03:19 AM
  4. F**K Hitachi
    By rbartlett in forum Air Conditioning
    Replies: 38
    Last Post: 24-10-2005, 05:12 PM
  5. Hitachi central controller
    By al in forum Air Conditioning
    Replies: 5
    Last Post: 28-09-2005, 07:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •