    defrost on freezer coldroom



    I have a freezer coldroom with two seperate systems.
    A control panel for each system. One system has a conventional defrost timer with built in fan delay and an eliwell controller (stat only) ie 1 relay. There is an evap
    termination stat as well.

    The other system has an eliwell 974 controller - 3 relays fan def comp.

    The problem is they defrost at different times. so one maybe cooling while the other is defrosting.

    What would be the best way to adapt them to defrost together.

    Many thanks andy



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: defrost on freezer coldroom

    Sounds as though you want to control both systems with just one controller.

    Can you take control signals from the 974 control system and connect them to the other control panel?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2003
    Location
    uk
    Age
    51
    Posts
    62
    Rep Power
    21

    Re: defrost on freezer coldroom

    Agree with brian..

    Or change the controler so they match.

  4. #4
    Join Date
    Jan 2006
    Location
    uk
    Age
    50
    Posts
    10
    Rep Power
    0

    Re: defrost on freezer coldroom

    Yeah! this can easily be done and have thought of doing it.
    The only thing is that if the system with the coil probe attached has a gas leak or any other outdoor unit problem the other system wont start too due to coil temp.
    The customer would have to accept that it would now be one complete sytem and defrosting efficiently.

    Cheers!!

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: defrost on freezer coldroom

    There's a Digital input on the models with an LX behind the type (cost almost nothing more then the conventionale version, and therefore, we only use LX models) which you can activate via parameter H21 till H32 as a defrost cycle.
    This input from controller 2 comes from controller 1.

    Carel has a range with the same possibilities.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: defrost on freezer coldroom

    Hi

    Surely the whole point of having two seperate systems is for them to back each other up, working independently and defrosting at alternate times so as there is not a massive temp drop.

    Regards Bernard

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: defrost on freezer coldroom

    Quote Originally Posted by bernard
    .. working independently and defrosting at alternate times so as there is not a massive temp drop.
    When you defrost 2 evaporators in a freezer at different times, then much of the heat generated in the defrosted one will be lost in the roo mdue to air movement of the running one, unless you can shut it off mechancially while defrosting.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  8. #8
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: defrost on freezer coldroom

    theres two ways of looking at this as bernard and peter says, why do you want to alter it?,is there a problem with the defrost?,if the coolers are not to close to each other i would leave it as is so the systems are independant,if they can influence each other peter has bought up a very important point,as a rough guide,the coolers need to be approx 3mtr apart mounted on the same cieling,facing the same way to be independant, otherwise i would adapt or build a new panel with inerlocks on the contactors,fully protect all the major components with MCB,s then you will still have a good level of back up.dont forget to set the elliwell so in the event of a probe failure it still runs.

  9. #9
    Join Date
    Jan 2006
    Location
    uk
    Age
    50
    Posts
    10
    Rep Power
    0

    Re: defrost on freezer coldroom

    the coldroom is approx 4m x 4m and both evapourators almost face each other but are slightly offset so if you can imagine they are in opposite corners and recirculating one anothers air.

    I think it was originally designed as a blast freezer but the customer no longer needs this application as everything goes in at -18 or below.

    The room will achieve -21 on one system but the customer likes both systems operating and this is when the problem starts as ice slowly starts to accumulate around both coils and ecspecially the driptrays.

    This is due to the fact that one will be trying to defrost whilst the other is in cooling mode and temperatures are well below sub zero.

    I'll take a look at the LX and carel range and decide what to do like you suggest Bernard I will certainally
    modify it to keep both systems in operation indepandant of each other except for defrost in case one does fail.

    Thanks for your input guys
    andy

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: defrost on freezer coldroom

    If one system is capable of holding the load then they should be used as run/standby (duty sharing) - not both at the same time.

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: defrost on freezer coldroom

    Quote Originally Posted by frank View Post
    If one system is capable of holding the load then they should be used as run/standby (duty sharing) - not both at the same time.
    Well, or as we set the thermostats.

    Thermostat 1 at -20°C and 2°C DT is starting at -18°C and stopping at -20°C.

    The 2nd at -17°C and a DT of 3°C or -16°C and a DT of 4°C so that it's ready as a back up and pulls the freezer to the same initial temperature of -20°C, eventually togetehr with n°1.

    2 will also start then when room for some reason comes too warm (for example introducing fresh goods)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: defrost on freezer coldroom

    if your looking at controlers i have found the carel IR33 range really good for freezer room aplications especially the one with real time clock built in, (cant think of the model # atm).

    IR33COHBOO - is the controlers i have been using.
    Last edited by Bones; 01-09-2006 at 10:18 AM.
    "Old fridgies never die, they just run out of gas!"

Similar Threads

  1. walk in freezer refrigeration sizing?
    By trammd in forum Technical Discussions
    Replies: 10
    Last Post: 02-11-2006, 11:56 AM
  2. Freezer operation in my garage
    By sonjand in forum Fundamentals
    Replies: 5
    Last Post: 02-08-2006, 10:25 PM
  3. please help with Kenmore Upright Freezer
    By lrn376 in forum Trouble Shooting
    Replies: 0
    Last Post: 09-07-2006, 10:40 PM
  4. Hot Gas vs. Electric Defrost
    By herefishy in forum Technical Discussions
    Replies: 26
    Last Post: 08-03-2005, 07:50 PM
  5. Fan quit in freezer compartment.
    By odam2k in forum Trouble Shooting
    Replies: 4
    Last Post: 05-07-2003, 02:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •