    Can an inverter run off an indoor socket?



    Been talking to an engineer today & was told that a Daikin 3.5KW inverter air conditioner can run off a 13amp ring main socket with the correct power breaker. Is this correct as the maximum load it will pull is 6.5- 10.5 amps. Even Daikin say its possible, will run ok but not recommended as a failing unit could pull up to 16amps. Then again wouldn’t a power breaker cut off at 10-13amps?



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: Can an inverter run off an indoor socket?

    I have seen a Daikin 71, quite a few 68's, loads of 50's, and squillions of 3.5/2/5/2.0/etc inverter(s) running off a 13a fused spur -and I have never gone to one with a blown fuse yet...

    I must admit to laughing at the recent 20a c/b thread and the ratings some are coming out with.

    As an example Daikin rate their in ceiling VRV ahu's at 16 a !! yes 16a for an indoor board and a 50w fan motor pulling less than one amp!!

    Our last VRV the sparks was adamant that we simply could not run a ring main round for all the indoor units and each should be fed 16a separately as that is what the indoor unit marked as.
    In the end I told him "just do it and I'll cover it and oh by the way change the 13a for a 6a while you're at it"

    I need to get my head round Daikins logic -the unit normally pulls 4 a but they want you to run a 16a supply as 'a failing unit can pull 16a'

    Personally I want my unit to switch off long before it's pulling 4x normal current.-and believe me 10a on a 3.5kW is NOT normal before you say..

    Cheers

    Richard

  3. #3
    Join Date
    Aug 2006
    Location
    London
    Posts
    8
    Rep Power
    0

    Re: Can an inverter run off an indoor socket?

    Quote Originally Posted by rbartlett
    I have seen a Daikin 71, quite a few 68's, loads of 50's, and squillions of 3.5/2/5/2.0/etc inverter(s) running off a 13a fused spur -and I have never gone to one with a blown fuse yet...

    I must admit to laughing at the recent 20a c/b thread and the ratings some are coming out with.

    As an example Daikin rate their in ceiling VRV ahu's at 16 a !! yes 16a for an indoor board and a 50w fan motor pulling less than one amp!!

    Our last VRV the sparks was adamant that we simply could not run a ring main round for all the indoor units and each should be fed 16a separately as that is what the indoor unit marked as.
    In the end I told him "just do it and I'll cover it and oh by the way change the 13a for a 6a while you're at it"

    I need to get my head round Daikins logic -the unit normally pulls 4 a but they want you to run a 16a supply as 'a failing unit can pull 16a'

    Personally I want my unit to switch off long before it's pulling 4x normal current.-and believe me 10a on a 3.5kW is NOT normal before you say..

    Cheers

    Richard
    I had to scratch my head and wonder what the so called technical expert at Daikin was talking about. Told me at start up it would pull about 4.5amps & at max would be about 6.5amps. But they still recommended 16amp supply just incase. But with a 16A supply I’d only know I had a faulty unit either after it went bang or I got my electricity bill. Think I’ll run it off an 13A spur & save myself about £200.

  4. #4
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Can an inverter run off an indoor socket?

    I understand it to be that the fuse rating is to protect the cable not the appliance. For instance TV's,Fridges,Hairdriers all come with a 13Amp fuse in the plug put they pull no where near that. Every appliance should be internally fused like all Daikin units, Mitsi units and so on. I think this is the way it works but ive been wrong before.

  5. #5
    Join Date
    Aug 2006
    Location
    London
    Posts
    8
    Rep Power
    0

    Re: Can an inverter run off an indoor socket?

    Thought TV’s were 3-5amps.
    I think I remember doing electronics at college many years ago & the fuse rating was always done by the maximum load the appliance would / might use. Now if Daikin & other manufactures are saying use a fuse rating up to four times the maximum input power just incase the compressor goes wrong then:
    1. The internal fuse has to be 16 or more amps to allow the compressor to pull that amount for current.
    2. Letting the compressor pull that sort of load if its faulty is going to do more harm then good.

  6. #6
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Can an inverter run off an indoor socket?

    I all ways calculate my breaker circuits for 1.5% of max load, this allows for inrush nicely for fast blow fuses or use max inrush and a slow blow.

    either way I want it to break the circuit if any anomaly is on there.

  7. #7
    Join Date
    Mar 2006
    Location
    Glasgow, Scotland
    Posts
    177
    Rep Power
    19

    Re: Can an inverter run off an indoor socket?

    Work this one out then Daikin Technical databook states MFA@15A for a RXS35CVMB but the internal fuse on the unit is 20A. Im really confused now not that it takes much to confuse me! LOL

  8. #8
    Join Date
    Dec 2003
    Location
    uk
    Age
    51
    Posts
    62
    Rep Power
    21

    Re: Can an inverter run off an indoor socket?

    16a to feed a ring main with up to 16 units and im happy, Individualy fuse an indoor with a 5 amp, If the unit blows the 5 amp fuse there is sopme thing wrong. I dont want to allow the unit to pull more than 5 amps.
    I love design engineers covering their arses at the expence of the trade.

    Old school.

  9. #9
    Join Date
    Aug 2006
    Location
    London
    Posts
    8
    Rep Power
    0

    Re: Can an inverter run off an indoor socket?

    Quote Originally Posted by puddleboy3 View Post
    Work this one out then Daikin Technical databook states MFA@15A for a RXS35CVMB but the internal fuse on the unit is 20A. Im really confused now not that it takes much to confuse me! LOL

    You've confused me as well

  10. #10
    Join Date
    Nov 2005
    Location
    Liverpool
    Age
    49
    Posts
    56
    Rep Power
    19

    Re: Can an inverter run off an indoor socket?

    I have just found TWO RSX60 invertors running off ONE 13a plug! I spluttered in horror, only to be told that the units had run hapilly all summer. I'm not condoning this, but the plug was only slightly warm and there were no signs of it over heating...which suggests we should take some of the specified ratings with a pinch of salt!

  11. #11
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: Can an inverter run off an indoor socket?

    Quote Originally Posted by daddymac View Post
    I have just found TWO RSX60 invertors running off ONE 13a plug! I spluttered in horror, only to be told that the units had run hapilly all summer. I'm not condoning this, but the plug was only slightly warm and there were no signs of it over heating...which suggests we should take some of the specified ratings with a pinch of salt!
    Dont forget that there is a difference between the closeness of protection between MCB's Cartridge fuse and open wired fuses. MCB's being the closest and Open wired fuses the other end.

    PLug running hot? What the socket or the plug itself?

    In the case of the 'plug top' that could be due to a poor connection on the cartridge fuse, but would probably show discoloration. Or it could be the cartridge fuse itself running close to its max load and heat being conducted from it to live pin and clips?

    This would possibly lead to a 'tired' cartridge fuse failure after time, due to running close to fuse failure rating.

    Breaking open a failed cartridge fuse and examining the wire ends under a high power lens reveals cause of failure. Sharp irregular end = Blow due to fault, and subsequent high current flow.
    'Blobs' on ends = melt due to overload.

    Myself I prefer close protection of correct rated MCB if its not too much extra work. You can get MCB's for about a fiver.

    Dont forget the emergency isolator next to the outside unit however its fed 13a or MCB.

    See also elswhere here about failures of RCD's due to inballance in the live and neutral sides due to current in the control wire?

  12. #12
    Join Date
    Nov 2005
    Location
    Liverpool
    Age
    49
    Posts
    56
    Rep Power
    19

    Re: Can an inverter run off an indoor socket?

    I'd never thought of breaking a cartridge fuse open to determine the characteristic of failure! Good idea!
    Oh! For the record, I'd never condone 2 units running off a 13a plug, and I'm with you on MCB's, and certainly ext isolators!! I was just suprised that this dodgy arrangement hadn't caused a problem!

  13. #13
    Join Date
    Jul 2006
    Location
    Northern Ireland
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: Can an inverter run off an indoor socket?

    Hi .... I'm going to fit a new Mitsubishi Heavy in my own house at the weekend....A SRK35ZD 3.5kw R410A Inverter unit It has no start current and runs at 5amps( isn't that about the same as a 32" TV or a large Fridge Freezer?) so the 13amp socket is what i'm going to use..... With 5amp fused spur at indoor and local isolator at condenser ......can't see a problem with that.

  14. #14
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Can an inverter run off an indoor socket?

    I can't see a problem also providing the ring main isn't overloaded with your 5A.

    What fuse are you going to put in your plug top?

    From memory, they come in 3A, 5A, 10A, 13A.

    I would go for a 10A (twice the running current) which should give you loads of protection in the event of a problem. 5A might trip.

  15. #15
    rbartlett's Avatar
    rbartlett Guest

    Re: Can an inverter run off an indoor socket?

    Can a mod lock these two threads as it's just going round and round in circles and I'm losing the will to live..?

    oh and those self installing please please please please for gods sake just bloody well get on with it the warranty will run out before it's installed......


    cheers

    Richard

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Can an inverter run off an indoor socket?

    AAhh com'n Richard - the thread is only 15 posts long. Plenty of room yet for repeat answers, repetitive questioning, circular thingies, more fun etc.

    Someone is bound to post yet with an interesting question like - HELP! I've got a nasty cold burn and the house electrics have just caught fire - what do I do now

Similar Threads

  1. noise inverter compressor
    By Airclima in forum Air Conditioning
    Replies: 1
    Last Post: 26-07-2007, 11:42 PM
  2. Inverter systems
    By Latte in forum The Trail of Tears
    Replies: 23
    Last Post: 11-07-2007, 12:14 AM
  3. Super inverter or 3 phase
    By Cooldawg in forum Air Conditioning
    Replies: 7
    Last Post: 24-08-2006, 11:35 PM
  4. strange inverter problem
    By rbartlett in forum Air Conditioning
    Replies: 11
    Last Post: 19-05-2006, 08:31 PM
  5. A/C Inverter
    By Jai in forum Air Conditioning
    Replies: 2
    Last Post: 06-11-2001, 01:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •