    Compressor replace



    Hi experts,
    I have MBP hermetic compressor (Emraco J9226GK)
    It has evaporating temperature range from -20C to +15C

    Can I replace it by LBP compressor (Danfoss SC21CL),which has evaporating temperature range from -45C to -10C ?

    Or I have to select HBP compressor (L'Unite Hermetique
    CAJ 4517Z),which has evaporating temperature range
    from -25C to +10C ?
    All compressors for R404A.

    What do you mean about compressor manufactures
    Embraco
    Danfoss
    L'Unite Hermetique
    Elektrolux
    Thanks for any advice.



  2. #2
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: Compressor replace

    Whats the application
    What is the cab temp you trying to achieve?

  3. #3
    Join Date
    Jul 2005
    Location
    Belarus
    Age
    51
    Posts
    26
    Rep Power
    0

    Re: Compressor replace

    Hi Abe
    Integral multideck cabinet should supply temperature
    from 0C to +7C

  4. #4
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    504
    Rep Power
    21

    Re: Compressor replace

    Go with the HBP. fitting the LBP on that unit is an invitation for a burnout.
    Takes a licking, keeps on ticking.

  5. #5
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26

    Re: Compressor replace

    Quote Originally Posted by slingblade
    Go with the HBP. fitting the LBP on that unit is an invitation for a burnout.
    As Sling says.........its got to be High Back Pressure


  6. #6
    rbartlett's Avatar
    rbartlett Guest

    Re: Compressor replace

    Quote Originally Posted by slingblade
    Go with the HBP. fitting the LBP on that unit is an invitation for a burnout.
    I know what you mean but I remember seeing two idnetical LBP l'unite condensing units both on 502 one running a freezer room and the other doing the coldroom. Both worked perfectly happliy.
    I ponder to think the main difference is in the compression ratio and possibly motor differences and providing a decent S.H will normally be ok.

    Of course the correct thing would be to go HBP but sometimes life can be difficult...

    Cheers

    Richard

  7. #7
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Compressor replace

    Quote Originally Posted by rbartlett
    I know what you mean but I remember seeing two idnetical LBP l'unite condensing units both on 502 one running a freezer room and the other doing the coldroom. Both worked perfectly happliy.
    I ponder to think the main difference is in the compression ratio and possibly motor differences and providing a decent S.H will normally be ok.

    Of course the correct thing would be to go HBP but sometimes life can be difficult...

    Cheers

    Richard
    We bought a cold room off Foster for -22 deg c. It came with R134a and would not pull lower than -13 deg c. Wwe changed the gas to R404a, the compressor was suitable for the pressures, room flew down and never looked back

    Seems Foster have the same unit for chill and deep freeze, they just change the gas to suit

    If your LBP compressor is R404a, you could run it on R134a for a MBP or HBP application.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Compressor replace

    Whats wrong with the MBP?

  9. #9
    rbartlett's Avatar
    rbartlett Guest

    Re: Compressor replace

    Quote Originally Posted by Andy
    We bought a cold room off Foster for -22 deg c. It came with R134a and would not pull lower than -13 deg c. Wwe changed the gas to R404a, the compressor was suitable for the pressures, room flew down and never looked back

    Seems Foster have the same unit for chill and deep freeze, they just change the gas to suit

    If your LBP compressor is R404a, you could run it on R134a for a MBP or HBP application.

    Kind Regards Andy
    And i used to engineer these units

    http://www.pkl.co.uk/foodservices/coldrooms.asp

    and they were a coldroom or freezer by swapping power from one eliwell controller preset at +1 to another preset at -20 deg c ....



    Cheers

    Richard
    Last edited by rbartlett; 24-08-2006 at 07:38 PM.

  10. #10
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Compressor replace

    i think he,s saying his MBP pots dead and wants to use a LBP,even if its a cappilary system it will expire in no time,as the guys advise you,go HBP with start capacitor,andy thats intersting about that foster freezer,must have been a friday afternoon job, was it hot gas defrost aswell? bet it grunted a bit if it was.

  11. #11
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    504
    Rep Power
    21

    Re: Compressor replace

    Quote Originally Posted by rbartlett
    And i used to engineer these units

    http://www.pkl.co.uk/foodservices/coldrooms.asp

    and they were a coldroom or freezer by swapping power from one eliwell controller preset at +1 to another preset at -20 deg c ....



    Cheers

    Richard

    I to have worked on dawson rental boxes which will work chiller or freezer at the flick of a switch. the biggest factor here is they are designed to do just that. a crank case pressure regulator stops overloading during pulldown, after defrost termination or higher temp. operation especially in high ambient conditions. 404A multidecks are not quite the same, think back 3 or 4 weeks to the sweltering summer we experienced. air on evap. 25/35 deg c. 404 can run nasty discharge temps at the best of times but on an open fronted unit in those conditions, it begs burnt oil blocked capillarys and premature failure.
    lets face it, how many of us have had burnt fingers from touching a running compressor to check how cold it is?


    We bought a cold room off Foster for -22 deg c. It came with R134a and would not pull lower than -13 deg c. Wwe changed the gas to R404a, the compressor was suitable for the pressures, room flew down and never looked back

    Seems Foster have the same unit for chill and deep freeze, they just change the gas to suit
    Im surprised one came out of the factory like that, did you get a credit for the rectification work?


    Just my thoughts,

    regards all.
    Takes a licking, keeps on ticking.

  12. #12
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24

    Re: Compressor replace

    Quote Originally Posted by old gas bottle
    andy thats intersting about that foster freezer,must have been a friday afternoon job, was it hot gas defrost aswell? bet it grunted a bit if it was.
    Yep hot gas defrost, with a water cooled condenser and a remote dry air cooler.

    Was R134a on the plate, charge and all stamped. One of my engineers, decanted and recharged to the correct charge, again with R134a, still wouldn,t come down in temp.
    I was on site, looked at it, compressor was R404a, the pressure switch for bringing on the cond pump was even set for 12 bar. I said to try recharging with R404a, as the compressor was fit for it.
    The things a bloody blast freezer now

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  13. #13
    Join Date
    Mar 2007
    Location
    England
    Posts
    34
    Rep Power
    0

    Re: Compressor replace

    Was R134a on the plate, charge and all stamped. One of my engineers, decanted and recharged to the correct charge, again with R134a, still wouldn,t come down in temp.
    I was on site, looked at it, compressor was R404a, the pressure switch for bringing on the cond pump was even set for 12 bar. I said to try recharging with R404a, as the compressor was fit for it.
    The things a bloody blast freezer now
    No disrespect but on the data plates they also include the type of gas which is used in the insulation of the panels/sides which as it happens is R134a