    Parker Hanifin Flo-Con



    Hello..sort of a newbie here.

    Have a Kramer 62 HP low temp system with hot gas defrost capabilities (thermobank system). Freezer runs at -16 F and the system runs pretty smooth during normal operation. when put into defrost, the suction and discharge valve closes and the holdback valve slowly modulates the liquid into the bank and maintains for a few moments at 20 psig until it looses control for awhile until it regains control again. During that time quite a bit of liquid has accumulated in the accumulator. Once the valve recovers, the system defrosts within 10 minutes. Only problem is I don't think these compressors can take this much of flooding abuse before we loose a wrist-pin or valve plate.

    I've moved the cap. from the outlet of the bank to the inlet for the holdback valve and lowered the discharge pressure control from 300 psig to 250. I'm just wondering with such a large system and short piping run that I might be building up too much head pressure during defrost that the flo-con can't respond fast enough. I can't explain the sudden increase in suction pressure for the life of me during defrost.

    Have quite a bit of expierience with these systems over the last 20 years and have never seen anything like this before. I'm thinking to much of all the the possible scenerios that may be going on and it might be time to throw it out to this forum for possible solutions.



  2. #2
    Join Date
    Apr 2009
    Location
    home
    Posts
    32
    Rep Power
    0

    Re: Parker Hanifin Flo-Con

    What refrigerant? And how is the discharge superheat? What temp is the suction line?

Similar Threads

  1. Parker vs. Sporlan filter driers - any difference?
    By Jeremy Martin in forum Technical Discussions
    Replies: 6
    Last Post: 27-09-2010, 10:48 PM
  2. Tony Parker
    By p_p in forum Chit Chat & Service Stories
    Replies: 0
    Last Post: 14-01-2010, 07:03 PM
  3. Parker A4AS Valve Issue
    By brian_chapin in forum NH3
    Replies: 8
    Last Post: 16-02-2009, 07:41 AM
  4. Welcome Ian Parker!
    By WebRam in forum New to RE
    Replies: 0
    Last Post: 20-10-2005, 04:05 PM
  5. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •