    Oct 2005
    United Kingdom
    11
    Water Chiller Evaporator Leaks
    Has anyone else experienced an excessive amount of shell and tube evaporator failures lately? I haven't seen one for quite a while and now I have had 2 in 6 weeks. I have pulled the bundle from one machine and found two pinholes in the same line within a foot of each other. No sign of freeze up etc, it just looks like poor quality copper has been used.
    Whisty
    Aug 2005
    5,302
    Re: Water Chiller Evaporator Leaks
    Hi Whisty,
    Where were the holes in the tubes?
    Close to the tube sheets?
    Sep 2005
    uk
    499
    21
    No, not done one for a while. does remind me of two chillers around the 300 kw size piped to a bulk tank which a company flushed with acid. only problem was the flush was supposed to be 24 hours but for some reason they left it in for 2 months, the result was very amusing indeed, and costly.
    Takes a licking, keeps on ticking.
    Oct 2005
    United Kingdom
    11
    There were no known "water treatment" issues and the tube has pinholed midway between baffles.
    I only ask since there have been rumours circulating lately that copper quality on some manufacturers chillers has been suspect due to cost cutting.
    Whisty
    Dec 2005
    Johor
    151
    Hi Whisty,
    Conduct proper Eddy Current Inspection on those vessels.
  1. Water Chiller Control
    By David PS in forum Air Conditioning
    Last Post: 29-08-2006, 11:14 PM
  2. Mcquay PES Flooded Water Cooled Screw Chiller
    By Brian in forum Technical Speculations
    Last Post: 05-07-2006, 09:43 PM
  3. water chiller
    By andrewuk in forum Technical Speculations
    Last Post: 17-10-2005, 09:28 PM
  4. Building a wine cabinet
  5. water chiller
    By dwallan in forum Air Conditioning
    Last Post: 12-12-2001, 03:17 AM