    Enyone experienced oil problems with this compressor. Have just got delivered 2 of these. And when starting they run, and sound normal. But after 10 min they start squeeking from the cylinders. Have measured the oil pressure and everything seems ok. Have also disassembly the oil pump, the back bearing and blowing nitrogen everything + the shaft..Everything seems ok. But the oil pressure drops suddenly, and there is not running eny oil thrugh the shaft.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: 8 cyl. Frascold

    I never used them but is rotation correct ( can oil pump run CW and CCW?),
    You're sure the compressor is getting 100% superheated refrigerant?
    I should not hesitate if these are new machines, call your wholesaler and he should solve this problem for you.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: 8 cyl. Frascold

    Is the oil the correct type as recommended by the manufacturer?

  4. #4
    Join Date
    Jul 2006
    Location
    Copenhagen
    Posts
    39
    Rep Power
    0

    Re: 8 cyl. Frascold

    The oil is the right one (GS4). The compressor dosent have eny rotation arrows, and the pump is a sprocket (dont know the right word), but they work no matter what the rotation is. The superheat is 10 degrees C, across evaporator, and the there is a heat exchanger between suction/ liquid.

  5. #5
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    191
    Rep Power
    19

    Question Re: 8 cyl. Frascold

    Superheat on evaporator outlet reduce to 5C.Also how many delt p you have on oil pump.Does compressor shake?Does it have crankcase heater?Does have oil separator?
    Does it have suction acumulator?How many kg of oil did you put in compressor?

    Renato

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,326
    Rep Power
    25

    Re: 8 cyl. Frascold

    Quote Originally Posted by ConDor
    But the oil pressure drops suddenly, and there is not running eny oil thrugh the shaft.
    I'm not familar with your compressors, but can offer this comment.

    On open drive recip. compressors the oil is usually picked up in the crankcase by a strainer on the oil pump suction line. The actual oil flow through the compressor needs to be studied.

    I have heard of several cases where the oil pump would produce pressure at the oil pump itself, but no oil flow to the crankcase.

    I believe the problem was due to the shaft seal leaking internally, which relieved all of the oil pressure back to the crankcase, with no oil flow through the crankshaft.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: 8 cyl. Frascold

    I'm very much familiar with those compressors, we use hundreds per year.
    Squeaking can be caused by two common situations: liquid flooding, but if it shakes, than it is a plate valve leaking.
    Recently they had a number of casted iron WIPs not correctly washed out, and so some dirt was trapped. Those small particles were nasty for the valve plates.
    If it's an 8 cilinders, than it is either a W70 206 or W80 240, both terribly unreliable.

    EDIT: I just see this thread. Sorry for not answering before