Results 1 to 6 of 6

Thread: Glycol

  1. #1
    jflaherty's Avatar
    jflaherty Guest

    Post Glycol



    What is the best mixture for an ice bar which is a system designed to create a solid ice section of a bar. We have been told by the installer that the mixture of glycol and water should be 40/60 respectively. We were running on a mixture of 73/30 glycol/water but were told that this is wrong, can anyone help.
    Last edited by jflaherty; 10-02-2002 at 06:42 AM.



  2. #2
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    For such an application, 40/60 should be more than enough for a 0 deg F surface, which is likely colder than you need to frost the surface. No harm in adding more glycol, though, other than the minor additional expense.

    But don't use a 73/30 mix. It spills all over the floor.

  3. #3
    Join Date
    Oct 2001
    Location
    Georgia, USA
    Posts
    58
    Rep Power
    23
    I would get the specifications of the glycol used and follow their
    reccomendations to obtain the proper mix for the application. Typically look for a freeze point about 20*F lower than what you are cooling. You can make the mix too rich which could actually raise the freeze point and cause high viscosity and resultant flow problems. After you figure it out test it on a regular basis or send a sample out to a lab for analysis. Even though it is a sealed system the mix can turn sour and create problems down the road. Also consider toxicity, the solution you are using may be toxic and or enviromentally unfriendly. If it is toxic what are the consequences if it leaks out on the bar ? Propylene glycol is considered non toxic although it is more expensive. What are you using?
    Mike Hopkins

  4. #4
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    Mike, I was assuming a solid stainless cold wall plate where the fluid wouldn't be a concern. But a cold plate application shouldn't reflect a 20 deg F TD, should it? I assumed that a nice frost was what was desired.

    Jim! What effect does your customer desire, and how is it displayed? My experience is limited to frosting surface displays. Perhaps you have something more demanding?

  5. #5
    Join Date
    Jun 2001
    Location
    Delaware
    Age
    63
    Posts
    11
    Rep Power
    0
    Dan is right you should be OK down to zero with a 40/60 solution but I wouldn't go much over 60/40 as you start coming back up the scale as you get closer to 100 % glycol. 60/40 is good down to at least -40 F. and that should be plenty for what you are doing.

  6. #6
    Join Date
    Aug 2001
    Location
    Leominster, MA
    Age
    71
    Posts
    45
    Rep Power
    0
    The maximum freeze protection is 69% glycol and as stated earlier the more glycol added the freeze point rises. The other consideration is heat transfer. When the glycol percentage rises heat transfer is reduces or slowed down. The other thing to think of is protecting the chiller barrel. The duo-check glycol tester will tell you your protection level.
    My wife says I don't listen to her....or something like that....

Similar Threads

  1. glycol charts
    By Feargal Loy in forum Technical Speculations
    Replies: 2
    Last Post: 28-03-2010, 03:19 AM
  2. Milk getting into glycol on chill press
    By balerjoe in forum Trouble Shooting
    Replies: 16
    Last Post: 06-09-2005, 09:41 PM
  3. Glycol Back To Refrigerant
    By JIMMYBOY in forum Supermarket Refrigeration
    Replies: 4
    Last Post: 16-08-2005, 10:54 PM
  4. Glycol water valves
    By eng_ab in forum Industrial
    Replies: 2
    Last Post: 03-06-2005, 09:15 PM
  5. which glycol to use ?
    By dchatta in forum Refrigerants
    Replies: 4
    Last Post: 12-07-2004, 09:26 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •