    Question YORK ducted split



    HI

    I want to ask you guys if anyone have exp' with the york brand.
    This unit have an orfice in the liquid line and from what i understand this orfice is for the heat cycle.

    My Q is:
    Did anyone expiriance any problems with HP during heating?
    I'm talking about 350 psi on 70 LP (R-22)
    During cooling cycle the pressurs are fine 50-200psi
    the problem is only when heating.

    now:
    Last time I had this problem with another york unit i changed the RV and the preformance were better.
    this time i also changed thr RV but still I'm getting around 320 psi
    I cacked airflow,filters,ducts,charge
    I'm thinking that maybe york had problems with those ducted splits?
    I know that on heating usualy you get higher pressurs but this looks abnormal

    If anyone can help that will be mutch apreciate.
    Thank you



  2. #2
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: YORK ducted split

    Please give details of exact location of the orifice which is installed in the liquid line i.e within the condensing unit or outwith?

    regards
    Jase

  3. #3
    Join Date
    May 2006
    Location
    Melbourne,Australia
    Posts
    38
    Rep Power
    0

    Re: YORK ducted split

    Hi
    The orfice is located at the exit of the outdoor unit on the liquid line
    I know from past exp' that other compenies used this kind of orfice for the heating cycle but i didnt recall pressurs problems
    After replacing the RV i cant think of other problems because if there were any other problems i think i could see it in cooling stage as well???????
    Thank you for your reply
    cheera

  4. #4
    Join Date
    Feb 2005
    Location
    Aberdeen
    Age
    48
    Posts
    168
    Rep Power
    20

    Re: YORK ducted split

    By what you are explaining, it sounds like one of those 'bullet-type' restrictor expansion devices that is installed within liquid line. If so, then this is only used for cooling purposes. Is the evaporator capillary fed and is there any sort of expansion device within the condensing unit?

    Regards
    Jase

  5. #5
    Join Date
    May 2006
    Location
    Melbourne,Australia
    Posts
    38
    Rep Power
    0

    Re: YORK ducted split

    Hi again

    This is not a bullet type restrictor but like a nuzlle orfice and I am quite sure that it's for the heating cycle.
    when I changed the r.v I opened the orfice and it wasn't block.
    The capilary is in the indoor unit.
    I am trying to think why they put this restrictor??????????????????????
    anyway it looks like those units work on hige pressurs in heating(no problem in cooling).
    I remember some kind of capilary in the condense unit but i'm not sure

    thanks
    regards
    Al

  6. #6
    Join Date
    Sep 2006
    Location
    Bribie Island , Queensland
    Age
    61
    Posts
    19
    Rep Power
    0

    Re: YORK ducted split

    This restrictor is a slide type accurator which allows expansion when in heating mode and allows full bypass when in cooling. There is usually a matching one at the indoor unit inside the brass connection of the liquid line.The orifice has a number on it which should match the capacity of the unit. Check with York to make sure that the correct orifice is fitted. If the liquid line is lagged , you can get rid of both the indoor orifice and the outdoor one and replace with a correctly sized capillary.
    Last edited by RickSter; 09-09-2006 at 05:06 AM.

  7. #7
    Join Date
    Apr 2007
    Location
    Phillipine
    Posts
    22
    Rep Power
    0

    Re: YORK ducted split

    Hi,
    York uses orifice instead of TXV. The orifice in the outdoor unit is first version of it and it is modify and put inside any fan coil unit. The problem with the orifice it has small inlet that usually clog up. Sometime it malfunction that is the reason it is converted to small txv. The cause smetime is the pressure it has limitation.

  8. #8
    Azmath Syed's Avatar
    Azmath Syed Guest

    Re: YORK ducted split

    Hello I want to migrate to australia for HVAC job

Similar Threads

  1. Help with York air conditioner.
    By Mohammed Qasim in forum Trouble Shooting
    Replies: 6
    Last Post: 16-07-2009, 07:35 PM
  2. York / Carrier/ Whirlpool ..split A/c
    By fireblade in forum Air Conditioning
    Replies: 2
    Last Post: 24-07-2006, 12:03 AM
  3. Cooling condenser of split with condensate from evaporator
    By smileypete in forum Air Conditioning
    Replies: 11
    Last Post: 10-07-2005, 08:21 AM
  4. LG ducted split
    By Abe in forum Air Conditioning
    Replies: 20
    Last Post: 08-06-2005, 07:19 PM
  5. York process chiller repairs
    By Matt in forum Commercial
    Replies: 5
    Last Post: 24-03-2004, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •