    Seal display unit



    Help please guys, I have recently changed a compressor on a "seal" refrigerated display unit, fitted new drier, cut back capilary and replaced vaporizing loop. However unit now never gets anywhere near set point and just runs excessively hot all the time. The new compreesor is an ACC (electrolux) GP12 TB (R134a), the old one was a tecumseh/ l'unite AE4448Y, I was wondering whether the new compressor is smaller capacity than the old one. - Idon't have any comparison / data on these compressors
    The compressor had already been replaced once so i don't know if it had the right one anyway.
    Also the new vaporizer loop is not as large as the old one - do you think this would make any diference?

    Any help greatly appreciated as this unit is begining to make me look a bit of a muppet

    Thanks

    Andy



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Seal display unit

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Seal display unit

    The swept volum of the Electrolux is 12cm³ and the UH is 14,15 cm³ but this can't be the reason for your problem.
    Restriction somewhere, undercharged, capillary too long, restricted dryer,
    What's your evaporating temerpature, HP, SC, SH? Without these figures, you never can diagnose proper your compressor.

    What's a vaporsing loop? Suppose it's the evaporator.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: Seal display unit

    Thanks for the help guys, it was a restriction in the capilary - nearly chaffed all the way through and slightly kinked as the pipework went through the bulkhead to the evaporator section. Unit hasn't run that well for a long time.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Seal display unit

    Thanks for the update Andy, it's always good to hear that a problem/query has been resolved.

    No doubt your customer is happier now also.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  2. M I T S U S H I T A ac unit with no condensing unit
    By Chinua in forum Air Conditioning
    Replies: 2
    Last Post: 28-07-2006, 06:54 PM
  3. Replies: 8
    Last Post: 20-05-2006, 04:21 PM
  4. Big Display Case
    By Abe in forum Commercial
    Replies: 4
    Last Post: 02-07-2003, 10:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •