    Question MCB Rating for Daikin & Mitsubishi



    Reading the installation instructions for my Daikin,
    It does not state the rating for the MCB?

    Should I fit 15a or 20a

    I have a Daikin
    FTXS25CVMB INTERNAL
    RXS25CVMB OUTSIDE UNIT (3Kw)

    I am also planning to buy a further unit
    Mitsubishi SRK25-ZD (3Kw)

    Im off for two weeks, so will pick up replies on my return, Thanks
    Last edited by mick2me; 12-08-2006 at 08:00 AM.



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: MCB Rating for Daikin & Mitsubishi

    I have a daikin ftxs50 installed in my conservatory which is run from a 15amp fuse spare from my cooker
    Hope this helps

  3. #3
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: MCB Rating for Daikin & Mitsubishi

    Quote Originally Posted by marc5180
    I have a daikin ftxs50 installed in my conservatory which is run from a 15amp fuse spare from my cooker
    Hope this helps
    MCB's offer much closer protection than fuses.
    Therefore need to be more accurately calculated.

    Wonder what MCBs installers are using?

    Right, I'm off on me olidays, better put the laptop
    away before SWMBO returns from the kennels....


    Eyup she's here already

  4. #4
    Join Date
    Oct 2005
    Location
    nottingham UK
    Posts
    109
    Rep Power
    19

    Re: MCB Rating for Daikin & Mitsubishi

    hi Mick2me
    my daikin book says the unit rxs25cv reqiuresa 15 amp fuse. start and run current show 4.4amps.

  5. #5
    Join Date
    Aug 2006
    Location
    England
    Age
    71
    Posts
    12
    Rep Power
    0

    Re: MCB Rating for Daikin & Mitsubishi

    Hi Mick.
    Not sure if your 3KW is input or output but from somebody else's post it would appear to be output. So from that, what size of cable are you running to it, and how far do you have to run it? Would suggest you run it 2.5mm2 and use 16a Type C breaker. A type B breaker may trip on motor start up, as start current is much more than run current. Ensure your breaker is to BS60898 as you should not use earlier types ( type1, type2, type3)and if it's fed from a TT supply You must install an RCD between the consumer unit and the service blocks.

  6. #6
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: MCB Rating for Daikin & Mitsubishi

    mswinman not realy, RXS25CVMB are inverter units so they start getel, so ... no shoc at starting a 16 amp, should do it, and 1.5 mm cable should be ok, and, yes RXS25CVMB has a'n nominal output of 2.5Kw, and max 3 Kw of cooling, and 3.4Kw nominal, and max 4.5 heating

  7. #7
    Join Date
    Nov 2005
    Location
    Liverpool
    Age
    49
    Posts
    56
    Rep Power
    19

    Re: MCB Rating for Daikin & Mitsubishi

    The primary job of the fuse is to protect the cable, it offers no real protection to the unit!
    For myself, I'd avoid 1.5mm cable for this job unless you're right near the Dist Board as the voltage drop could adversely affect your unit's performance!
    If you're running 2.5mm cable, then a 16a MCB will adequate. Non-inverters (fixed-speed) would need a C-type, but if this is an inverter, a standard B-type should do the trick!

    Hope this helps!

    Richie (aka Daddymac)

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: MCB Rating for Daikin & Mitsubishi

    Quote Originally Posted by daddymac
    The primary job of the fuse is to protect the cable, it offers no real protection to the unit!
    For myself, I'd avoid 1.5mm cable for this job unless you're right near the Dist Board as the voltage drop could adversely affect your unit's performance!
    If you're running 2.5mm cable, then a 16a MCB will adequate. Non-inverters (fixed-speed) would need a C-type, but if this is an inverter, a standard B-type should do the trick!

    Hope this helps!

    Richie (aka Daddymac)
    Even a 16A mcb will protect a 1.5mm cable which is rated at 19A.

    The RXS25 runs at 4.4A so 1.5mm2 cable will be sufficient

  9. #9
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: MCB Rating for Daikin & Mitsubishi

    so, let's talck some math , the unit whe are talking abaut is rated at max 1.46Kw so .... 14600 / 220 = 6.6 Amp ok, next Volt Drop formula per m is like this :

    voltdrop over length = length X volt drop X amps

    where 1.5 mm2 whorst cable is 28 mV /amp/m resulting from this

    11.000 mV (11 V) = 59 m X 28 mv X 6.6 Amp

    so a 11 volt drop (0.5% that is recomended by daikin) mens u can have a conductor of 59 m , do u thing he is havin a whire of 59 m ??? highly improbabal , and let's be serios when is it working at that loud
    Attached Images Attached Images

  10. #10
    Join Date
    Aug 2006
    Location
    England
    Age
    71
    Posts
    12
    Rep Power
    0

    Re: MCB Rating for Daikin & Mitsubishi

    Sorry! Didn't realize they were inverters so B curve breakers are fine. I'd still use 2.5mm cabling though, 1.5mm cabling is at its upper limit at 16A even though the unit only draws 4 amps you have to consider fault/overload conditions, I've seen a 16a breaker connected to a load drawing 28A! and no trip. 2.5mm cable has an upper limit of 25A. There are other factors to consider such as thermal insulation, If you bury the cable in any insulation you have to derate the whole cable run depending on how much is buried in insulation and of course theres that other unit to consider that may be installed later.Just for the record, voltage drop for 1.5mm is 29mv per amp of load per metre and 2.5 is 18mv per amp of load per metre. Something else springs to mind, if your consumer unit/dist board does not have an RCD, and as you're connecting to an outside unit it should have. You might consider fitting an RCBO, These are the same size as normal MCB's and offer the same O/L protection but also detects earth leakage.
    Regards Paul.
    Last edited by mswinman; 22-08-2006 at 07:50 PM.

  11. #11
    Join Date
    Jun 2005
    Location
    Romania
    Posts
    213
    Rep Power
    19

    Re: MCB Rating for Daikin & Mitsubishi

    so , judginh by what u say :

    "I'd still use 2.5mm cabling though, 1.5mm cabling is at its upper limit at 16A even though the unit only draws 4 amps you have to consider fault/overload conditions, I've seen a 16a breaker connected to a load drawing 28A! and no trip. 2.5mm cable has an upper limit of 25A.
    "
    , 2.5mm2 it whuldnt be enought because

    "'ve seen a 16a breaker connected to a load drawing 28A! and no trip."

    "2.5mm cable has an upper limit of 25A."


    and still if that unit whould drain more 16 amps it whould burst in flames, and it whoult make a big short cirrcuit that whoul for shore make it trip, orr make the MCB burst in flames, so 2.5 mm2 whould be too mutch and not a real use

  12. #12
    Join Date
    Aug 2006
    Location
    England
    Age
    71
    Posts
    12
    Rep Power
    0

    Re: MCB Rating for Daikin & Mitsubishi

    I'm taking into account the second unit to be fitted later. If it was one unit 1.5mm would be fine, this second unit is only mentioned in the original post. the volt drop calcs were posted whilst I was writing my answer so sorry for the apparent duplication.

  13. #13
    Join Date
    May 2006
    Location
    Sussex
    Posts
    362
    Rep Power
    21

    Re: MCB Rating for Daikin & Mitsubishi

    1) Daikin-FTXS25 inverters are suitable for the general power ring main, surely.

    Run a separate 15A circuit from the consumer unit/power distribution board if you like but, well, sounds a bit unnecessary.

    2) As for a 5kW system in the conservatory, well I would have thought that system should be on its own circuit, probably a 20A type-C MCB (check with the manufacturer). Being a conservatory, one would also have that circuit protected with an RCD (Residual Current Device).

    (I’m not a sparkie, though, so don't listen to me, eh.)

  14. #14
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: MCB Rating for Daikin & Mitsubishi

    Well I've just returned from Las Vegas/Los Angeles, Family visit, not gambling.

    Let me tell you thats the place to be to sell Air!
    8pm and 108f!

    Anyways thanks for the replies.

    The Unit and second unit are mounted externally on the opposite side of the wall from a split load consumer unit. there is no power point anywhere near. Direct feed from MCB's (1 per unit) is the easy option.

    Route ... MCB-->2.5mmT&E(3m)-->20a double pole external disconnector switch-->Outside unit-->1.5mm 3core&e(6m)-->Inside unit.

    The only issue is what size MCB to run the Daikin only? bearing in mind the close protection of such an animal.

  15. #15
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: MCB Rating for Daikin & Mitsubishi

    Quote Originally Posted by mick2me View Post
    The only issue is what size MCB to run the Daikin only? bearing in mind the close protection of such an animal.
    May have been asked before - but - (RTFM) what does the installation manual recommend ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #16
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: MCB Rating for Daikin & Mitsubishi

    Quote Originally Posted by Brian_UK View Post
    May have been asked before - but - (RTFM) what does the installation manual recommend ?
    It does not say Brian?

  17. #17
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: MCB Rating for Daikin & Mitsubishi

    Quote Originally Posted by mick2me View Post
    It does not say Brian?
    AH!!? Frank, one for you here
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  18. #18
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: MCB Rating for Daikin & Mitsubishi

    240V single phase 16A

  19. #19
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Thumbs up Re: MCB Rating for Daikin & Mitsubishi

    Quote Originally Posted by frank View Post
    240V single phase 16A
    Thanks Frank

    Exactly what I bought today.

    16a Wylex MCB's (B) @ £4.45 each inc vat.

    Good old Screwfix.com

    http://www.screwfix.com/app/sfd/cat/...79276&ts=55741


  20. #20
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: MCB Rating for Daikin & Mitsubishi

    Quote Originally Posted by mick2me View Post
    Thanks Frank

    Exactly what I bought today.

    16a Wylex MCB's (B) @ £4.45 each inc vat.

    Good old Screwfix.com

    http://www.screwfix.com/app/sfd/cat/...79276&ts=55741

    Hi Mick

    For any motor - inverter driven or not I would recommend a type C breaker.

  21. #21
    Join Date
    May 2006
    Location
    Nottingham
    Age
    72
    Posts
    163
    Rep Power
    18

    Re: MCB Rating for Daikin & Mitsubishi

    Bu**er

    I am sure they will change them.

Similar Threads

  1. Mitsubishi vrv
    By dakesojo in forum Air Conditioning
    Replies: 20
    Last Post: 22-09-2009, 01:04 PM
  2. Mitsubishi problem
    By marc5180 in forum Trouble Shooting
    Replies: 15
    Last Post: 17-01-2007, 10:06 PM
  3. Mitsubishi heavy industrial A/C.
    By Langer in forum Air Conditioning
    Replies: 10
    Last Post: 14-08-2006, 11:31 AM
  4. mitsubishi fault
    By techni in forum Air Conditioning
    Replies: 6
    Last Post: 23-12-2005, 11:30 AM
  5. help with mitsubishi starion 82 model car a/c
    By fridg in forum Trouble Shooting
    Replies: 4
    Last Post: 12-12-2005, 10:38 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •