Ok I got my home brew frankinstin chiller built, its mix of odds n ends.

First thing I did was take the lable from the origional aplication of the condencing unit for a Vending machine and converted the values from R-12 to R-134a along with temp, this yeilded the following table:

70F = 21.1C = HS 125+-5 ; LS 10+-1
80F = 26.7C = HS 145+-5 ; LS 11+-1
90F = 32.2C = HS 165+-5 ; LS 12+-1
100F = 37.8C = HS 185+-5 ; LS 13+-1 for R-12 after conversion I got this table:

70F = 21.1C = HS 126+-5 ; LS 11+-1
80F = 26.7C = HS 149+-5 ; LS 11+-1
90F = 32.2C = HS 172+-5 ; LS 13+-1
100F = 37.8C = HS 192+-5 ; LS 14+-1 This is of course a ruff estimate of what I should see for the plant Today I messured and got this for readings:

Ambient = 22C+-1
Coolant liquid @ 10C
HS = 140 dead on
LS = 13 +-1
This was after 15 or so minutes of pulling down 15Gallons of water @ 21.5C to 10C

So how would you say the unit is? Do the readings look as good as I think they are?