    May 2006
    63
    5
    Chilled Water Coil
    1st part
    Has any one ever had a chilled water coil that has differant temps througout the coil,, It seems like it has tubes stopped up in it.
    2nd part
    If my coil is stopped up does anyone have any ideas on how to unstop it
    Aug 2001
    1,046
    Re: Chilled Water Coil
    What sort of coil is it?
    If it is a shell and tube evaporator where the refrigerant is in the tube and the water surrounds it in the shell, partial freezing up will deform the shape of the tube, sometimes even crushing it in places. This arrangement does not split the tube if it freezes; (the ice tends to crush the tube). This may have happened progressively in the past especially if the water flow rate is low and there is a regular lack of load. I know it shouldn?t happen, but in the real world it often does. If you are really unlucky it may crush the tube where it enters the tube sheet and flood the chiller.
    If you can detach the end covers, a visual check can usually determine if the tubes are crushed and how many. If it is too small for this you may have to make a decision to replace the lot.
    Depending on the size and make of the evaporator, you may get away with up to 10% of the tubes out of action before there is a lack of performance that cannot be compensated for with water flow adjustments. The manufacturer will advise you about this. In my experience, if it was only a few tubes that were affected, you could plug them off at the tube sheet, with out affecting the performance.
    Alternatively, some large evaporators can be re-tubed ? it?s an expensive and a skilled job.
    ________
    Toyota Pod specifications
    Sep 2005
    uk
    499
    If on the other hand if it is chilled water to air hx and partially blocked then try backflushing it or running an acidic cleaner or descaler through. it may possibly just need bleeding.
    Feb 2005
    Jamaica
    121
    Can I also add ,If Its a chill water coil as in a AHU unit u can also do a water pressure check (inlet reading,outlet reading) If a big pressure drop at outlet and flow rate drops then as u said coil might be blocked.
    How to clear,counterflow or backwash the coil(use the inlet as the outlet and use the outlet as the inlet). If that works then u might want to think about strainers on your inlet to catch any stuff in the future and also look into your chill water treatment system if rust inhibitor is being used(if the blockage is rust).
    Feb 2005
    Jamaica
    121
    Slingblade got here before me so,DITTO
  1. Do I need a chilled water buffer vessel
    By Consultant in forum Commercial
    Last Post: 02-03-2011, 09:40 AM
  2. water cooling coil
    Last Post: 02-09-2006, 08:45 PM
  3. water coil anti-freeze
    Last Post: 17-08-2005, 07:25 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Last Post: 13-07-2004, 08:28 PM
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Last Post: 31-07-2002, 08:25 PM