    Need ideas !!!



    Hi every body , i have a McQuay centrifugal chiller PEH 050 , R 134A , the problem is that its not capable of completing the loading sequence , it goes up 10 or 15 % nd goes back , keeps on playing like that , at the same time the motor is not getting any cooling and then fails on high motor temp.
    Oil pressure is OK , but the capacity control valve doesn't respond ( when calibrating the load unload screws).
    The comp has over 50.000 hours , any ideas from the pros will be appreciated , thanks , all the best , tzvi.



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Age
    59
    Posts
    25
    Rep Power
    0

    Re: Need ideas !!!

    Hi Z,

    Have you checked if the unit is low on refrigerant? as this will stop the compressor from loading.

  3. #3
    Join Date
    Jul 2006
    Location
    Israel
    Age
    70
    Posts
    12
    Rep Power
    0

    Re: Need ideas !!!

    Yes , i have , the pressure and refrigerant temps are OK , some times it works for a while at 100% load and it works good , good DT at evap and condenser , but when reaches set point and unloads it will shut down at : high suction temperature fault , all the best Tzvi.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Need ideas !!!

    sounds like the seals are passing, the unit probably needs a tear down and overhaul.

    al

  5. #5
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Need ideas !!!

    Quote Originally Posted by zvikard
    Hi every body , i have a McQuay centrifugal chiller PEH 050 , R 134A , the problem is that its not capable of completing the loading sequence , it goes up 10 or 15 % nd goes back , keeps on playing like that , at the same time the motor is not getting any cooling and then fails on high motor temp.
    Oil pressure is OK , but the capacity control valve doesn't respond ( when calibrating the load unload screws).
    The comp has over 50.000 hours , any ideas from the pros will be appreciated , thanks , all the best , tzvi.
    Hi I haven`t worked on centrifs for years but it sounds like your current limiter is acting up check it out

    regards Toosh

  6. #6
    Join Date
    Jul 2006
    Location
    Israel
    Age
    70
    Posts
    12
    Rep Power
    0

    Re: Need ideas !!!

    Hi Al, i think you are right , i was thinking in the same way , the seals are probably damaged , when the unit operates at less than 60% load the motor will not get cooling and eventually will fail for high temp . It only happened once but , my first impression was that we need to do a overhaul , thanks , all the best , Tzvi.

Similar Threads

  1. Any Ideas? Worrying noise from Fujitsu ASY 30E
    By MrThin in forum Air Conditioning
    Replies: 9
    Last Post: 29-06-2006, 11:45 AM
  2. bit of a pickle.. any ideas??
    By mr cool (aus) in forum Transport
    Replies: 9
    Last Post: 05-05-2006, 05:35 AM
  3. Your opinions and ideas greatly appreciated for this project.
    By fridg in forum Technical Discussions
    Replies: 0
    Last Post: 04-12-2005, 09:19 AM
  4. Ideas To submit
    By Alt Concepts in forum New Technologies
    Replies: 6
    Last Post: 13-09-2005, 12:55 PM
  5. Great Idea...!
    By Steve in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 24-01-2001, 08:52 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •