Hi every body , i have a McQuay centrifugal chiller PEH 050 , R 134A , the problem is that its not capable of completing the loading sequence , it goes up 10 or 15 % nd goes back , keeps on playing like that , at the same time the motor is not getting any cooling and then fails on high motor temp.
Oil pressure is OK , but the capacity control valve doesn't respond ( when calibrating the load unload screws).
The comp has over 50.000 hours , any ideas from the pros will be appreciated , thanks , all the best , tzvi.
11-08-2006, 01:18 AM #2
Re: Need ideas !!!
Hi Z,
Have you checked if the unit is low on refrigerant? as this will stop the compressor from loading.
16-08-2006, 07:25 PM #3
Re: Need ideas !!!
Yes , i have , the pressure and refrigerant temps are OK , some times it works for a while at 100% load and it works good , good DT at evap and condenser , but when reaches set point and unloads it will shut down at : high suction temperature fault , all the best Tzvi.
16-08-2006, 08:22 PM #4
Re: Need ideas !!!
sounds like the seals are passing, the unit probably needs a tear down and overhaul.
al
17-08-2006, 03:47 AM #5
Re: Need ideas !!!
Originally Posted by zvikard
regards Toosh
17-08-2006, 08:34 PM #6
Re: Need ideas !!!
Hi Al, i think you are right , i was thinking in the same way , the seals are probably damaged , when the unit operates at less than 60% load the motor will not get cooling and eventually will fail for high temp . It only happened once but , my first impression was that we need to do a overhaul , thanks , all the best , Tzvi.
Any Ideas? Worrying noise from Fujitsu ASY 30E
By MrThin in forum Air ConditioningReplies: 9Last Post: 29-06-2006, 11:45 AM -
bit of a pickle.. any ideas??
By mr cool (aus) in forum TransportReplies: 9Last Post: 05-05-2006, 05:35 AM -
Your opinions and ideas greatly appreciated for this project.
By fridg in forum Technical DiscussionsReplies: 0Last Post: 04-12-2005, 09:19 AM -
Ideas To submit
By Alt Concepts in forum New TechnologiesReplies: 6Last Post: 13-09-2005, 12:55 PM -
Great Idea...!
By Steve in forum Chit Chat & Service StoriesReplies: 4Last Post: 24-01-2001, 08:52 AM