    How is a filter drier sized



    Lets say there is no drier in the system. Generally you would replace with same. Do you go by HP, BTU, tubing size of course gives you some indication but what would be the correct way to choose. Ken



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: How is a filter drier sized

    Hi Ken,

    Here is some information on the Sporlan filter/driers.

    http://www.sporlan.com/40-10.pdf (3 MB file size)

    When you look in the manual you will see several different categories for selection.

    The center column shows the capacity for a specified pressure drop of 1 psi for one Ton of Refrigeration.

    The columns in light blue to the right are some different areas and capacities that can be used. Depending on the system operating conditions.

    If you notice the OEM air conditioning column that usually has the highest capacity. I would expect this is due to better fabrication methods in a shop, rather than in the field.

    I tend to use these as a starting reference and then up-size the driers. I prefer to have larger driers rather than one that might be just right.

    Remember, you don't want a lot of pressure drop in the liquid line, since that will cause flashing in the tubing.

    Unless you have a lot subcooling.

    The other interesting data is the water capacity ratings. This is showing you the drier cores have a much better absorbing capacity as the drier gets colder.
    Last edited by US Iceman; 08-08-2006 at 02:33 PM.

  3. #3
    Join Date
    Feb 2006
    Location
    WA, USA
    Posts
    62
    Rep Power
    19

    Re: How is a filter drier sized

    I just read the back of the box...
    Will melt ice for $101/hr

Similar Threads

  1. Attention! Air Conditioning Filter Experts I Need Help
    By hoffa4444 in forum Air Conditioning
    Replies: 4
    Last Post: 10-07-2006, 09:43 AM
  2. Drier
    By Vincent Yu in forum Fundamentals
    Replies: 6
    Last Post: 07-02-2006, 03:02 AM
  3. AAF HEPA filter
    By watana in forum Air Conditioning
    Replies: 2
    Last Post: 02-04-2005, 12:09 PM
  4. Shelf life of an uncapped dessicant drier.
    By eberg in forum Air Conditioning
    Replies: 2
    Last Post: 22-08-2001, 01:22 PM
  5. Drier Position
    By subzero*psia in forum Commercial
    Replies: 8
    Last Post: 23-07-2001, 10:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •