    condensor- temp effect on amount of liquid



    hoping you guys can help me out please,as im getting a little confused

    If the condensor temp is increased by say one fan not running and so the rise in temp/pressure , will this mean more liquid in the condensor as it is condensing at a higher temperature and therfore less laten heat is required to be removed to turn to a liquid as per PH diagram ?
    and if so does this mean there will be more sub cooling ??

    thanks in advance for any help

    Joe



  2. #2
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    23

    Re: condensor- temp effect on amount of liquid

    ya but you'll all so have a higher over all liquid temp thus loos more to flash gass on the way to the metering device over the pipes internal pressure drop! How ever the side with a dead fan will still reject small amounts of heat due to convection.

    (Now don't take this too heavily as I am still a student, but so far that would be my understanding)

  3. #3
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: condensor- temp effect on amount of liquid

    Thanks

    yeah i realize the overall liquid temp will be high and so a negative effect , just trying to get into my head (amongst over things )weather with a very high condensing pressure you could read a high subcooling and so would get the same effect as if the system was overcharged , when it could be air flow etc to the condensor .
    also cant get into my head quite where the new point of inlet to the expansion valve would be on a PH diagram

    thanks
    Joe

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: condensor- temp effect on amount of liquid

    Hi, Joe
    Quote Originally Posted by kfjoe
    hoping you guys can help me out please,as im getting a little confused

    If the condensor temp is increased by say one fan not running and so the rise in temp/pressure , will this mean more liquid in the condensor
    Compression pressure will increase - HPS (high pressure switch) functions and unit will stop.

    Evaporting pressure will slightly increase.

    Discharge temp will increase - oil deterioration -compressor failure.

    Suction temperature will slightly increase.

    Amount of superheat remains constant.

    Amount of subcool remains constant.

    Compression ratio increase - weight of refrigerant circulated decrease.

    Refrigerating effect will decrease - cooling capacity decrease - COP will decrease

    Thermal equivalent of compression work increase - running current increase

    Best regards, Josip
    Attached Files Attached Files
    Last edited by Josip; 09-08-2006 at 10:08 PM. Reason: attachment upload

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: condensor- temp effect on amount of liquid

    Thanks Josip

    so subcooling would remain the same then

    so what governs subcooling in a system other than the refrigerant charge ,no condensables , is there anything else than can effect it ?

    thanks

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: condensor- temp effect on amount of liquid

    Quote Originally Posted by kfjoe
    Thanks Josip

    so subcooling would remain the same then
    so what governs subcooling in a system other than the refrigerant charge ,no condensables , is there anything else than can effect it ?

    thanks
    Some examples:

    Insufficient refrigerant circulation

    a) amount of ref in a system is insufficient
    1. undercharge of refrigerant
    2. refrigerant leakage

    .....SC decreases

    b) amount of ref passing through a metering device is insufficient
    1. choked filter, drier or metering device
    2. faulty metering device

    ....SC increases

    Excessive refrigerant circulation
    With TXV - SC decrease
    With capilary tube - SC increase

    Excessive cooling load
    SC - decrease

    That's all folks

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: condensor- temp effect on amount of liquid

    Tricky questions.I would say that the amount of liquid in the condenser will decrease if you lose a fan. The subcooling question is a good one. I can see it actually increasing. Once the liquid has condensed, it does not take much work to finish the sensible cooling, thus you might have a liquid at 95 degrees at the outlet of the condenser both with the fan on and with the fan off. The pressure will be higher with the fan off, thus the 95 deg liquid will be more subcooled under the higher pressure.

    I see it as similar to a phenomenon I puzzled over for years regarding noncondensibles in a system. The discharge pressure would be very high, but the liquid return line would feel cool. Actually, the liquid return line was the same temperature as other liquid return lines.

    Noncondensibles in essence take away valuable condensing surface from a condenser, thus the pressure will be higher. But surprisingly, the liquid return temperature is not as significantly higher, thus, the return liquid is more subcooled in the situation of noncondensibles. Why not the same pattern with a fan disabled?

    Not so simple questions, Joe.

  8. #8
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: condensor- temp effect on amount of liquid

    thanks guys
    that helps .

    but it sure does confuse me why reducing the capacity of a condensor by non condensables , which to me means the condensor has to work at a higher TD so therefore presure, is different to reducing the capacity of a condensor by say less airflow as this also raises the pressure , so why does one have high subcooling and not the other

    maybe im missing something

    thxs

  9. #9
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: condensor- temp effect on amount of liquid

    so why does one have high subcooling and not the other
    Subcooling is the amount of sensible heat below saturation temperature: If you have a liquid at 95 degrees F with a saturated condensing temperature of 105 deg F, you have 10 deg of subcooling. You can increase the subcooling in any of two ways: By lowering the liquid temperature, or by raising the saturated condensing temperature. So if you raise the saturated condensing temperature to 115 deg F, and you still have 95 deg liquid, you now have 20 deg subcooling. Same as if you lowered the liquid temperature to 85 deg F. Don't confuse subcooling with enthalpy or net refrigerating effect. Subcooling is simply a relative term indicating the relationship of a liquid to its saturated pressure and temperature conditions.

  10. #10
    Join Date
    Jul 2002
    Location
    Derby
    Posts
    74
    Rep Power
    22

    Re: condensor- temp effect on amount of liquid

    thanks Dan

    yes that makes sence to me

    but lets say you have a system running at 105 degf
    with a 95 degf liquid so a 10 degf subcooling and then raise the condensing temp to 115 degf by say blocking off part of the condesor air flow , what would be the subcooling or how would it change if at all ?
    thats the bit i cant get mt head around

    thxs for all the help

  11. #11
    Join Date
    Jun 2006
    Location
    USA
    Age
    58
    Posts
    42
    Rep Power
    0

    Re: condensor- temp effect on amount of liquid

    Quote Originally Posted by kfjoe
    thanks Dan

    yes that makes sence to me

    but lets say you have a system running at 105 degf
    with a 95 degf liquid so a 10 degf subcooling and then raise the condensing temp to 115 degf by say blocking off part of the condesor air flow , what would be the subcooling or how would it change if at all ?
    thats the bit i cant get mt head around

    thxs for all the help

    As far as I know when you push the condenser beyond the design temperatures the efficiency of it will decrease resulting on less subcooling, condenser are designed to serve as desuperheaters, condensers and subcoolers under normal operating conditions, as the temperature of the air/water increases it takes more of condensers surface to desuperheat refrigerant vapors moving the condensation process further down towards the bottom of the condenser that under normal circumstances would had been using for subcooling purposes.

  12. #12
    Join Date
    Aug 2006
    Location
    China
    Posts
    15
    Rep Power
    0

    Re: condensor- temp effect on amount of liquid

    how are you ?

  13. #13
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: condensor- temp effect on amount of liquid

    With a fan being off in an air cooled condenser, there will be reduced condensation, which means that the temperature and pressure shall be high and there will more vapour at hihg temperature than liquid. This will result in flash gas formation ahead of the TEV resulting in reduction of capacity in refrigeration capacity.

    For any refrigeration system it is very important that proper condensation is there and the subcooling is maintained. In air cooled condenser a seperate section is usualy set aside for subcooling, but it is better to install a liquid suction heat exchanger as it will offer a better subcooling and also maintain proper superheat. However everything depends on proper design.

    With best wishes,

    Samarjit

  14. #14
    Join Date
    Aug 2006
    Location
    China
    Age
    54
    Posts
    52
    Rep Power
    18

    Re: condensor- temp effect on amount of liquid

    hello,friends, i'm a new comer. it's a very good forum.

  15. #15
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25

    Re: condensor- temp effect on amount of liquid

    but lets say you have a system running at 105 degf
    with a 95 degf liquid so a 10 degf subcooling and then raise the condensing temp to 115 degf by say blocking off part of the condesor air flow , what would be the subcooling or how would it change if at all ?
    thats the bit i cant get mt head around
    Subcooling equals Saturated Condensing Temperature (SCT) (converted from pressure per your T/P chart) minus your actual liquid temperature. Thus, in an R22 system:

    Condensing pressure: 210 psig = 105 deg F SCT
    Temperature of liquid refrigerant at outlet of condenser: 95 deg F
    105 SCT minus 95 = 10 deg F subcooling.

    If you are condensing at 115 SCT,

    115 SCT minus 95 = 20 deg F subcooling.
    As far as I know when you push the condenser beyond the design temperatures the efficiency of it will decrease resulting on less subcooling, condenser are designed to serve as desuperheaters, condensers and subcoolers under normal operating conditions, as the temperature of the air/water increases it takes more of condensers surface to desuperheat refrigerant vapors moving the condensation process further down towards the bottom of the condenser that under normal circumstances would had been using for subcooling purposes.
    Well spoken, and I don't really disagree, other than the fact you haven't considered the new dynamic of increasing the condenser TD. By going from a 10 deg TD (105 F condensing - 95 deg air, for example) to a 20 deg TD, you have doubled the capacity of the remaining active suface of the condenser. But that is a quagmire I don't want to step into.

    My point is that it is entirely possible you will not get an increase in liquid temperature even though you have raised the condensing pressure. I am not denying that at some point you will get an increase in liquid temperature as you turn fans off, but I have seen instances where you can cycle fans off on a multifan condenser and you do not get as large an increase in liquid temperature as you do in Saturated condensing temperature, thus you gain subcooling.

    Here are some other examples of reducing the condensers capacity that will show up as increases in subcooling:

    Condenser flooding valves. They will not open until the condensing pressure exceeds their setting. The way they do this is to fill or "flood" the condenser with lquid until the pressure rises as a result of the reduced condensing surface.

    An overcharged self-contained refrigerator. The condensing pressure again rises because liquid is backed up into the condenser, but as in the case of the previous example, more tubes are now dedicated to subcooling as the liquid fills more of the tubing from the outlet inward - thus, more subcooling.

    Just speculations on my part.

  16. #16
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17

    Re: condensor- temp effect on amount of liquid

    Quote Originally Posted by kfjoe View Post
    thanks guys
    that helps .

    but it sure does confuse me why reducing the capacity of a condensor by non condensables , which to me means the condensor has to work at a higher TD so therefore presure, is different to reducing the capacity of a condensor by say less airflow as this also raises the pressure , so why does one have high subcooling and not the other

    maybe im missing something

    thxs
    When non condensibles are in system the surface area available for condenser gets affected consequently effect the temperature.If non condensibles present the pressure gauge needle will oscillate.
    other reason could be due to refrigerant over charge then both suction and discharge will be high.

  17. #17
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: condensor- temp effect on amount of liquid

    I would have thought losing one fan, is the same as high ambient temperatures or fouled condenser which causes a reduction in condenser capacity. The condenser can no longer reject enough heat, for it to operate efficently. If theres not enough heat rejection then surely you cannot condense the same amount of gas into a liqiud.
    Systems which have operated fine in lower ambient conditions then fail under high ambient conditions, because the liquid in the condenser is reducing the surface area for heat rejection.
    What would the symptons of a undersized condenser be??

    CB

  18. #18
    skinnymanpig's Avatar
    skinnymanpig Guest

    Re: condensor- temp effect on amount of liquid

    ive got a similar question, didnt want to make a new thread. what would happen if the heat transfer to the evaporator was reduced?

Similar Threads

  1. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  2. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 02:29 PM
  3. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM
  4. Liquid Refrigerant Pumping
    By bersaga in forum Technical Discussions
    Replies: 34
    Last Post: 09-08-2003, 08:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •