03-08-2006, 10:19 PM #1
HELP with LG dual zone
Have a split system LG running R410A, my problem is that the unit when started up was pulling a vac on the suction side(no where to hook hi side gauge so i dont know whats happening there). i found that the only ***** in the system was what was added to the indoor units after install so i recovered etc.
recharged to factory specs and suction pressure shot up to 300 and wouldnt fall. i thought i overcharged so i evacuated but the system had only gas, the 4 pounds i charged seemed to dissappear.
I found the ***** by cracking the flare nut on the high side and it spewed oil/*****, meanwhile i can pull a vac on the suction side and spew ***** on the high side at the same time?
i normally work on air dryers not conditioners so if this is a really stupid problem cut me a little slack
-
03-08-2006, 10:29 PM #2
Re: HELP with LG dual zone
Is the discharge valve open ??
Otherwise, if it's an LG, bin itBrian - Newton Abbot, Devon, UK
Retired March 2015
-
03-08-2006, 11:55 PM #3
Re: HELP with LG dual zone
could be a blockage in liquid line or dreaded moisture in system. have a look at indoor unit and see if there is any liquid getting there if so then its moisture or a knackered tev mate best of luck, mr cool
-
04-08-2006, 07:07 AM #4
Re: HELP with LG dual zone
It sounds like you do not have any air conditioning experience, if I was you, employ the services of some one who knows what they are doing, you can not go letting gas and oil out of the system, you will be hung up by your big toes.
-
05-08-2006, 05:03 AM #5
Re: HELP with LG dual zone
Originally Posted by Andy W
I didn't bleed the system to atmosphere, when i cracked the flare nut on the liquid side and got liquid ***** i closed it back. I guess someone who knows what they are doing would have known that even though the system could be leak tested with N and have a 450 mic vac pulled on it(on the only service connection available), regardless of that, I should have known there was ***** trapped on the hi side.
anyway, the prob was the TEV, and it's been taken care of(by someone who did not know what he was doing), so thanks to those who offered help and to those who offered toe hangings...
,.|..
-
05-08-2006, 07:22 AM #6
Re: HELP with LG dual zone
Originally Posted by stretch
Similar Threads
-
dual source heat pump
By Lc_shi in forum New TechnologiesReplies: 29Last Post: 12-08-2010, 02:24 AM -
Dual Scroll Compressor
By ernestlin in forum Technical DiscussionsReplies: 7Last Post: 27-06-2006, 04:14 AM -
Need help with a dual compressor display case
By kengineering in forum Technical DiscussionsReplies: 15Last Post: 15-03-2006, 07:32 PM -
Dual vs. Parallel Piped
By Cool Temp in forum IndustrialReplies: 0Last Post: 28-09-2005, 03:32 PM -
zone heating /cooling work station
By Lc_shi in forum FundamentalsReplies: 6Last Post: 22-04-2005, 01:26 AM