    TXV's



    I have a air unit that i will be installing soon, I am going to replace the TXV on this unit at the time, the valve is a sporland DAE-5-L what does the L on the end of the part # designate, I can get a C from our local supply the C is for medium temp, i will be running this unit at about 60 degrees so i do not really need meduim temp. just a ?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: TXV's

    Hi Jerry

    According to the Sporlan documents available here:-
    http://www.sporlan.com/10-9.htm

    your valve designation of DAE-5-L means this:-

    D = FPT or socket weld body
    A = R717
    E = External equalizer
    5 = TR duty
    L = Thermostatic charge, L is the only one available for R717.

    Hope this helps,
    Brian
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Liquid receiver
    By Renato RR in forum Fundamentals
    Replies: 134
    Last Post: 02-03-2011, 07:55 AM
  2. Help geting more info on some TXVs
    By The MG Pony in forum Chit Chat & Service Stories
    Replies: 5
    Last Post: 07-07-2006, 05:47 PM
  3. inverter vs liquid amplification
    By fridge51 in forum New Technologies
    Replies: 16
    Last Post: 18-12-2005, 11:21 AM
  4. TXV's and LST compressors
    By DaBit in forum Technical Speculations
    Replies: 32
    Last Post: 18-06-2002, 02:27 PM
  5. Superheat
    By subzero*psia in forum Commercial
    Replies: 63
    Last Post: 14-06-2001, 10:47 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •