    Tinkering with an old Ref glass display case



    I think I may have a High Low limit switch problem.Iam pretty sure someone adjusted it, not knowing what they where doing. I know I prob need more info but can anyone tell me what the switch might need to be set on???



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Tinkering with an old Ref glass display case

    HI,

    What refrigerant is the unit working on?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: Tinkering with an old Ref glass display case

    Quote Originally Posted by fix_it_man74
    I think I may have a High Low limit switch problem.Iam pretty sure someone adjusted it, not knowing what they where doing. I know I prob need more info but can anyone tell me what the switch might need to be set on???
    Hi First of all as Bryan says what refrigerant is being used, and it probably being controlled by a low Pressure control. We also need the temp required, and running pressures.ie what pressure is it cutting out at.

    regards Toosh

  4. #4
    Join Date
    Jan 2006
    Location
    Adelaide , Australia
    Posts
    192
    Rep Power
    19

    Re: Tinkering with an old Ref glass display case

    Turn or unplug the power supply and bridge out ( electrically ) all the controls then turn it back on at least you will know if its the controls or the system is dead first .
    So if it goes then take out the bridging and trace which control is open circuit and stopping the operation of unit . If its the LP just narrow the differential that is probably too wide and holding the unit out.

Similar Threads

  1. display case evaparator fans
    By Mark in forum Supermarket Refrigeration
    Replies: 68
    Last Post: 16-01-2011, 03:03 AM
  2. Need help with a dual compressor display case
    By kengineering in forum Technical Discussions
    Replies: 15
    Last Post: 15-03-2006, 07:32 PM
  3. display case temp alarms
    By shark26 in forum Supermarket Refrigeration
    Replies: 9
    Last Post: 17-01-2006, 10:07 AM
  4. Fogal Open Display Case
    By Abe in forum Commercial
    Replies: 2
    Last Post: 07-05-2005, 08:47 PM
  5. Big Display Case
    By Abe in forum Commercial
    Replies: 4
    Last Post: 02-07-2003, 10:53 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •