Results 1 to 10 of 10
Thread: Help Me
    hery's Avatar
    hery Guest
    Help Me
    How to design a heat pump dehumidifer for tobacco curing with capacity of the romm is 20 x 15 x 4 m.
    The outside design is 25oC and 75% RH....and the inside design room for tobacco curing is 40oC and 60% RH...please also include the psychrometric chart
    Apr 2006
    41
    1,620
    Re: Help Me
    why not just add in a bunch of dehumidifyers?
    Oct 2001
    Nottingham UK
    5,668
    Re: Help Me
    Quote Originally Posted by hery
    From the data you have posted it would appear that you require a dehumidifier and a reheater to achieve your 'in box conditions'
    15K temp increase and 15% humidity decrease.
    Are there any specialists in your area that can help?
    Dec 2004
    Weihai,China
    800
    Re: Help Me
    Hi Hery
    Tobacco air circulation pass evaporator and heating fin-tube heat exchanger ,and the air temp increase and humidity is decrease. The issue needed attention is the condenser split into two parts: inside part for heating air and outside condenser and related heat capacity adjustment component.
    The system capacity depends on how to balance the drying time and the initial cost.
    only for your reference
    regards
    LC
    Oct 2003
    5,630
    34
    Re: Help Me
    Lc, you can also use another gas so that you can install the condensor inside so that the machine can run on a higher indoor temperature.
    We've buikd some 15 years ago on r114a as far as I can remember (wood drying) Inside temperature +/- 55°C.
    How will the tobacco stacked in the room? You need a very good air circulation around your prodcuts, apart from the dehumidifier.
    I think you can find a lot of information in this link http://pubs.caes.uga.edu/caespubs/ES-pubs/RB439.htm
    http://www.bulk-online.com/Forum/sho...?threadid=4986
    Aug 2005
    5,302
    Re: Help Me
    Peter,
    Do you have a flow diagram of the heat pump you built for the wood drying? I'm trying to understand how this process works of drying applications.
    Thanks also for posting the link on the tobacco curing. It is very informative.
    Oct 2003
    5,630
    34
    Re: Help Me
    Just noted now you message USIceman.
    For some reason, I didn't receive a mail that there was a new post.
    The setup is really basic as you can see.
    The R114 was to avoid excessive HP but this did you know.
    Attached Files Attached Files
    Jun 2005
    Madison
    61
    32
    Re: Help Me
    Hery,
    Based on the data you provided, you should add moisture to the air. At 25 degree C and RH=75%, the humility rate is 0.015 kg/kg. At 40 degree C and RH=60%, the humility rate is 0.02855kg/kg. So you need to add 13.55 gram water per 1 kg dry air.
    Aug 2005
    5,302
    Re: Help Me
    Peter,
    Thanks for the diagrams. It was just as I expected. Nothing too fancy, very simple.
    Was there anything specific you ordered for the fan motors? Perhaps heavier motor insulation rating for higher temperatures?
    Thanks for sharing the information Peter.
    May 2006
    Xi an, China
    65
    Re: Help Me
    Hery,
    Here is the process in psychrometric chart, wmf format.
    You need add water like vincent yu said.
    autt