01-08-2006, 09:50 PM #1
Searle Condensing Unit
Hi
I,ve been having head pressure problems with searle condensing units
Model no NCU 84-3LS
The fan speed controller sensor connected to one of the condenser bends is secured with a rubber band which streches with the heat, lifting the sensor of the bend.Once cable tied securely problem sorted.Just thought I,d share my findings with you.
Regards Bernard
-
01-08-2006, 10:39 PM #2
Re: Searle Condensing Unit
Thanks for that Bernard, any "tips" are always welcomed.
Just got to find a safe place to file them..Brian - Newton Abbot, Devon, UK
Retired March 2015