    Toshiba VRF systems



    Hi gang

    is anyone familiar with these systems? am wondering is there a minumum distance that the flow control boxes should be apart? have an install where i can place boxes is 1m proximity to each other due to lack of ceiling space. also can the refnet joints be placed vertically?

    Thanks

    Al



  2. #2
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Toshiba VRF systems

    Quote Originally Posted by al
    Hi gang

    is anyone familiar with these systems? am wondering is there a minumum distance that the flow control boxes should be apart? have an install where i can place boxes is 1m proximity to each other due to lack of ceiling space. also can the refnet joints be placed vertically?

    Thanks

    Al

    One word Al NOISE

    The BS boxes are usually placed away from the unit to kepthe noise out of the occupied space, just watch that there is not too much carry over of that noise to any area you don't want

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Toshiba VRF systems

    I've got photo that might answer your question. I think it's on the work computer. I'll have a look tomorrow.

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Toshiba VRF systems

    NO, no, no, Refnet joints should be horizontal or the branch slighty below the main to ensure even flow of refrigerant.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Toshiba VRF systems

    Thanks guys

    noise could be an issue, but there's no other space available.....the install instructions state that vertical is ok but i know with daikin this isn't so....are tosh that good

    regards

    al

  6. #6
    Join Date
    May 2006
    Location
    Hayling Island, UK
    Age
    60
    Posts
    143
    Rep Power
    21

    Re: Toshiba VRF systems

    Hi Al,

    I'm very familiar with these systems in fact we are having both a 3-pipe and a 2-pipe Tosh VRF installed in our offices.

    The header type refnet should be kept within 10° of the horizontal.

    The Y type refnets can be either verticle or horizontal - although if horizontal then within 15°.

    See page 21 of the 'SHRM' (3-pipe) installation manual A04-002.

    Noise is not a problem with these BS boxes and they can be installed close to the indoor unit. They are well insulated internally.

    Standard is a 5m limit between BS box and the indoor unit, although there is an extension accessory to take this up to 15m.

    Also worth noting that there is spec calling for a 500mm straight pipe into the BS box. To reduce turbulance and noise I guess.

    So the answer to your question would be minimum 1000mm between boxes - with a refnet half way between the pair of them that is.

    The BS boxes must be kept up-right for correct flow through the PMVs.

    Cheers

    Loops

  7. #7
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Toshiba VRF systems

    loops

    Thanks very much for that.

    al

Similar Threads

  1. Toshiba Digital Inverter range?
    By Slim R410a in forum Air Conditioning
    Replies: 19
    Last Post: 18-10-2010, 02:45 PM
  2. My local Apprentice Training Classes
    By shogun7 in forum Training
    Replies: 12
    Last Post: 17-03-2007, 03:10 PM
  3. Toshiba VRF systems
    By puddleboy3 in forum Air Conditioning
    Replies: 16
    Last Post: 01-08-2006, 09:28 PM
  4. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Replies: 15
    Last Post: 21-04-2006, 10:02 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •