    Evaporating Pressure



    What should the "ideal" evaporating pressure be on a R410 split air conditioning system, in cooling mode in a 30C ambient

    Should it be around 150psi ( which is evap temp +10C ) or should it be less.

    On a pre charged system how is the charge adjusted??

    Same question for R22

    Thx in advance



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Evaporating Pressure

    Quote Originally Posted by Abe
    What should the "ideal" evaporating pressure be on a R410 split air conditioning system, in cooling mode in a 30C ambient

    Should it be around 150psi ( which is evap temp +10C ) or should it be less.

    On a pre charged system how is the charge adjusted??

    Same question for R22

    Thx in advance
    Typical mistake Abe.
    Never refer to pressures. Look at temperatures using the Saturation tables for the gas you are using. With Air Conditioning you should aim to keep your evaporating temperatures above freezing to avoid frosting on the evaporator. With R22 the saturation temperature at 0C is 49.7psig so most "eng'rs" look for a suction pressure of 50/55psig which ensures that the evap stays free of frost. Likewise you need to look at the sat temp of R410a (sorry, I don't have it to hand) for 0 - 5 C saturation pressure.

    from experience it is about 7.5bar

  3. #3
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Evaporating Pressure

    Thx Frank

    Actually this morning when I posted , I did really mean evap temp, not pressure.........Grrrrrrrrrrrrrrrr But what the heck

    Ive printed it out
    Appreciate your help

    Picked up an order for 6 systems today, ranging from a couple of wall splits, to cassettes and one floor mounted

    and.............also got a cold room!!!!!
    Last edited by Abe; 31-07-2006 at 09:06 PM.

Similar Threads

  1. This a long one - AKV
    By Peter_1 in forum Industrial
    Replies: 6
    Last Post: 26-12-2008, 11:47 AM
  2. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  3. TEV capacity related to pressure drop
    By DaBit in forum CPU Overclockers
    Replies: 8
    Last Post: 06-12-2002, 05:11 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •