31-01-2002, 08:36 AM #1
R407C composition
I am working on a 407c system that has lost some of its charge.I can't tell the percentage that was lost. I would like to find out if the composition (chemistry) of the remaining LIQUID in the system has changed. If I remove ONLY the LIQUID (not vapour) from the system, would this liquid be 100% R407C.
-
31-01-2002, 06:50 PM #2If I remove ONLY the LIQUID (not vapour) from the system, would this liquid be 100% R407C.
Normally, liquid or vapor leaks do not cause sufficient fractionation to be a concern. Leaks at the evaporator and condenser coil (where refrigerant is in its two-phase region) can be more of a problem.
Verifying the pressure-temperature relationship of the refrigerant blend would be in order if one suspects composition has changed significantly.Prof Sporlan
-
01-02-2002, 12:21 AM #3
Correct me if I'm wrong, Prof.,
But having the conversation regarding fractionization with a refrigerant mfgr rep., it was stated that the conditions under which actual fractionization could actually occur would have to be entirely "static" (for lack of a better word), in relation to constant temperature and/or agititation in order for a measureable amount of fractionization to occur.
As such, these conditions are rarely found in field service. being that equipment is typically in service and operating at the time that such occurances (leakage) occurs.
I concern myself with such matters when addressing refrigerant leaks on systems containing blends when re-activating systems which may have been "moth-balled", or inactive for some time.
In the end, I was left with the impression that the affects of fractionization are not that significant in the realm of practical, or everyday refrigeration/leak reaair of equipment "in service". That furthermore the refrigerant industry has lessened somewhat it's emphasis on the fractionization issue in the realm of "everyday service/repair.
-
01-02-2002, 02:36 AM #4But having the conversation regarding fractionization with a refrigerant mfgr rep., it was stated that the conditions under which actual fractionization could actually occur would have to be entirely "static"
But from a practical standpoint, the Prof doubts that your average refrigerant leak in an operating system could cause sufficient fractionation to cause problems.Prof Sporlan
-
01-02-2002, 08:59 AM #5
R407C goes west
ISTR that ASHRAE data gives somthing like +/-2% tolerance on fluid properties so you have to loose a lot before you were left with R134a(?) perfromance.
Theres a number of papers showing R407C performance drops off with time and my only deduction is fractional loss.
Pressures and temperatures should be a reasonable guideline but having a sample tested is only valid at the time you took it and probably not worth the time of money.
If your loosing cooling perfromance and there's no other explaination then recover and recycle (if you have the facility or supplier access).
DerekDerek
Similar Threads
-
P/h chart for R407c
By Coolie in forum Technical SpeculationsReplies: 4Last Post: 29-05-2011, 06:17 PM -
R407C vs R22
By Abe in forum RefrigerantsReplies: 4Last Post: 05-10-2010, 08:34 AM -
R407C to R404a
By MaDiNfO in forum Air ConditioningReplies: 10Last Post: 30-07-2006, 09:34 AM -
Toshiba R407c Reversing Valves
By Brian_UK in forum Air ConditioningReplies: 2Last Post: 03-09-2005, 11:22 PM -
R22 vs R407C.....................again!!
By Abe in forum Air ConditioningReplies: 5Last Post: 24-07-2003, 12:21 AM