    Superheat Correction facter for R12-TXV - R134a?



    Ok I have a Singer M:207C TXV for R-12 (Same as the american Control company TXV) it comes preset to 9F (-12C) superheat.

    It is a 6,000BTU/hr unit (1.76 KW/hr) liquid cross charged head internaly equilized


    I'm thinking I need to set the super heat higher for it to work correctly with R-134a correct?

    Thanks guys for any Help.

    Head pressure during pull down is 150PSI



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Superheat Correction facter for R12-TXV - R134a?

    Quote Originally Posted by The MG Pony
    it comes preset to ... (-12C) superheat. ...
    I'm thinking I need to set the super heat higher for it to work correctly
    You must have made some kind of error in your calculations.

    If you are running a negative superheat, that is a unique kind of refrigeration system you are working on.

    If the evaporator has any appreciable pressure drop, the internally equalized valve may not remain stable no matter where it is set at.

  3. #3
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,261
    Rep Power
    31

    Re: Superheat Correction facter for R12-TXV - R134a?

    Quote Originally Posted by The MG Pony
    Ok I have a Singer M:207C TXV for R-12 (Same as the american Control company TXV) it comes preset to 9F (-12C) superheat.

    It is a 6,000BTU/hr unit (1.76 KW/hr) liquid cross charged head internaly equilized


    I'm thinking I need to set the super heat higher for it to work correctly with R-134a correct?

    Thanks guys for any Help.

    Head pressure during pull down is 150PSI
    Hi, The MG Pony

    I think in this case this 9F means 5K or 5C but only like a difference, because the superheat we always write in K and K is always positive number, there is not negative temp shown in K scale at all.

    So if you run your sistem at 9F(-12,778C) your superheat will be 18F(-7,778C) (difference of 9F or 5K or 5C)

    For *****s it is Ok to have min of 5K, with ammonia you can go to 0K.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  4. #4
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: Superheat Correction facter for R12-TXV - R134a?

    This is what I read off the TXVs manual it is presset to 9degrees fehren?

    I guess there is no sort of correction facter eh? just a good thermometer and a set of guages and some time tuning it all?

    But if it is going as a differance then is there some basic way to set it correctly to work with R-134a? IE Increasing super heat or reducing it slightly to match the R-12 curve.
    Last edited by The MG Pony; 01-08-2006 at 04:06 AM.

Similar Threads

  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  2. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM
  3. Replies: 5
    Last Post: 01-03-2004, 09:59 PM
  4. How do you calculate Superheat?
    By zolar1 in forum Training
    Replies: 39
    Last Post: 10-05-2002, 02:37 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •