Swimming pool and ice rink is this a match made in heaven
My company operates a large swimming pool complex (2370 M3 of water in circulation), directly adjacent to an ice rink which is operated by another copmany.
My annual energy consumption for the pool water heating is 1,798,990 kWh, taken from heat meters.
I am considering using my pool water at 30 centigrade to recover the heat from their cooling plant which uses R407c.
Is the pool water at this temperature suitable for the task or does it need an intermediate heat transfer circuit to achieve the appropriate transfer of heat.
-
29-07-2006, 12:09 PM #2
Re: Swimming pool and ice rink is this a match made in heaven
Originally Posted by chuffin
The rink plant will probably have to have it's head pressure risen to allow it to fully condense the refrigerant. Use it's existing condenser as a subcooler and there will be no energy penalty when doing this.
Kind Regards AndyIf you can't fix it leave it that no one else will:rolleyes: