    panasonic 3 phase split



    a panasonic (r22) split system has threw up a fault code of f 30 (only one split being controlled of the controller) . the manuel states that there is a problem with the outside unit. to cut a story short the voltage across the red and blue phase is 1.5v but between red/yellow and yellow/blue are both 415v . this is even the same at the dis board (tried disconnecting the s.w.a. feed to the isolator but still the same). if any one could explain how this could accour and what effect it will have to the condensing unit.



  2. #2
    rbartlett's Avatar
    rbartlett Guest

    Re: panasonic 3 phase split

    Quote Originally Posted by mike live
    a panasonic (r22) split system has threw up a fault code of f 30 (only one split being controlled of the controller) . the manuel states that there is a problem with the outside unit. to cut a story short the voltage across the red and blue phase is 1.5v but between red/yellow and yellow/blue are both 415v . this is even the same at the dis board (tried disconnecting the s.w.a. feed to the isolator but still the same). if any one could explain how this could accour and what effect it will have to the condensing unit.
    the only possible way i can think of is the red and blue are being fed off the same phase..

    anyone else ??

    cheers

    richard

  3. #3
    Join Date
    May 2006
    Location
    aberdeen
    Posts
    125
    Rep Power
    18

    Re: panasonic 3 phase split

    Hi mike, Whats the readings between the 3 lives and the neutral??

  4. #4
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: panasonic 3 phase split

    with a visual check i can see the feeds for the dis board come straight from the meter. at the time i checked voltage down to earth on each phase and got 240v, but as i've said across the red and the blue phase theres no voltage. i eventually checked the board supply from the meter and hadthe same out come , no voltage between red and blue but 240v down to earth. needless to say i've told the customer that they need an electrian but would like to know if anyone had any ideas.

    think i remember testing the 3 phases down to neutral and had the same. checked earth to neutral just incaes but there was no voltage on neutral a so that rules that out
    Last edited by mike live; 27-07-2006 at 06:45 PM.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: panasonic 3 phase split

    Have you tried a phase checker? http://www.martindale-electric.co.uk/misc.htm#mm42

  6. #6
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    196
    Rep Power
    20

    Re: panasonic 3 phase split

    I'm not a refrigeration engeneer... but I had a similar problem with freezer at work.... turned out one of the 3 phase contactors (not sure on the technical term for them... the little boxes with the magnet in the middle that jumps in and out)

    anyway... the contactor had burnt out, disconnected one of the positives and shorted it to another

  7. #7
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: panasonic 3 phase split

    looks like i'll have to spend some money on a phase checker.(cheers frank) would like to know though if i did have a phase supply down how would there be 240v to earth on that phase ?

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: panasonic 3 phase split

    Voltage and phase are 2 different things

  9. #9
    Join Date
    Jul 2006
    Location
    Northern Ireland
    Age
    54
    Posts
    19
    Rep Power
    0

    Re: panasonic 3 phase split

    Hi , I had a problem similar to this a while back . I traced the fault back to the main dis board were there was a loose/faulty connection on the breaker ..this may be the same thing???

  10. #10
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: panasonic 3 phase split

    mike live, or not so as the case is, is this a new install,assume not bein on 22. Can,t understand your fault code, is it a 3phase outdoor? surely fault code of missing phase would display don't you tink? do you have a 'volt stick', try that to check phases coming into board, far cheaper than rotation checker + whats rotation checker gonna tell you more than you allready know? not a lot. keeping things simple, i've never needed one and I'm really simple

  11. #11
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: panasonic 3 phase split

    will probably go for the volt stick test (cheers debad)

    if frank could further explain the difference between voltage and phases i would like to know more ?

  12. #12
    rbartlett's Avatar
    rbartlett Guest

    Re: panasonic 3 phase split

    Quote Originally Posted by bebad
    mike live, or not so as the case is, is this a new install,assume not bein on 22. Can,t understand your fault code, is it a 3phase outdoor? surely fault code of missing phase would display don't you tink? do you have a 'volt stick', try that to check phases coming into board, far cheaper than rotation checker + whats rotation checker gonna tell you more than you allready know? not a lot. keeping things simple, i've never needed one and I'm really simple
    A phase checker will confirm if you have the right 3 phases and they are in sync. a volt stick will tell you if you have voltage-but no indication of what the voltage actually is or which phase either .

    A volt stick is not a instrument of measurement merely an indicator and not a suitable substitute for a skilled engineer..use with caution as this is of absolutely no use in this instance



    cheers

    richard
    Last edited by rbartlett; 27-07-2006 at 09:43 PM.

  13. #13
    rbartlett's Avatar
    rbartlett Guest

    Re: panasonic 3 phase split

    Quote Originally Posted by mike live
    will probably go for the volt stick test (cheers debad)

    if frank could further explain the difference between voltage and phases i would like to know more ?

    you tested with a meter now you think a red neon will solve the problem...!!!!



    cheers

    richard

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: panasonic 3 phase split

    Thoughts:-

    Red or blue phase blown but shorted, draw that out and you will get your volt readings.

    Isolate dist. board and remove MCB.

    Check dist. board phases at MCB position.

    Check MCB.

    Check condensing unit isolator for breaks/welds, failure.

    Check condensing unit contactor for breaks/welds, failure.

    Check cable.

    Get coffee, call office, declare a national holiday and go home.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: panasonic 3 phase split

    with a 'neon' and multi meter is all that i believe to be needed to identify the conditions/fault a skilled engineer should surely only need to employ these if not just one of to confirm fault, as frank states its more than likely fault is on 3 pole mcb or main switch gear to board, maybe incoming fuse gear. still don't see the need for rotation test.

  16. #16
    Join Date
    Nov 2004
    Location
    Nottingham
    Posts
    37
    Rep Power
    0

    Re: panasonic 3 phase split

    also don't bother to buy rotation tester if one is fitted to condenser like in many cases does your system have fault code relevant

  17. #17
    Join Date
    Jun 2006
    Location
    england
    Posts
    25
    Rep Power
    0

    Re: panasonic 3 phase split

    just would like to finally explain true problem of the lack of 415v across the phases. comes down to roadworks in the area. contractors had dug up a power cabel and therefore disconecting one of the phases to the petrol station. the reason i was getting 240v on the phase was due to tracking back off another phase. (well this was what the sparky tells me)

  18. #18
    Join Date
    Aug 2006
    Location
    Ireland
    Age
    46
    Posts
    26
    Rep Power
    0

    Re: panasonic 3 phase split

    Quote Originally Posted by mike live
    just would like to finally explain true problem of the lack of 415v across the phases. comes down to roadworks in the area. contractors had dug up a power cabel and therefore disconecting one of the phases to the petrol station. the reason i was getting 240v on the phase was due to tracking back off another phase. (well this was what the sparky tells me)
    Was going to ask if you disconected the power and all. Its the same with checking anything, back feed
    can put you off. Thought someone would have pointed this out to you.

  19. #19
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: panasonic 3 phase split

    Quote Originally Posted by Langer
    Thought someone would have pointed this out to you.
    This would have been shown up by the phase tester but spending money on a decent piece of kit was ridiculed earlier in the thread.

    Just can't help some people

Similar Threads

  1. Single phase contactor
    By Andy T in forum Commercial
    Replies: 9
    Last Post: 23-10-2006, 01:45 PM
  2. Phase Failure Protection
    By Abe in forum Electrical
    Replies: 11
    Last Post: 08-11-2005, 10:23 PM
  3. Cooling condenser of split with condensate from evaporator
    By smileypete in forum Air Conditioning
    Replies: 11
    Last Post: 10-07-2005, 08:21 AM
  4. LG ducted split
    By Abe in forum Air Conditioning
    Replies: 20
    Last Post: 08-06-2005, 07:19 PM
  5. 3 phase connections
    By davidler in forum Industrial
    Replies: 2
    Last Post: 22-03-2004, 03:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •